If the generator is 3-phase 120/208 v. it produces 104.21amps per phase using the formula 30,000 / (1.73 x 208 x .80). If it is 277/480 v. It gives 45.18 amps. A singlephase generator will give 125 amps at 240 volts and 62.5 amps at 480v.

User Avatar

Wiki User

14y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

9y ago

A 415 v three phase system has a line-to neutral voltage of 240 v on each of the three phase wires. Each wire supplies 250,000/3 or 83,333 VA so the current is 83,333 / 240 or 347 amps.

The current in each live wire is 347 amps. If a balanced load was delta-connected to it, the load current would be 200 amps at 415 volts.

Another Answer I suspect that you are really asking what the line current, rather than the phase current, would be.... however,

Assuming the machine is supplying a balanced load, to find out the line current (and, therefore, the phase current, in the case of a star-connected machine), you simply divide the kVA by (1.732 x line voltage):

current = (250 000) / (1.732 x 415) = 347 A.

This equation applies to both star and delta connections, so If the machine was delta connected, it would supply exactly the same line current, but the load current would be the line current divided by 1.732, or 200 A.

This answer is:
User Avatar

User Avatar

Wiki User

13y ago

Use the formula, amperage when kva is shown; I = kva x 1000 / 1.73 x volts.

This answer is:
User Avatar

User Avatar

Wiki User

14y ago

Here, power p=2000kva

v=550 v

Now P= 1.73*V*I*COS(PHY)

ASSUMING POWER FACTOR IS UNITY HENCE COS=1

HENCE I=(2000*1000)/(1.73*550*1)

=2101AMP

This answer is:
User Avatar

User Avatar

Wiki User

11y ago

Amps/3*0.8=(kva*1000)/(1.73*volts)

220v 380v

250kva 175amp 101amp

This answer is:
User Avatar

User Avatar

Wiki User

9y ago

For a 415 v three-phase generator the current is 278 amps for 200 kVA.

This answer is:
User Avatar

User Avatar

Wiki User

9y ago

To answer this question correctly, the voltage of the generator must be given.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How many amps for 250 kva generator per phase at 415v?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How many amps will a 240 volt single phase 15 kva generator supply?

62.5 amps


How many amps does a 18000 watt generator supply at 240 volts?

75 Amps theoretically Need to know if the generator is 3 phase or single phase.


How many amps for 1010 KVA generator per phase?

To answer this question the voltage of the generator must be given.


How many output amps is a 75 KVA generator single phase?

The formula you are looking for is , A = kva x 1000/Volts.


How many amps will a 240 volt single phase 20KW generator supply?

Typically 75 amps on natural gas, 85 amps using propane. Peak amps(for less than a second) to start a big appliance, like an A/C condenser, are 130.


How many output amps is a 75 KVA generator?

It depends upon the Generator system voltage. For 3 Phase, 600 Volt system, it will be 73 Amps For 3 Phase, 480 Volt system, it will be 90 Amps For 3 Phase, 208 Volt system, it will be 208 Amps


How many amps on 3 phase 225 amp panelboard each phase?

It means 225 amps on each phase.


How many amperes for 3 phase 220v 5 tonner?

50 Amps Single Phase 20 Amps Three Phase


How many amps is 8500 watts generator?

The equation that you are looking for is I = W/E. Amps = Watts/Volts. The generator has the capacity to supply 25 amps. Of course the load is what governs the amount of amperage drawn. Any load greater than 25 amps will load the generator down and probably trip the generator's breaker.


How many amps does a 5500 watt generator uses?

A generator does not use amps it generates amperage. To answer this question the generators voltage must be stated.


How many amps is 5.5KVA generator good for?

5.5kva


How many watt generator to run a 150 amp service?

You will need a 50 kW generator for a single phase 120/240 volt service.