answersLogoWhite

0

Cable sizing is based on load amperage. The formula you need to use is Amps = Watts/Volts. Amps = 1000/220 = 4.55 amps. A #14 copper wire with a insulation factor of 60, 75 and 90 degrees C is rated at 15, 15 and 15 amps respectively.

User Avatar

Wiki User

11y ago

What else can I help you with?

Related Questions

What cable wire size for 1000 watts aircondition?

The only way to determine the cable wire size needed for a 1000 watt air conditioner is to find the load size. To get the load size you will need to use the formula Amps = Watts or Volts. With that being said, you will need a number 14 copper wire.


What size hot wire do you need for a 1900 watt amp?

A 12 gauge wire can support a load of approximately 2200 watts.


What size wire for 55kw?

Wire is sized by the amperage that it will carry. 5 kW is 5000 watts. The equation to find watts is W = Amps x Volts. The equation to find amps is Amps = Watts/Volts. As you can see a voltage is needed to calculate the amperage. Once the amperage is stated, the wire size can be given for that particular amperage.


How many watts do you need in a PA system for 5000-10000 people?

For a crowd of 5000-10000 people, you would typically need a PA system with at least 10000-20000 watts of power to ensure sufficient coverage and volume. It's also important to consider the size of the venue, acoustics, and the type of event when determining the wattage needed for a PA system.


What size wire do you need to run to a new flattop range using 32 feet of wire?

Wire size is based on the current draw of the device. It can be obtained from the wattage of the device by dividing the watts by the voltage. Once you have the current re ask the question.


What size breaker do you need for 5.7kw neff oven?

A breaker is sized by the wire size. The wire is sized by the amperage. The formula for amperage is I = W/E. Amps = Watts/Volts. As you can see with no voltage stated an answer can not be given.


How many amp in 10000 watt 220 volt?

10000 watts / 220 volts = 45.4545 amperes


What gauge wire will you need for a 400 watt amp?

To answer this question a voltage needs to be stated. The formula needed to find the amperage is I = W/E. Amps = Watts/Voltage. Once the amperage is found, the proper size conductor to handle that current can be established. Without knowing the amperage on 400 watts a good guess would be a #14 wire. This wire size is good up to 1440 watts at 120 volts.


How many amps are produced by 10000 watts at 240 volts?

41.666 amps. Divide watts by volts.


What size ground wire for a 30 kva transformer?

The size of grounding wire is based on the amperage output of the transformer. The voltage of the transformer needs to be stated. Without this voltage a calculation can not be made. Amps = Watts/Volts = 30000/?.


What size cable is needed for 7.2KW oven?

To answer this question a voltage needs to be stated. Wire sizing is based on amperage that the wire can safely conduct. I = W/E. Amps = Watts/Volts.


What size wire do you need for 650 watts?

To answer this question a voltage needs to be stated. Wire is sized by the amount of amperage the load takes. W = Amps x Volts. Amps = 650/ volts.