A 3 phase motor does not require a neutral conductor because the impedances that make up the stator coils are of equal magnitude and it is what is known as a balanced 3 phase load. If the loads of a wye connected 3 phase system were unbalanced, i.e. the load currents in each of the 3 phases are different, then the unbalanced currents would require a return path to the service transformer via a neutral conductor. The neutral conductor is the transformer centre tap and is usually earthed locally.

ANOTHER ANSWER

The impedance of each phase winding of a three phase motor is identical (we call it a 'balanced load'). For a star (wye) connected motor, the phasor sum of three identical phase currents is zero, so no current will flow through a neutral, so a neutral isn't required. For a delta-connected motor, there is no provision for a neutral.

User Avatar

Wiki User

10y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

13y ago

This is because the impedances that make up the stator coils are of equal impedance and it is what is known as a balanced 3 phase load. If the 3 loads of a wye connected 3 phase system were unbalanced, i.e. the load currents in each phase are different, then the unbalanced currents would require a return path to the service transformer via a neutral conductor.

This answer is:
User Avatar

User Avatar

Wiki User

11y ago

The answer that three phase motors are more efficient than single phase motors and require less power to perform the work load required.

To put it in simple terms, the poles in a single phase motor are 180 degrees apart to match the sign wave of single phase current. The poles in a three phase motor are only 120 degrees apart. Therefore, the motor only needs to turn 120 degrees before it receives its next pulse of electricity whereas the single phase motor must turn 180 degrees which requires more initial energy.

This answer is:
User Avatar

User Avatar

Wiki User

12y ago

3 phase motors don't have a neutral. Your power line in will have a ground and 3 hot wires, L1, L2 and L3. The motor will have 9 wires, T1, T2, T3 etc... The 3 phase motor can be wired up for high voltage or low voltage depending on power supply coming in. Wire up motor for proper configuration ( usually a little wiring diagram on motor / jbox) and check that motor runs in proper direction. If not switch any 2 of the 3 line wires coming in and direction will change.

This answer is:
User Avatar

User Avatar

Wiki User

11y ago

A neutral wire is used to carry the returning current from electrical equipment back to the source of supply. In a 3 phase system the sine waves on each phase are shifted 120 degrees. So for a balanced 3 phase load, such as a motor, the current to the motor is carried by two phases and the returning current by the other phase.

This answer is:
User Avatar

User Avatar

Wiki User

9y ago

neutral is only used for single phase motor's.Where we used three phase's in a motor this motor can't use neutral. Three phase motor's inside connected to the rotor and stater.

Answer

If the motor's windings are delta connected, then there is no neutral conductor. If the windings are connected in star (wye) then, because the windings represent a balanced load, there is no neutral current (the sum of the phase currents is zero for a balanced load) -so a neutral conductor would serve no purpose.

This answer is:
User Avatar

User Avatar

Wiki User

11y ago

As the phase windings of a three-phase motor are identical, it is considered to be a 'balanced' load. The phasor sum (i.e. the neutral current) of the phase currents in a star or wye connected load is zero, so there is no need for a neutral.

This answer is:
User Avatar

User Avatar

Wiki User

13y ago

A three phase motor uses phase to phase voltage in its operation.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Why neutral not conect in 3phase motor?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What is the Max amp rating for 3phase dc motor?

the three phase dc motor never seen yet motor eaither 3phase m/r or dc motor.


Which starter is best for 7.5 hp 3phase motor?

Which starter is best for 7.5 hp 3phase motor?Read more: Which_starter_is_best_for_7.5_hp_3phase_motor


You switched leads on your 3phase motor and it did not reverse?

Then it is not a three phase motor.


How do you convert 3phase 1hp motor into units?

Into units of what?


What size of wire use for 3kw motor 380volts 3phase?

How to calculate a cable size of 3kw motor


Can a 220 volt 3 phase motor be connected to a 208 3phase curcit?

Yes.


Can a 415volt 3phase motor run on 525 volt 3 phase?

It is not advisable to run lower voltage motor on a higher voltage.


What is the cable size for 1.5KW 3 phase induction motor?

Sir, what is the cable size for 1.5kw 3phase induction motor 400v?


What is the amperage and kw of a 75hp 380v 3phase 50hz motor...same for 25hp and 1hp?

100


How can you operate a electric motor rated at 400V 3phase 50Hz on a 400V 3phase 60Hz system?

Yes, however, the RPM will increase by 20%, if the motor is connected to a shaft or driving something that can not handle the torque, then you might run to heating issues or performance issues.


How can you operate a electric motor rated at 400V 3phase 50Hz on a 480V 3phase 60Hz system?


How many AMPs does a 7.5HP motor need?

depending on 1phase or 3phase voltage motor , the amphere requirement is found outfor 3phase AC motor use this formula: (HP x 746)/(1.73 x E x Eff x PF)for 1phase AC motor : (HP x 746) / (E x Eff x PF)