A 12 AWG wire would give you approximately 2.6 percent drop, which is less than the maximum allowable voltage drop. 14 AWG would drop you 10 volts (4.2 percent), which is still workable until you factor in the 80 percent design factor (i.e., you are only allowed to run a circuit at 80 percent of its design capacity).
If you REALLY need 15 amps, you have to design for 18.75 amps (which works out to a 14 AWG voltage drop of over 5 percent, which is not allowed), so you would need to use the larger wire (12 AWG) for a 3.3 percent drop.
More information is needed. The voltage and current that are required will have a significant effect on the wire size needed. In general a higher current requires thicker wire.
If the voltage is higher, e.g. 240 v instead of 120 v, the current drawn will be less for a given kilowatt load and that allows thinner wire.
First calculate the voltage drop allowed: 5% of 220 v is 11 v. Divide by the current to find the resistance: 11/25 is 0.44 ohms.
The total wire length is 500 ft or 152.4 metres so the resistance allowed per metre is 0.44/152.5 or 0.00288 ohms/m.
Copper wire of 1 mm2 is 0.0168 ohms per metre so the wire size required is a minimum of 0.0168/0.00288 mm2, which is 5.82 mm2. Therefore 6 mm2 cable should be used and this size of cable is a common one in Europe. The nearest suitable AWG size is #9 but #8 is probably commoner.
It is more important to know what the amps that are going to be required. That will determine what gauge wire to use.
If you combine two 110 volt power lines it does not give you 220 volts, the voltage will be the same. The only way to turn 110 volts into 220 volts is with a step-up transformer.
Mine was 220 and I suppose they all are.
6 AWG
Typically they are either 220V or 110 volts not both. Plugging a 11o volt blanket to a 220 volt line has a huge risk of fire.
No !
If you combine two 110 volt power lines it does not give you 220 volts, the voltage will be the same. The only way to turn 110 volts into 220 volts is with a step-up transformer.
Mine was 220 and I suppose they all are.
# 3 gauge
6 AWG
No !
Typically they are either 220V or 110 volts not both. Plugging a 11o volt blanket to a 220 volt line has a huge risk of fire.
no
A 220 volt treadmill will not run on 110 volt power. if you would wire it to plug in, the low voltage would causes the treadmill to burn up. You will need to install a 220 volt receptacle for it to plug into and work properly. <<>> In the above answer the treadmill will not burn up but at these amperages it will make a very big flash if it shorted out. Also it must be some treadmill to draw 220 amps and I have never seen a 110 amp wall socket.
no
France uses 220-240 volts for their electrical system.
You need a step down voltage transformer that converts 220 volt to 110 volt to use a 110 volt printer with 220 volt. You can get good quality transformers at East West International in Houston, TX. If you order online or over the phone, they can ship it to you in 2-3 business days.
No, unless it is dual rated for 110 - 220 volt use. Check the manual or look at the rating sticker that should be somewhere on the printer.