Answer for USA, Canada and countries running a 60 Hz supply service.THHN 6 gauge is rated at 75 amps at 240. I ran it through a 2 1/2' conduit and it works great. You will need a real wire puller to get it through though, this fishline or string stuff just won't pull 4 stands of 6 gauge around any corners at all.

<><><>

I would recommend 6ga for runs under 75ft, 4ga for under 150, and 2 for under 225.

<><><>

Ok #6 is good for 65 Amp @ 75degC. I know the table for thhn wire shows #6 is good for 75 Amp @ 90degC. But you can not use that column. You have to use the 75degC column. The reason for using the 75degC column is the terminations (wire lugs) (circuit breakers) (wire nuts) (etc.) are only rated 75degC. not 90degC. You have to use the weakest link as the max. If one of the terminals in the circuit were rated 60degC then #6 thhn wire would be good for 55amp @ 60degC. You must not run hotter than the rating!

<><><>

(by - tbcguy) I am a Licensed Electrician, and have been in the trade for 22 yrs.

As mentioned above you Cannot use the 90degC column for the above mentioned reasons.

** Also note the 65amp rating is the maximum @ the 75degC column, but the STANDARD size "Breaker" is 60 amps, so you would drop down the rating of the 6 awg wire to 60a maximum load.

<><

As always, if you are in doubt about what to do, the best advice anyone should give you is to call a licensed electrician to advise what work is needed.

Before you do any work yourself,

on electrical circuits, equipment or appliances,

always use a test meter to ensure the circuit is, in fact, de-energized.

IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOB

SAFELY AND COMPETENTLY

REFER THIS WORK TO QUALIFIED PROFESSIONALS.

User Avatar

Wiki User

βˆ™ 2010-12-15 23:55:42
This answer is:
πŸ€“
🀯
πŸ€”
User Avatar

Your Answer

Loading...

Related Questions

What gauge wire do you need for 220V 75A power?

3 AWG


What gauge wire do you need for 220V 30A power?

In order to safely run 30 amps of electricity, a minimum of a #10 gauge wire is needed. For longer runs of wire, #8 gauge is better.


What gauge wire do you need for 220V 30amp?

10 AWG.


What gauge wire do you need for 220v 100a power?

A 100 amp residential panel requires that you use AWG # 3 service entrance wire.


What gauge wire do you need for a water heater?

30 amp 220v circuit requires #10 wire


What is the gauge of wire for a 13.8 dc power cords?

You need to know the current to determine the wire gauge.


What gauge wire is needed to supply a 220v 50' 30amp service?

10 AWG.


What gauge is use on low votage?

The lower the voltage the larger gauge wire you will need to get the same power.


What size gauge power wire do you need for a 4000 watt amp?

2 or 4


What gauge wire is required for a 220V welder outlet with 2 30 amp breakers in the breaker box?

10 AWG.


What is a good wire gauge for a car radio?

A good wire gauge for car radios is 18 gauge. This wire runs between the radio and its power supply from the vehicle.


Is an audio signal affected by wire gauge?

Absolutely for maximum power transfer impedance's are to be matched a low wire gauge will insure that the power is not dissipated on the wire as appose in the speakers.


You are hooking up a 220v air conditioner you were told to use 10-2 wire how do you hook this up?

10-2 wire refers to 10 gauge, 2 conductor wire. Youshould use wire that is 10 gauge or larger (8 gauge, 6 gauge, 4 gauge, 2 gauge). The larger the wire, the more it will cost. most people install using the smallest size permitted, which in this case is 10 gauge. The are specifying the wire size to ensure that you do not connect the air conditioner to electric power using wire that is two small. If you are having problems with this type of question, you should consult an licensed electrician for help in connecting your air conditioner.


Electric range 220 or 110?

Electrical range is usually 220V and requires at least a 40A breaker. In a three wire configuration, the white power carries 110V, the black wire carries 220V and the green wire is the ground. A four wire configuration has an additional wire that is neutral.


How do you wire a 220v three prong to a 220v four prong?

Two hots, a neutral and a grounding wire.


What is the orange wire on your fuel pump harness for a 1990 ford f150 used for Is it a power wire?

It is the ground wire for the fuel pump. The Red wire is the power wire for the pump. the dark blue is the signal wire for the gauge and the black is the ground for the gauge.


What gauge wire do you need for amplifier?

It depends on where the wire is being used, but for the power supply for an ordinary domestic audio amplifier, wire of 0.75 mmsq is adequate, and need to be protected by a 5-amp fuse.


What gauge wire is needed to supply a 220v 100' 30amp service?

You would need a #8 copper wire insulation rating of 90 degrees C to supply 240 volts 100 feet to a 30 amp single phase load.


What size breaker do you need for a Whirlpool 4 cycle dryer?

It should take a two pole (220V) 50 amp breaker and matching plug wired with # 8 or # 6 gauge wire. Check your manual.


What gauge wire do you need for a 34.539 milliampere?

34.539 miliamps is only 0.034539 amps. A 16 gauge wire will handle that.


What size gauge power wire do you need for a 800 watt amp?

4 gauge although i think you could use 8 but i have my 800 watt amp to a 4 gauge so just go with that


What wire gauge do you need for a small electric welder when runnung for a distance of 35 feet?

You need to provide the voltage it operates at and the power it draws in watts.


Which kind of wires will I need to hook up my Amp?

You'll need RCA style cables to connect from your headunit to the amp. You'll then need Speaker Wire to run from the outputs of the Amp to the speaker terminals. You'll also need a heavy gauge power wire. A wiring kit such as the StreetWires Power Station PSK04Ri 4-gauge amplifier wiring kit.


What gauge wire do you need for 12.5 amps?

14Awg


What wire size to run 60 AMP 220v 250 FT?

wire size to run 60 amp 220v 110 ft