Background
A smoke detector is a device that senses the presence of smoke in a building and warns the occupants, enabling them to escape a fire before succumbing to smoke inhalation or burns. Equipping a home with at least one smoke detector cuts in half the chances that the residents will die in a fire. In 1992 the readers of R&D Magazine selected home smoke alarms as one of the "30 Products that Changed Our Lives." Smoke detectors became widely available and affordable in the early 1970s. Prior to that date, fatalities from fires in the home averaged 10,000 per year, but by the early 1990s the figure dropped to fewer than 6,000 per year.
Two basic types of smoke detectors are currently manufactured for residential use. The photoelectric smoke detector uses an optical beam to search for smoke. When smoke particles cloud the beam, a photoelectric cell senses the decrease in light intensity and triggers an alarm. This type of detector reacts most quickly to smoldering fires that release relatively large amounts of smoke.
The second type of smoke detector, known as an ionization chamber smoke detector (ICSD), is quicker at sensing flaming fires that produce little smoke. It employs a radioactive material to ionize the air in a sensing chamber; the presence of smoke affects the flow of the ions between a pair of electrodes, which triggers the alarm. Between 80 and 90% of the smoke detectors in American homes are of this type. Although most residential models are self-contained units that operate on a 9-volt battery, construction codes in some parts of the country now require installations in new homes to be connected to the house wiring, with a battery backup in case of a power failure.
The typical ICSD radiation source emits alpha particles that strip electrons from the air molecules, creating positive oxygen and nitrogen ions. In the process, the electrons attach themselves to other air molecules, forming negative oxygen and nitrogen ions. Two oppositely charged electrodes within the sensing chamber attract the positive and negative ions, setting up a small flow of current in the air space between the electrodes. When smoke particles enter the chamber, they attract some of the ions, disrupting the current flow. A similar reference chamber is constructed so that no smoke particles can enter. The smoke detector constantly compares the current flow in the sensing chamber to the flow in the reference chamber; if a significant difference develops, an alarm is triggered.
History
The development of these life-saving appliances began in 1939 when Ermst Meili, a Swiss physicist, devised an ionization chamber device capable of detecting combustible gases in mines. The real breakthrough was Meili's invention of a cold-cathode tube that could amplify the small electronic signal generated by the detection mechanism to a strength sufficient to activate an alarm.
Although ionization chamber smoke detectors have been available in the United States since 1951, they were initially used only in factories, warehouses, and public buildings because they were expensive. By 1971 residential ICSDs were commercially available; they cost about $125 per detector and sold at a rate of a few hundred thousand per year.
A fluny of new technological developments occurred over the next five years, reducing the cost of the detectors by 80% and boosting sales to 8 million in 1976 and 12 million in 1977. By this time, solid-state circuitry had replaced the earlier cold-cathode tube, significantly reducing the size of the detectors as well as their cost. Design refinements, including more energy-efficient alarm horns, enabled the use of commonly available sizes of batteries rather than the hard-to-find specialty batteries that had previously been required. Improvements in the circuitry made it possible to monitor both the decrease in voltage and the build-up of internal resistance in the battery, either of which would trigger a signal to replace the power source. The new generation of detectors could also function with smaller amounts of radioactive source material, and the sensing chamber and smoke detector enclosure were redesigned for more effective operation.
Raw Materials
An ICSD smoke detector is composed of a housing made of polyvinylchloride or poly-styrene plastic, a small electronic alarm horn, a printed circuit board with an assortment of electronic components, and a sensing chamber and reference chamber, each containing a pair of electrodes and the radioactive source material.
Americium 241 (Am-241), a radioactive isotope, has been the preferred source material for ICSDs since the late 1970s. It is very stable and has a half-life of 458 years. It is usually processed with gold and sealed within gold and silver foils.
The Manufacturing
Process
The production of a smoke detector consists of two major steps. One is fabrication of the Am-241 into a form (typically a foil) that can be installed into the sensing and reference chambers. The other is assembly of the entire ICSD, beginning either with all of the individual components or with prefabricated sensing and reference chambers obtained from the manufacturer of the radioactive source material. The following description covers all steps, even though some may be done by different manufacturers. Tests and inspections at several stages of the assembly process ensure a reliable product.
Radioactive source
The sensing and reference chambers
The circuit board
Housing
Final assembly
New Developments
Some recent developments may make smoke detectors even more effective. One model, for example, uses a strobe light alarm to alert hearing-impaired people of danger. The remote strobe light can be mounted in a bedroom even though the detector may be located in another room or hallway, giving the same advantage of early warning available to hearing people when an alarm sounds from outside the bedroom.
In 1993 Newtron Products redesigned a traditional smoke detector to fit in the standard air filters of a central heating or air conditioning system in order to examine air that circulates through an entire building. When it detects smoke, the device shuts off the system's blower to prevent the air flow from helping spread the smoke and fire. In addition, it triggers an alarm that resonates through the duct work and is audible anywhere in the building.
Another kind of fire detector may utilize sound. Investigators at the Building and Fire Research Laboratory of the National Institute of Standards and Technology have found that various types of housing materials, such as wood, plastic, and drywall, make identifiable sounds as they expand from rapid heating. Piezoelectric transducers can detect those sounds even before the materials actually begin to burn. This would be especially helpful in detecting incipient fires caused by overheated electrical wiring within a building's walls.
Where To Learn More
Books
Belanger, R., D.W. Buckley, and J.B. Swenson. Environmental Assessment of Ionization Chamber Smoke Detectors Containing Am-241. Science Applications Inc., November 1979.
Bukowski, Richard W., and G.W. Mulhol-land. Smoke Detector Design and Smoke Properties. National Bureau of Standards, National Engineering Laboratory, Center for Fire Research, 1978.
Periodicals
Andrews, Edmund L. "Central System for Smoke Detection." The New York Times, February 1, 1993, p. D2.
"Sounds Like Fire." Discover, May 1994, p. 16 "Listening for Hidden Fires." Science News, July 24, 1993, p. 63.
"Smoke Detectors: Essential for Safety." Consumer Reports, May 1994, pp. 336-39.
[Article by: Loretta Hall]
A device for sensing the presence of smoke in a building—usually by means of a photoelectric detector, ionization detector, ultraviolet flame detector, or a heat detector.
A smoke detector is a device that detects smoke, typically as an indicator of fire. Commercial, industrial, and mass residential devices issue a signal to a fire alarm system, while household detectors, known as smoke alarms, generally issue a local audible or visual alarm from the detector itself.
Smoke detectors are typically housed in a disk-shaped plastic enclosure about 150 millimetres (6 in) in diameter and 25 millimetres (1 in) thick, but the shape can vary by manufacturer or product line. Most smoke detectors work either by optical detection (photoelectric) or by physical process (ionization), while others use both detection methods to increase sensitivity to smoke. Sensitive alarms can be used to detect, and thus deter, smoking in areas where it is banned such as toilets and schools. Smoke detectors in large commercial, industrial, and residential buildings are usually powered by a central fire alarm system, which is powered by the building power with a battery backup. However, in many single family detached and smaller multiple family housings, a smoke alarm is often powered only by a single disposable battery.
|
Contents
|
The first automatic electric fire alarm was invented in 1890 by Francis Robbins Upton (U.S. patent no. 436,961). Upton was an associate of Thomas Edison, but there is no evidence that Edison contributed to this project.
George Andrew Darby patented the first electrical Heat detector and Smoke detector in 1902 in Birmingham, England.[1]
In the late 1930s the Swiss physicist Walter Jaeger tried to invent a sensor for poison gas. He expected that gas entering the sensor would bind to ionized air molecules and thereby alter an electric current in a circuit in the instrument. His device failed: small concentrations of gas had no effect on the sensor's conductivity. Frustrated, Jaeger lit a cigarette—and was soon surprised to notice that a meter on the instrument had registered a drop in current. Smoke particles had apparently done what poison gas could not. Jaeger's experiment was one of the advances that paved the way for the modern smoke detector.
It was 30 years, however, before progress in nuclear chemistry and solid-state electronics made a cheap sensor possible. While home smoke detectors were available during most of the 1960s, the price of these devices was rather high. Before that, alarms were so expensive that only major businesses and theaters could afford them.
The first truly affordable home smoke detector was invented by Duane D. Pearsall in 1965, featuring an individual battery powered unit that could be easily installed and replaced. The first units for mass production came from Duane Pearsall’s company, Statitrol Corporation, in Lakewood, Colorado. These first units were made from strong fire resistant steel and shaped much like a bee's hive. The battery was a rechargeable specialized unit created by Gates Energy. The need for a quick replace battery didn't take long to show itself and the rechargeable was replaced with a pair of AA batteries along with a plastic shell encasing the detector. The small assembly line sent close to 500 units per day before Statitrol sold its invention to Emerson Electric in 1980 and Sears’s retailers picked up full distribution of the 'now required in every home' smoke detector.
The first commercial smoke detectors came to market in 1969. Today they are installed in 93% of U.S. homes and 85% of UK homes. However it is estimated that any given time over 30% of these alarms do not work, as users remove the batteries, or forget to replace them.
An optical detector is a light sensor. When used as a smoke detector, it includes a light source (incandescent bulb or infrared LED), a lens to collimate the light into a beam, and a photodiode or other photoelectric sensor at an angle to the beam as a light detector. In the absence of smoke, the light passes in front of the detector in a straight line. When smoke enters the optical chamber across the path of the light beam, some light is scattered by the smoke particles, directing it at the sensor and thus triggering the alarm.
Also seen in large rooms, such as a gymnasium or an auditorium, are devices that detect a projected beam. A wall-mounted unit sends out a beam, which is either received by a separate monitoring device or reflected back via a mirror. When the beam becomes less visible to the "eye" of the sensor, it sends an alarm signal to the fire alarm control panel.
According to the National Fire Protection Agency, "photoelectric smoke detection is generally more responsive to fires that begin with a long period of smoldering (called smoldering fires)." Also, studies by Texas A&M and the NFPA cited by the City of Palo Alto California state, "Photoelectric alarms react slower to rapidly growing fires than ionization alarms, but laboratory and field tests have shown that photoelectric smoke alarms provide adequate warning for all types of fires and have been shown to be far less likely to be deactivated by occupants."
Although optical alarms are highly effective at detecting smoldering fires and do provide adequate protection from flaming fires, fire safety experts and the National Fire Protection Agency recommend installing what are called combination alarms, which are alarms that either detect both heat and smoke, or use both the ionization and photoelectric / optical processes. Also some combination alarms may include a carbon monoxide detection capability.
Not all optical or photoelectric detection methods are the same. The type and sensitivity of the photodiode or optical sensor, and type of smoke chamber differ between manufacturers.
An ionization smoke detector uses a radioisotope such as americium-241 to produce ionization in air; a difference due to smoke is detected and an alarm is generated. Ionisation detectors are more sensitive to flaming fires than optical detectors, while optical detectors are more sensitive to smouldering fires.[2]
The radioactive isotope americium-241 in the smoke detector emits ionizing radiation in the form of Alpha particles into an ionization chamber that is open to the air and a sealed reference chamber. The air molecules in the chamber become ionized and these ions allow the passage of a small electric current between charged electrodes placed in the chamber. If any smoke particles pass into the chamber the ions will attach to the particles and so will be less able to carry the current. An electronic circuit detects the current drop, and sounds the alarm. The reference chamber cancels effects due to air pressure, temperature, or the aging of the source. [3] Other parts of the circuitry monitor the battery (where used) and sound an intermittent warning when the battery nears exhaustion. A self-test circuit simulates an imbalance in the ionization chamber and verifies the function of power supply, electronics, and alarm device. The standby power draw of an ionization smoke detector is so low that a small battery can provide power for months or years, making the unit independent of AC power supply or external wiring; however, batteries require regular test and replacement.
An ionization type smoke detector is generally cheaper to manufacture than an optical smoke detector; however, it is sometimes rejected because it is more prone to false (nuisance) alarms than photoelectric smoke detectors.[4][5] It can detect particles of smoke that are too small to be visible.
Americium-241, an alpha emitter, has a half-life of 432 years. Alpha radiation, as opposed to beta and gamma, is used for two additional reasons: Alpha particles have high ionization, so sufficient air particles will be ionized for the current to exist, and they have low penetrative power, meaning they will be stopped by the plastic of the smoke detector or the air. About one percent of the emitted radioactive energy of 241Am is gamma radiation. The amount of elemental americium-241 is small enough to be exempt from the regulations applied to larger sources. It includes about 37 kBq or 1 µCi of radioactive element americium-241 (241Am), corresponding to about 0.3 µg of the isotope. [6][7] This provides sufficient ion current to detect smoke, while producing a very low level of radiation outside the device. The presence of americium-241 means that every decommissioned smoke detector must be properly disposed of lest it constitute an environmental hazard.[8]
An air-sampling smoke detector is capable of detecting microscopic particles of smoke. Most air-sampling detectors are aspirating smoke detectors, which work by actively drawing air through a network of small-bore pipes laid out above or below a ceiling in parallel runs covering a protected area. Small holes drilled into each pipe form a matrix of holes (sampling points), providing an even distribution across the pipe network. Air samples are drawn past a sensitive optical device, often a solid-state laser, tuned to detect the extremely small particles of combustion. Air-sampling detectors may be used to trigger an automatic fire response, such as a gaseous fire suppression system, in high-value or mission-critical areas, such as archives or computer server rooms.
Most air-sampling smoke detection systems are capable of a higher sensitivity than spot type smoke detectors and provide multiple levels of alarm threshold, such as Alert, Action, Fire 1 and Fire 2. Thresholds may be set at levels across a wide range of smoke levels. This provides earlier notification of a developing fire than spot type smoke detection, allowing manual intervention or activation of automatic suppression systems before a fire has developed beyond the smoldering stage, thereby increasing the time available for evacuation and minimizing fire damage.
Some smoke alarms use a carbon dioxide sensor or carbon monoxide sensor to detect extremely dangerous products of combustion.[9][10] However, not all smoke detectors that are advertised with such gas sensors are actually able to warn of poisonous levels of those gases in the absence of a fire.[citation needed]
Photoelectric smoke detectors respond quickly to smoldering fires, which are made up of combustion particles between 0.3 and 10.0 microns. Ionization smoke detectors, however, are superior when detecting flaming fires, which can be characterized by combustion particles between 0.01 and 0.3 microns. Also, ionization detectors are weaker in high air-flow environments, and because of this, the photoelectric smoke detector is more reliable for detecting smoke in both the smoldering and flaming stages of a fire.[11]
According to fire tests conformant to EN 54, the CO2 cloud from smoke can usually be detected before particulate.[10]
Due to the varying levels of detection capabilities between detector types, manufacturers have designed multi-criteria devices which cross-reference the separate signals to both rule out false alarms and improve response times to real fires.[11] Examples include Photo/heat, photo/CO, and even CO/photo/heat/IR.
Obscuration is a unit of measurement that has become the standard definition of smoke detector sensitivity. Obscuration is the effect that smoke has on reducing sensor visibility; higher concentrations of smoke result in higher obscuration levels.
| Typical smoke detector obscuration ratings[12] | |
|---|---|
| Type of Detector | Obscuration Level |
| Ionization | 2.6–5.0% obs/m (0.8–1.5% obs/ft) |
| Photoelectric | 6.5–13.0% obs/m (2–4% obs/ft) |
| Beam | 3% obs/m (0.9% obs/ft)[citation needed] |
| Aspirating | 0.005–20.5% obs/m (0.0015–6.25% obs/ft) |
| Laser | 0.06–6.41% obs/m (0.02–2.0% obs/ft)[13] |
| This section requires expansion. |
Commercial smoke detectors are either conventional or analog addressable, and are wired up to security monitoring systems or fire alarm control panels (FACP). These are the most common type of detector, and usually cost a lot more than a household smoke alarms. They exist in most commercial and industrial facilities, such as high rises, ships and trains. These detectors don't need to have built in alarms, as alarm systems can be controlled by the connected FACP, which will set off relevant alarms, and can also implement complex functions such as a staged evacuation.
The word "conventional" is slang used to distinguish the method used to communicate with the control unit from that used by addressable detectors whose methods were unconventional at the time of their introduction. So called “Conventional Detectors” cannot be individually identified by the control unit and resemble an electrical switch in their information capacity. These detectors are connected in parallel to the signaling path or (initiating device circuit) so that the current flow is monitored to indicate a closure of the circuit path by any connected detector when smoke or other similar environmental stimulus sufficiently influences any detector. The resulting increase in current flow is interpreted and processed by the control unit as a confirmation of the presence of smoke and a fire alarm signal is generated.
This type of installation gives each detector on a system an individual number, or address. Thus, addressable detectors allow an FACP, and therefore fire fighters, to know the exact location of an alarm where the address is indicated on a diagram.
Analog addressable detectors provide information about the amount of smoke in their detection area, so that the FACP can decide itself, if there is an alarm condition in that area (possibly considering day/night time and the readings of surrounding areas). These are usually more expensive than autonomous deciding detectors.[14]
The main function of a single station or "standalone" smoke alarm is to alert persons at risk. Several methods are used and documented in industry specifications published by Underwriters Laboratories[15] Alerting methods include:
Some models have a hush or temporary silence feature that allows silencing without removing the battery. This is especially useful in locations where false alarms can be relatively common (e.g. due to "toast burning") or users could remove the battery permanently to avoid the annoyance of false alarms, but removing the battery permanently is strongly discouraged.
While current technology is very effective at detecting smoke and fire conditions, the deaf and hard of hearing community has raised concerns about the effectiveness of the alerting function in awakening sleeping individuals in certain high risk groups such as the elderly, those with hearing loss and those who are intoxicated.[16] Between 2005 and 2007, research sponsored by the United States' National Fire Protection Association (NFPA) has focused on understanding the cause of a higher number of deaths seen in such high risk groups. Initial research into the effectiveness of the various alerting methods is sparse. Research findings suggest that a low frequency (520 Hz) square wave output is significantly more effective at awakening high risk individuals. Wireless smoke and carbon monoxide detectors linked to alert mechanisms such as vibrating pillow pads for the hearing impaired, strobes, and remote warning handsets are more effective at waking people with serious hearing loss than other alarms.[17]
Most residential smoke detectors run on 9-volt alkaline or carbon-zinc batteries. When these batteries run down, the smoke detector becomes inactive. Most smoke detectors will signal a low-battery condition. The alarm may chirp at intervals if the battery is low, though if there is more than one unit within earshot, it can be hard to locate. It is common, however, for houses to have smoke detectors with dead batteries. It is estimated, in the UK, that over 30% of smoke alarms may have dead or removed batteries. As a result, public information campaigns have been created to remind people to change smoke detector batteries regularly. In Australia, for example, a public information campaign suggests that smoke alarm batteries should be replaced on April Fools' Day every year.[18] In regions using daylight saving time, campaigns may suggest that people change their batteries when they change their clocks or on a birthday.
Some detectors are also being sold with a lithium battery that can run for about 7 to 10 years, though this might actually make it less likely for people to change batteries, since their replacement is needed so infrequently. By that time, the whole detector may need to be replaced. Though relatively expensive, user-replaceable 9-volt lithium batteries are also available.
Common NiMH and NiCd rechargeable batteries have a high self-discharge rate, making them unsuitable for use in smoke detectors. This is true even though they may provide much more power than alkaline batteries if used soon after charging, such as in a portable stereo. Also, a problem with rechargeable batteries is a rapid voltage drop at the end of their useful charge. This is of concern in devices such as smoke detectors, since the battery may transition from "charged" to "dead" so quickly that the low-battery warning period from the detector is either so brief as to go unnoticed, or may not occur at all.
The NFPA, recommends that home-owners replace smoke detector batteries with a new battery at least once per year, when it starts chirping (a signal that its charge is low), or when it fails a test, which the NFPA recommends to be carried out at least once per month by pressing the "test" button on the alarm.[19]
In 2004, NIST issued a comprehensive report[5] that concludes, among other things, that "smoke alarms of either the ionization type or the photoelectric type consistently provided time for occupants to escape from most residential fires", and "consistent with prior findings, ionization type alarms provided somewhat better response to flaming fires than photoelectric alarms (57 to 62 seconds faster response), and photoelectric alarms provided (often) considerably faster response to smoldering fires than ionization type alarms (47 to 53 minutes faster response)".
The NFPA strongly recommends the replacement of home smoke alarms every 10 years. Smoke alarms become less reliable with time, primarily due to aging of their electronic components, making them susceptible to nuisance false alarms. In ionization type alarms, decay of the 241Am radioactive source is a negligible factor, as its half-life is far greater than the expected useful life of the alarm unit.
Regular cleaning can prevent false alarms caused by the build up of dust or other objects such as flies, particularly on optical type alarms as they are more susceptible to these factors. A vacuum cleaner can be used to clean ionization and optical detectors externally and internally. However, on commercial ionisation detectors it is not recommended for a lay person to clean internally. To reduce false alarms caused by cooking fumes, use an optical or 'toast proof' alarm near the kitchen. [20]
A jury in the United States District Court for the Northern District of New York decided in 2006 that First Alert and its parent company, BRK Brands, was liable for millions of dollars in damages because the ionization smoke alarm in the Hackert's house was a defective design by its nature, typically failing to detect the slow-burning fire and choking smoke that filled the home as the family slept.[21]
In the United States, most state and local laws regarding the required number and placement of smoke detectors are based upon standards established in NFPA 72, National Fire Alarm and Signaling Code.
Laws governing the installation of smoke detectors vary depending on the locality. Homeowners with questions or concerns regarding smoke detector placement may contact their local fire marshal or building inspector for assistance. However, some rules and guidelines for existing homes are relatively consistent throughout the developed world. For example, Canada and Australia require a building to have a working smoke detector on every level. The United States NFPA code cited in the previous paragraph requires smoke detectors on every habitable level and within the vicinity of all bedrooms. Habitable levels include attics that are tall enough to allow access.
In new construction, minimum requirements are typically more stringent. All smoke detectors must be hooked directly to the electrical wiring, be interconnected and have a battery backup. In addition, smoke detectors are required either inside or outside every bedroom, depending on local codes. Smoke detectors on the outside will detect fires more quickly, assuming the fire does not begin in the bedroom, but the sound of the alarm will be reduced and may not wake some people. Some areas also require smoke detectors in stairways, main hallways and garages.
Wired units with a third "interconnect" wire allow a dozen or more detectors to be connected, so that if one detects smoke, the alarms will sound on all the detectors in the network, improving the chances that occupants will be alerted, even if they are behind closed doors or if the alarm is triggered one or two floors from their location. Wired interconnection may only be practical for use in new construction, especially if the wire needs to be routed in areas that are inaccessible without cutting open walls and ceilings. As of the mid-2000s, development has begun on wirelessly networking smoke alarms, using technologies such as ZigBee, which will allow interconnected alarms to be easily retrofitted in a building without costly wire installations. Some wireless systems using Wi-Safe technology will also detect smoke or carbon monoxide through the detectors, which simultaneously alarm themselves with vibrating pads, strobes and remote warning handsets. As these systems are wireless they can easily be transferred from one property to another.
In the UK the placement of detectors are similar however the installation of smoke alarms in new builds need to comply to the British Standards BS5839 pt6. BS 5839: Pt.6: 2004 recommends that a new-build property consisting of no more than 3 floors (less than 200sqm per floor) should be fitted with a Grade D, LD2 system. Building Regulations in England, Wales and Scotland recommend that BS 5839: Pt.6 should be followed, but as a minimum a Grade D, LD3 system should be installed. Building Regulations in Northern Ireland require a Grade D, LD2 system to be installed, with smoke alarms fitted in the escape routes and the main living room and a heat alarm in the kitchen, this standard also requires all detectors to have a main supply and a battery back up.
|
||||||||||||||||
This entry is from Wikipedia, the leading user-contributed encyclopedia. It may not have been reviewed by professional editors (see full disclaimer)