This depends upon the circuit breaker capacity. You may never load a circuit to greater than 80% of it's capacity. So you may load up to 12 Amps on a 15 Amp circuit, and, 16 Amps on a 20 Amp circuit.

The National Electrical Code requires you to calculate each receptacle at 180 VA.

If the circuit is 120 volts and 15 amps, you would have 1800 VA, divide by 180 VA per receptacle, equals 10 receptacles per circuit (minus the wattage of each luminaire or light fixture added to the circuit, before dividing by the 180 VA).

If the circuit is 120 volts and 20 amps, you would have 2400 VA, divide by 180 VA per receptacle, equals 13.333 receptacles per circuit (round down to 13 receptacles),(minus the wattage of each luminaire or light fixture added to the circuit, before dividing by the 180 VA).

123
๐Ÿ™
0
๐Ÿคจ
0
๐Ÿ˜ฎ
0
๐Ÿ˜‚
0

Related Questions

User Avatar

Your bathroom plug and light are on the same circuit. When you plug in a hair dryer that uses more electricity then the bulb the bulb will dim. To fix this you need to call an electrician and have him put the lights on a separate circuit from the plugs.

User Avatar

Lights that don't workThis is caused by what is called an "open circuit condition."Open circuit conditions are caused by things like blown fuses, cut or broken wires, disconnected "connector" plugs, or corrosion buildup anywhere in any connections or connectors.

User Avatar

Electricians go with about 12 plugs or up to 15 combination of plugs and lights. Yet the way best way to calculate is by adding the total watts "if known" which will be used on the circuit. The max the NEC code allows is 80% of the circuit,s capacity. So 15 x .8 = 12 amp x 120V = 1440watts.

User Avatar

The size of circuit breaker you use for the plugs and geysers depends on the size of the house. Circuit breakers play an important role in homes in keeping electricity supplied.

User Avatar

They are parallel. Each plug is in parallel with the other plugs.

User Avatar

Check the fuse again; tailights and dash lights are fused together on most vehicles. You need to pull fuse and test with a circuit tester and test both sides where the fuse plugs in.

User Avatar

You will need an electrician. Tim is probably right in that unless you are knowledgable, call an electrican. Saying that, if you are knowledgable, you must install a GFCI circuit outdoors. This can be tied into an existing circuit if that circuit has no more than 9 existing lights & plugs already connected. Use 12/2 with ground wiring.

User Avatar

Yes, up to a combination of 12 devices. Devices include receptacles, switches and light outlets. Each outlet box counts as one device

User Avatar

The trailer plug in the Jeep may be wired wrong. Make sure the tail light plug is connected to the jeep taillight circuit. Some trailer plugs include a "hot" wire that allows the trailer to run a few accessories. Your trailer tail lights may be connected to that circuit.

User Avatar

Electricity is supplied around the house through a service distribution panel. From this panel specific circuit are wired to supply power to plugs, lights and appliances. Each circuit is protected by a breaker that is located in the distribution panel. These breakers vary in trip values to accommodate the load wattage's of different appliances that are connected to the circuit.

User Avatar

The hazard lights are a seprate circuit even though they share the same bulbs. I would first replace the hazard flasher; it simply plugs in. Usually the hazard flasher is located in the interior fuse panel. I hope this helps you. Mark

User Avatar

If you have used several strands of lights, make sure the plugs are plugged in securely. If the plugs are plugged in, check the bulbs. With some types of lights, if one bulb is burned out, left out, or loose, the entire strand will not light. If the bulbs are all working, it is probably time to buy a new strand of lights.

User Avatar

according to electrical code, a maximum on 12 outlets on a branch circuit unless the loads are known.

User Avatar

Deoends on code you are governed by. In USA, a GFCI outlet or a circuit controlled by a GFCI circuit breaker would be required.

User Avatar

You can put one end at the top and spin the lights around and around the tree until the tree is covered in lights. Then you plug in the end at the bottom!

User Avatar

Don't Understand your question, all of your circuit breakers start at the load center and then branch out to your recepticles(plugs) ETC.

User Avatar

You may have disconnected the earth return or battery wire for the brake lights. This is only a possible solution if the brake lights do not use the frame as an earth return directly adjacent to the brake light housing. Normally the switch operated by the brake pedal or lever connects and earth to the brake circuit to light the brake lamp.

User Avatar

In the United States, commercial and industrial installations are limited to 13 receptacles on a 20 amp circuit, 10 receptacles on a 15 amp circuit. There is no limit for residential installations.

User Avatar

It depends on what type of Christmas lights. If they are the (now) standard 50 , 100, 150, mini-lights, they use a 3A fuse and you COULD use a MAXIMUM of about 750 lights if they are strung together from one string (end to end plugs) before blowing the fuse built into the plug of the first light set. If you plug them into separate outlets (or into an outlet-strip), then you could light about 3750 lights on a (otherwidse unused) 15 A household circuit. With the new LED type Christmas lights, it might be even more.

User Avatar

They started to turn off the lights when not needed and to unplug the plugs when not using.

User Avatar

If electrical plugs had only one prong, nothing would happen. Electricity would not complete a circuit. Nothing would work.


Copyright ยฉ 2020 Multiply Media, LLC. All Rights Reserved. The material on this site can not be reproduced, distributed, transmitted, cached or otherwise used, except with prior written permission of Multiply.