What would you like to do?

Can you replace a 15A circuit breaker with a 30A breaker?

already exists.

Would you like to merge this question into it?

already exists as an alternate of this question.

Would you like to make it the primary and merge this question into it?

exists and is an alternate of .

I believe that the wires supplying a 30 amp circuit must be at least 10 gauge. If you have 14 or 12 gauge wires going to or from your 15 amp breaker, then drawing 30 amps over it could cause a fire hazard. It's like using those cheapo non-UL certified extension cords to plug a MILLION X-mas lights into (drawing more power than the wires can handle). You also have to make sure this GFI outlet you refered to is rated for 30 amps.



Do not simply swap out breakers. Overloading the wires in the circuit protected by that breaker will cause a fire.

If you need a 30 amp circuit you must run #10 gauge wire.
6 people found this useful
Thanks for the feedback!

How can you use an electrical circuit breaker?

A circuit breaker is a device use in series with the load in many electrical application, residential, commercial end industrial. The power needs to be on in order for this pr

What is a circuit breaker for?

The circuit breaker obviously breaks the circuit but only in an attempt to stop a surge of electricity going through your house and possibly hurting you if you're using an app

If a circuit breaker is a 30A 240V for a dryer and the dryer calls for a 20A do you need to change your breaker?

  No, you're fine.   Answer   Breakers are mainly used to protect the wires (and people), not the appliance. The appliance should have its own overcurrent protect

How many wall outlets can you have in a circuit using a 15A breaker?

One View:In USA: As many as you want. There's no magic number. You have 15A to play with, so you can divide that up however you wish. It all depends on what you intend to plug

What is the biggest circuit breaker in a house?

The biggest circuit breaker in any home is the main breaker located in your main breaker panel that is installed where your electrical service cable comes into your home.

What is the difference of a Circuit Breaker from an Air Circuit breaker?

All circuit breakers are overcurrent protection devices, which are used to disconnect a circuit in the event of a prolonged overload current or a short-circuit current. An ai

How much does it cost to replace fuse box with circuit breaker?

This project is a service upgrade and requires a permit and inspections. In the central United States where I live, you might get it for $800 but don't be surprised if it co

How many lights and outlets can go on 15A or 20A breakers?

Answer for USA, Canada and countries running a 60 Hz supply service.Lights Lights and outlets are normally wired on separate branch circuits, which means that the lights will

How many switches can you have in a circuit using a 15A breaker?

It is not so much how many switches as it is devices per circuit.    Circuit loading    In Canada the electrical code states that there shall be not more that 12

Can circuit breaker isolate circuit?

That's just what a circuit-breaker is designed to do - Isolate a circuit from the rest of the system.   Not necessarily. A circuit breaker is a protective device, design

What is a Circuit breaker and explain type circuit breakers?

A circuit breaker is a switching device which can make,brake and carrying (or trip the circuit) that specified over currents for a small interval of time . There is a differ

What is generator circuit breaker and utility circuit breaker?

The generator circuit breaker or gcb is a circuit breaker which is connected with the generator . Whenever there is a fault in the generator the circuit breaker trips and disc

Can you replace a 50A receptacle with a 30A 3-prong receptacle and keep the existing dedicated 20A pair of breakers?

No. The receptacle, wiring, and breaker ratings should all be matched properly.   Replacing the 50A receptacle with a 30A receptacle isn't a problem, since the wire should
In Science

What is a circuit breaker?

A circuit breaker is an automatically operated electrical switch  designed to protect an electrical circuit from damage caused by  overload or short circuit. Its basic funct