A device to open or close an electric power circuit either during normal power system operation or during abnormal conditions. A circuit breaker serves in the course of normal system operation to energize or deenergize loads. During abnormal conditions, when excessive current develops, a circuit breaker opens to protect equipment and surroundings from possible damage due to excess current. These abnormal currents are usually the result of short circuits created by lightning, accidents, deterioration of equipment, or sustained overloads.
Formerly, all circuit breakers were electromechanical devices. In these breakers a mechanism operates one or more pairs of contacts to make or break the circuit. The mechanism is powered either electromagnetically, pneumatically, or hydraulically. The contacts are located in a part termed the interrupter. When the contacts are parted, opening the metallic conductive circuit, an electric arc is created between the contacts. This arc is a high-temperature ionized gas with an electrical conductivity comparable to graphite. Thus the current continues to flow through the arc. The function of the interrupter is to extinguish the arc, completing circuit-breaking action.
In oil circuit breakers, the arc is drawn in oil. The intense heat of the arc decomposes the oil, generating high pressure that produces a fluid flow through the arc to carry energy away. At transmission voltages below 345 kV, oil breakers used to be popular. They are increasingly losing ground to gas-blast circuit breakers such as air-blast breakers and SF6 circuit breakers.
In air-blast circuit breakers, air is compressed to high pressures. When the contacts part, a blast valve is opened to discharge the high-pressure air to ambient, thus creating a very-high-velocity flow near the arc to dissipate the energy. In SF6 circuit breakers, the same principle is employed, with SF6 as the medium instead of air. In the “puffer” SF6 breaker, the motion of the contacts compresses the gas and forces it to flow through an orifice into the neighborhood of the arc. Both types of SF6 breakers have been developed for ehv (extra high voltage) transmission systems.
Two other types of circuit breakers have been developed. The vacuum breaker, another electromechanical device, uses the rapid dielectric recovery and high dielectric strength of vacuum. A pair of contacts is hermetically sealed in a vacuum envelope. Actuating motion is transmitted through bellows to the movable contact. When the contacts are parted, an arc is produced and supported by metallic vapor boiled from the electrodes. Vapor particles expand into the vacuum and condense on solid surfaces. At a natural current zero the vapor particles disappear, and the arc is extinguished. Vacuum breakers of up to 242 kV have been built.
The other type of breaker uses a thyristor, a semiconductor device which in the off state prevents current from flowing but which can be turned on with a small electric current through a third electrode, the gate. At the natural current zero, conduction ceases, as it does in arc interrupters. This type of breaker does not require a mechanism. Semiconductor breakers have been built to carry continuous currents up to 10,000 A.
| Computer Desktop Encyclopedia: circuit breaker |
A protective device that opens a circuit upon sensing a current overload. Unlike a fuse, it can be reset.
Download Computer Desktop Encyclopedia to your iPhone/iTouch
| Investment Dictionary: Circuit Breaker |
Refers to any of the measures used by stock exchanges during large sell-offs to avert panic selling. Sometimes called a "collar."
Investopedia Says:
After an index has fallen a certain percentage, the exchange might activate trading halts or restrictions on program trading. For example, if the Dow Jones Industrial Average falls by 10%, the NYSE might halt market trading for one hour. There are other circuit breakers for 20% and 30% falls.
Related Links:
Find out what it means when investors are selling off their stocks for safer investments. Panic Selling - Capitulation Or Crash?
From a tulip craze to a dotcom bubble, read the cautionary tales of the stock market's greatest disasters. The Greatest Market Crashes
Investors of course are human, but find out here how our bad habits can cause market turbulence. How Investors Often Cause The Market's Problems
| Financial & Investment Dictionary: Circuit Breakers |
Measures instituted by the major stock and commodities exchanges to halt trading temporarily in stocks and stock index futures when the market has fallen by an amount based on specified percentage declines in a specified period. For example, circuit breakers instituted at the New York Stock Exchange in spring 1998 halt stock trading when the Dow Jones Industrial Average falls 10%, 20%, and 30%, with the point settings revised quarterly on the first day of January, April, July, and October. Circuit breakers were originally instituted after Black Monday in 1987 and modified following another sharp market drop in October 1989. They are subject to change from time to time, but may include trading halts, curtailment of automated trading systems, and/or price movement limits on index futures. Their purpose is to prevent a market free-fall by permitting a rebalancing of buy and sell orders. See also Curbs In; Program Trading.
| Architecture: circuit breaker |
An electric device for opening and closing a circuit, designed to open the circuit automatically upon flow of a predetermined value of abnormally high current; may be repeatedly reclosed and reused as an automatic over-current protection device without replacement of any components.
| Columbia Encyclopedia: circuit breaker |
| Electronics Dictionary: circuit breaker |
A protective device used to open a circuit when current exceeds a maximum value. In effect a reusable fuse.
| Wikipedia: Circuit breaker |
A circuit breaker is an automatically-operated electrical switch designed to protect an electrical circuit from damage caused by overload or short circuit. Its basic function is to detect a fault condition and, by interrupting continuity, to immediately discontinue electrical flow. Unlike a fuse, which operates once and then has to be replaced, a circuit breaker can be reset (either manually or automatically) to resume normal operation. Circuit breakers are made in varying sizes, from small devices that protect an individual household appliance up to large switchgear designed to protect high voltage circuits feeding an entire city.
Contents |
An early form of circuit breaker was described by Edison in an 1879 patent application, although his commercial power distribution system used fuses.[1] Its purpose was to protect lighting circuit wiring from accidental short-circuits and overloads.
All circuit breakers have common features in their operation, although details vary substantially depending on the voltage class, current rating and type of the circuit breaker.
The circuit breaker must detect a fault condition; in low-voltage circuit breakers this is usually done within the breaker enclosure. Circuit breakers for large currents or high voltages are usually arranged with pilot devices to sense a fault current and to operate the trip opening mechanism. The trip solenoid that releases the latch is usually energized by a separate battery, although some high-voltage circuit breakers are self-contained with current transformers, protection relays, and an internal control power source.
Once a fault is detected, contacts within the circuit breaker must open to interrupt the circuit; some mechanically-stored energy (using something such as springs or compressed air) contained within the breaker is used to separate the contacts, although some of the energy required may be obtained from the fault current itself. Small circuit breakers may be manually operated; larger units have solenoids to trip the mechanism, and electric motors to restore energy to the springs.
The circuit breaker contacts must carry the load current without excessive heating, and must also withstand the heat of the arc produced when interrupting the circuit. Contacts are made of copper or copper alloys, silver alloys, and other materials. Service life of the contacts is limited by the erosion due to interrupting the arc. Mechanical circuit breakers are usually discarded when the contacts are worn, but power circuit breakers and high-voltage circuit breakers have replaceable contacts.
When a current is interrupted, an arc is generated. This arc must be contained, cooled, and extinguished in a controlled way, so that the gap between the contacts can again withstand the voltage in the circuit. Different circuit breakers use vacuum, air, insulating gas, or oil as the medium in which the arc forms. Different techniques are used to extinguish the arc including:
Finally, once the fault condition has been cleared, the contacts must again be closed to restore power to the interrupted circuit.
Mechanical low-voltage circuit breakers use air alone to extinguish the arc. Larger ratings will have metal plates or non-metallic arc chutes to divide and cool the arc. Magnetic blowout coils deflect the arc into the arc chute.
In larger ratings, oil circuit breakers rely upon vaporization of some of the oil to blast a jet of oil through the arc.[2]
Gas (usually sulfur hexafluoride) circuit breakers sometimes stretch the arc using a magnetic field, and then rely upon the dielectric strength of the sulfur hexafluoride (SF6) to quench the stretched arc.
Vacuum circuit breakers have minimal arcing (as there is nothing to ionize other than the contact material), so the arc quenches when it is stretched a very small amount (<2–3 mm). Vacuum circuit breakers are frequently used in modern medium-voltage switchgear to 35,000 volts.
Air circuit breakers may use compressed air to blow out the arc, or alternatively, the contacts are rapidly swung into a small sealed chamber, the escaping of the displaced air thus blowing out the arc.
Circuit breakers are usually able to terminate all current very quickly: typically the arc is extinguished between 30 ms and 150 ms after the mechanism has been tripped, depending upon age and construction of the device.
A circuit breaker must incorporate various features to divide and extinguish the arc.
The maximum short-circuit current that a breaker can interrupt is determined by testing. Application of a breaker in a circuit with a prospective short-circuit current higher than the breaker's interrupting capacity rating may result in failure of the breaker to safely interrupt a fault. In a worst-case scenario the breaker may successfully interrupt the fault, only to explode when reset.
Miniature circuit breakers used to protect control circuits or small appliances may not have sufficient interrupting capacity to use at a panelboard; these circuit breakers are called "supplemental circuit protectors" to distinguish them from distribution-type circuit breakers.
Many different classifications of circuit breakers can be made, based on their features such as voltage class, construction type, interrupting type, and structural features.
Low voltage (less than 1000 VAC) types are common in domestic, commercial and industrial application, include:
The characteristics of LV circuit breakers are given by international standards such as IEC 947. These circuit breakers are often installed in draw-out enclosures that allow removal and interchange without dismantling the switchgear.
Large low-voltage molded case and power circuit breakers may have electrical motor operators, allowing them to be tripped (opened) and closed under remote control. These may form part of an automatic transfer switch system for standby power.
Low-voltage circuit breakers are also made for direct-current (DC) applications, for example DC supplied for subway lines. Special breakers are required for direct current because the arc does not have a natural tendency to go out on each half cycle as for alternating current. A direct current circuit breaker will have blow-out coils which generate a magnetic field that rapidly stretches the arc when interrupting direct current.
Small circuit breakers are either installed directly in equipment, or are arranged in a breaker panel.
The 10 ampere DIN rail-mounted thermal-magnetic miniature circuit breaker is the most common style in modern domestic consumer units and commercial electrical distribution boards throughout Europe. The design includes the following components:
Magnetic circuit breakers use a solenoid (electromagnet) whose pulling force increases with the current. Certain designs utilize electromagnetic forces in addition to those of the solenoid. The circuit breaker contacts are held closed by a latch. As the current in the solenoid increases beyond the rating of the circuit breaker, the solenoid's pull releases the latch which then allows the contacts to open by spring action. Some types of magnetic breakers incorporate a hydraulic time delay feature using a viscous fluid. The core is restrained by a spring until the current exceeds the breaker rating. During an overload, the speed of the solenoid motion is restricted by the fluid. The delay permits brief current surges beyond normal running current for motor starting, energizing equipment, etc. Short circuit currents provide sufficient solenoid force to release the latch regardless of core position thus bypassing the delay feature. Ambient temperature affects the time delay but does not affect the current rating of a magnetic breaker.
Thermal magnetic circuit breakers, which are the type found in most distribution boards, incorporate both techniques with the electromagnet responding instantaneously to large surges in current (short circuits) and the bimetallic strip responding to less extreme but longer-term over-current conditions.
Circuit breakers are rated both by the normal current that are expected to carry, and the maximum short-circuit current that they can safely interrupt.
Under short-circuit conditions, a current many times greater than normal can exist (see prospective short circuit current). When electrical contacts open to interrupt a large current, there is a tendency for an arc to form between the opened contacts, which would allow the current to continue. Therefore, circuit breakers must incorporate various features to divide and extinguish the arc. In air-insulated and miniature breakers an arc chute structure consisting (often) of metal plates or ceramic ridges cools the arc, and magnetic blowout coils deflect the arc into the arc chute. Larger circuit breakers such as those used in electrical power distribution may use vacuum, an inert gas such as sulphur hexafluoride or have contacts immersed in oil to suppress the arc.
The maximum short-circuit current that a breaker can interrupt is determined by testing. Application of a breaker in a circuit with a prospective short-circuit current higher than the breaker's interrupting capacity rating may result in failure of the breaker to safely interrupt a fault. In a worst-case scenario the breaker may successfully interrupt the fault, only to explode when reset, injuring the technician.
International Standard IEC 60898-1 and European Standard EN 60898-1 define the rated current In of a circuit breaker for low voltage distribution applications as the current that the breaker is designed to carry continuously (at an ambient air temperature of 30 °C). The commonly-available preferred values for the rated current are 6 A, 10 A, 13 A, 16 A, 20 A, 25 A, 32 A, 40 A, 50 A, 63 A, 80 A and 100 A[3] (Renard series, slightly modified to include current limit of British BS 1363 sockets). The circuit breaker is labeled with the rated current in ampere, but without the unit symbol "A". Instead, the ampere figure is preceded by a letter "B", "C" or "D" that indicates the instantaneous tripping current, that is the minimum value of current that causes the circuit-breaker to trip without intentional time delay (i.e., in less than 100 ms), expressed in terms of In:
| Type | Instantaneous tripping current |
|---|---|
| B | above 3 In up to and including 5 In |
| C | above 5 In up to and including 10 In |
| D | above 10 In up to and including 20 In |
| K | above 8 In up to and including 12 In
For the protection of loads that cause frequent short duration (approximately 400 ms to 2 s) current peaks in normal operation. |
| Z | above 2 In up to and including 3 In for periods in the order of tens of seconds.
For the protection of loads such as semiconductor devices or measuring circuits using current transformers. |
When supplying a branch circuit with more than one live conductor, each live conductor must be protected by a breaker pole. To ensure that all live conductors are interrupted when any pole trips, a "common trip" breaker must be used. These may either contain two or three tripping mechanisms within one case, or for small breakers, may externally tie the poles together via their operating handles. Two pole common trip breakers are common on 120/240 volt systems where 240 volt loads (including major appliances or further distribution boards) span the two live wires. Three-pole common trip breakers are typically used to supply three-phase electric power to large motors or further distribution boards.
Two and four pole breakers are used when there is a need to disconnect the neutral wire, to be sure that no current can flow back through the neutral wire from other loads connected to the same network when people need to touch the wires for maintenance. Separate circuit breakers must never be used for disconnecting live and neutral, because if the neutral gets disconnected while the live conductor stays connected, a dangerous condition arises: the circuit will appear de-energized (appliances will not work), but wires will stay live and RCDs will not trip if someone touches the live wire (because RCDs need power to trip). This is why only common trip breakers must be used when switching of the neutral wire is needed.
Medium-voltage circuit breakers rated between 1 and 72 kV may be assembled into metal-enclosed switchgear line ups for indoor use, or may be individual components installed outdoors in a substation. Air-break circuit breakers replaced oil-filled units for indoor applications, but are now themselves being replaced by vacuum circuit breakers (up to about 35 kV). Like the high voltage circuit breakers described below, these are also operated by current sensing protective relays operated through current transformers. The characteristics of MV breakers are given by international standards such as IEC 62271. Medium-voltage circuit breakers nearly always use separate current sensors and protection relays, instead of relying on built-in thermal or magnetic overcurrent sensors.
Medium-voltage circuit breakers can be classified by the medium used to extinguish the arc:
With rated current up to 3000 A, these breakers interrupt the current by creating and extinguishing the arc in a vacuum container. These are generally applied for voltages up to about 35,000 V,[4] which corresponds roughly to the medium-voltage range of power systems. Vacuum circuit breakers tend to have longer life expectancies between overhaul than do air circuit breakers.
Medium-voltage circuit breakers may be connected into the circuit by bolted connections to bus bars or wires, especially in outdoor switchyards. Medium-voltage circuit breakers in switchgear line-ups are often built with draw-out construction, allowing the breaker to be removed without disturbing the power circuit connections, using a motor-operated or hand-cranked mechanism to separate the breaker from its enclosure.
Electrical power transmission networks are protected and controlled by high-voltage breakers. The definition of high voltage varies but in power transmission work is usually thought to be 72.5 kV or higher, according to a recent definition by the International Electrotechnical Commission (IEC). High-voltage breakers are nearly always solenoid-operated, with current sensing protective relays operated through current transformers. In substations the protection relay scheme can be complex, protecting equipment and busses from various types of overload or ground/earth fault.
High-voltage breakers are broadly classified by the medium used to extinguish the arc.
Some of the manufacturers are ABB, AREVA, Mitsubishi Electric, Pennsylvania Breaker, Siemens, Toshiba, Končar HVS, BHEL and others.
Due to environmental and cost concerns over insulating oil spills, most new breakers use SF6 gas to quench the arc.
Circuit breaker can be classified as "live tank", where the enclosure that contains the breaking mechanism is at line potential, or dead tank with the enclosure at earth potential. High-voltage AC circuit breakers are routinely available with ratings up to 765 kV.
High-voltage circuit breakers used on transmission systems may be arranged to allow a single pole of a three-phase line to trip, instead of tripping all three poles; for some classes of faults this improves the system stability and availability.
The following types are described in separate articles.
| Wikimedia Commons has media related to: Circuit breakers |
This entry is from Wikipedia, the leading user-contributed encyclopedia. It may not have been reviewed by professional editors (see full disclaimer)
| Best of the Web: circuit breaker |
Some good "circuit breaker" pages on the web:
How? home.howstuffworks.com |
| Shopping: circuit breaker |
| CKT BKR | |
| CIR BKR | |
| Collar (business term) |
Copyrights:
![]() | Dictionary. The American Heritage® Dictionary of the English Language, Fourth Edition Copyright © 2007, 2000 by Houghton Mifflin Company. Updated in 2009. Published by Houghton Mifflin Company. All rights reserved. Read more | |
![]() | Sci-Tech Encyclopedia. McGraw-Hill Encyclopedia of Science and Technology. Copyright © 2005 by The McGraw-Hill Companies, Inc. All rights reserved. Read more | |
![]() | Computer Desktop Encyclopedia. THIS COPYRIGHTED DEFINITION IS FOR PERSONAL USE ONLY. All other reproduction is strictly prohibited without permission from the publisher. © 1981-2009 Computer Language Company Inc. All rights reserved. Read more | |
![]() | Investment Dictionary. Copyright ©2000, Investopedia.com - Owned and Operated by Investopedia Inc. All rights reserved. Read more | |
![]() | Financial & Investment Dictionary. Dictionary of Finance and Investment Terms. Copyright © 2006 by Barron's Educational Series, Inc. All rights reserved. Read more | |
![]() | Architecture. McGraw-Hill Dictionary of Architecture and Construction. Copyright © 2003 by McGraw-Hill Companies, Inc. All rights reserved. Read more | |
![]() | Columbia Encyclopedia. The Columbia Electronic Encyclopedia, Sixth Edition Copyright © 2003, Columbia University Press. Licensed from Columbia University Press. All rights reserved. www.cc.columbia.edu/cu/cup/. Read more | |
![]() | Electronics Dictionary. Copyright 2001 by Twysted Pair. All rights reserved. Read more | |
![]() | Wikipedia. This article is licensed under the Creative Commons Attribution/Share-Alike License. It uses material from the Wikipedia article "Circuit breaker". Read more |