Share on Facebook Share on Twitter Email
Answers.com

circuit breaker

 
Dictionary: circuit breaker

n.
An automatic switch that stops the flow of electric current in a suddenly overloaded or otherwise abnormally stressed electric circuit.


Search unanswered questions...
Enter a question here...
Search: All sources Community Q&A Reference topics
Sci-Tech Encyclopedia: Circuit breaker
Top

A device to open or close an electric power circuit either during normal power system operation or during abnormal conditions. A circuit breaker serves in the course of normal system operation to energize or deenergize loads. During abnormal conditions, when excessive current develops, a circuit breaker opens to protect equipment and surroundings from possible damage due to excess current. These abnormal currents are usually the result of short circuits created by lightning, accidents, deterioration of equipment, or sustained overloads.

Formerly, all circuit breakers were electromechanical devices. In these breakers a mechanism operates one or more pairs of contacts to make or break the circuit. The mechanism is powered either electromagnetically, pneumatically, or hydraulically. The contacts are located in a part termed the interrupter. When the contacts are parted, opening the metallic conductive circuit, an electric arc is created between the contacts. This arc is a high-temperature ionized gas with an electrical conductivity comparable to graphite. Thus the current continues to flow through the arc. The function of the interrupter is to extinguish the arc, completing circuit-breaking action.

In oil circuit breakers, the arc is drawn in oil. The intense heat of the arc decomposes the oil, generating high pressure that produces a fluid flow through the arc to carry energy away. At transmission voltages below 345 kV, oil breakers used to be popular. They are increasingly losing ground to gas-blast circuit breakers such as air-blast breakers and SF6 circuit breakers.

In air-blast circuit breakers, air is compressed to high pressures. When the contacts part, a blast valve is opened to discharge the high-pressure air to ambient, thus creating a very-high-velocity flow near the arc to dissipate the energy. In SF6 circuit breakers, the same principle is employed, with SF6 as the medium instead of air. In the “puffer” SF6 breaker, the motion of the contacts compresses the gas and forces it to flow through an orifice into the neighborhood of the arc. Both types of SF6 breakers have been developed for ehv (extra high voltage) transmission systems.

Two other types of circuit breakers have been developed. The vacuum breaker, another electromechanical device, uses the rapid dielectric recovery and high dielectric strength of vacuum. A pair of contacts is hermetically sealed in a vacuum envelope. Actuating motion is transmitted through bellows to the movable contact. When the contacts are parted, an arc is produced and supported by metallic vapor boiled from the electrodes. Vapor particles expand into the vacuum and condense on solid surfaces. At a natural current zero the vapor particles disappear, and the arc is extinguished. Vacuum breakers of up to 242 kV have been built.

The other type of breaker uses a thyristor, a semiconductor device which in the off state prevents current from flowing but which can be turned on with a small electric current through a third electrode, the gate. At the natural current zero, conduction ceases, as it does in arc interrupters. This type of breaker does not require a mechanism. Semiconductor breakers have been built to carry continuous currents up to 10,000 A.


Computer Desktop Encyclopedia: circuit breaker
Top

A protective device that opens a circuit upon sensing a current overload. Unlike a fuse, it can be reset.

Download Computer Desktop Encyclopedia to your iPhone/iTouch

Investment Dictionary: Circuit Breaker
Top

Refers to any of the measures used by stock exchanges during large sell-offs to avert panic selling. Sometimes called a "collar."

Investopedia Says:
After an index has fallen a certain percentage, the exchange might activate trading halts or restrictions on program trading. For example, if the Dow Jones Industrial Average falls by 10%, the NYSE might halt market trading for one hour. There are other circuit breakers for 20% and 30% falls.

Related Links:
Find out what it means when investors are selling off their stocks for safer investments. Panic Selling - Capitulation Or Crash?
From a tulip craze to a dotcom bubble, read the cautionary tales of the stock market's greatest disasters. The Greatest Market Crashes
Investors of course are human, but find out here how our bad habits can cause market turbulence. How Investors Often Cause The Market's Problems


Financial & Investment Dictionary: Circuit Breakers
Top

Measures instituted by the major stock and commodities exchanges to halt trading temporarily in stocks and stock index futures when the market has fallen by an amount based on specified percentage declines in a specified period. For example, circuit breakers instituted at the New York Stock Exchange in spring 1998 halt stock trading when the Dow Jones Industrial Average falls 10%, 20%, and 30%, with the point settings revised quarterly on the first day of January, April, July, and October. Circuit breakers were originally instituted after Black Monday in 1987 and modified following another sharp market drop in October 1989. They are subject to change from time to time, but may include trading halts, curtailment of automated trading systems, and/or price movement limits on index futures. Their purpose is to prevent a market free-fall by permitting a rebalancing of buy and sell orders. See also Curbs In; Program Trading.

Architecture: circuit breaker
Top

An electric device for opening and closing a circuit, designed to open the circuit automatically upon flow of a predetermined value of abnormally high current; may be repeatedly reclosed and reused as an automatic over-current protection device without replacement of any components.


 
Columbia Encyclopedia: circuit breaker
Top
circuit breaker, electric device that, like a fuse, interrupts an electric current in a circuit when the current becomes too high. The advantage of a circuit breaker is that it can be reset after it has been tripped; a fuse must be replaced after it has been used once. When a current supplies enough energy to operate a trigger device in a breaker, a pair of contacts conducting the current are separated by preloaded springs or some similar mechanism. Generally, a circuit breaker registers the current either by the current's heating effect or by the magnetism it creates in passing through a small coil. Because it is usual for an electric arc to form between the contacts when a breaker opens, some means must be provided for preventing rapid erosion of the contacts. Normally this is done by opening the contacts fast enough to make the arc of short duration.


Electronics Dictionary: circuit breaker
Top

A protective device used to open a circuit when current exceeds a maximum value. In effect a reusable fuse.


Wikipedia: Circuit breaker
Top
Circuit breaker switchgear
A 2 pole miniature circuit breaker
Four 1 pole circuit breakers

A circuit breaker is an automatically-operated electrical switch designed to protect an electrical circuit from damage caused by overload or short circuit. Its basic function is to detect a fault condition and, by interrupting continuity, to immediately discontinue electrical flow. Unlike a fuse, which operates once and then has to be replaced, a circuit breaker can be reset (either manually or automatically) to resume normal operation. Circuit breakers are made in varying sizes, from small devices that protect an individual household appliance up to large switchgear designed to protect high voltage circuits feeding an entire city.

Contents

Origins

An early form of circuit breaker was described by Edison in an 1879 patent application, although his commercial power distribution system used fuses.[1] Its purpose was to protect lighting circuit wiring from accidental short-circuits and overloads.

Operation

All circuit breakers have common features in their operation, although details vary substantially depending on the voltage class, current rating and type of the circuit breaker.

The circuit breaker must detect a fault condition; in low-voltage circuit breakers this is usually done within the breaker enclosure. Circuit breakers for large currents or high voltages are usually arranged with pilot devices to sense a fault current and to operate the trip opening mechanism. The trip solenoid that releases the latch is usually energized by a separate battery, although some high-voltage circuit breakers are self-contained with current transformers, protection relays, and an internal control power source.

Once a fault is detected, contacts within the circuit breaker must open to interrupt the circuit; some mechanically-stored energy (using something such as springs or compressed air) contained within the breaker is used to separate the contacts, although some of the energy required may be obtained from the fault current itself. Small circuit breakers may be manually operated; larger units have solenoids to trip the mechanism, and electric motors to restore energy to the springs.

The circuit breaker contacts must carry the load current without excessive heating, and must also withstand the heat of the arc produced when interrupting the circuit. Contacts are made of copper or copper alloys, silver alloys, and other materials. Service life of the contacts is limited by the erosion due to interrupting the arc. Mechanical circuit breakers are usually discarded when the contacts are worn, but power circuit breakers and high-voltage circuit breakers have replaceable contacts.

When a current is interrupted, an arc is generated. This arc must be contained, cooled, and extinguished in a controlled way, so that the gap between the contacts can again withstand the voltage in the circuit. Different circuit breakers use vacuum, air, insulating gas, or oil as the medium in which the arc forms. Different techniques are used to extinguish the arc including:

  • Lengthening of the arc
  • Intensive cooling (in jet chambers)
  • Division into partial arcs
  • Zero point quenching[clarification needed]
  • Connecting capacitors in parallel with contacts in DC circuits

Finally, once the fault condition has been cleared, the contacts must again be closed to restore power to the interrupted circuit.

Arc interruption

Mechanical low-voltage circuit breakers use air alone to extinguish the arc. Larger ratings will have metal plates or non-metallic arc chutes to divide and cool the arc. Magnetic blowout coils deflect the arc into the arc chute.

In larger ratings, oil circuit breakers rely upon vaporization of some of the oil to blast a jet of oil through the arc.[2]

Gas (usually sulfur hexafluoride) circuit breakers sometimes stretch the arc using a magnetic field, and then rely upon the dielectric strength of the sulfur hexafluoride (SF6) to quench the stretched arc.

Vacuum circuit breakers have minimal arcing (as there is nothing to ionize other than the contact material), so the arc quenches when it is stretched a very small amount (<2–3 mm). Vacuum circuit breakers are frequently used in modern medium-voltage switchgear to 35,000 volts.

Air circuit breakers may use compressed air to blow out the arc, or alternatively, the contacts are rapidly swung into a small sealed chamber, the escaping of the displaced air thus blowing out the arc.

Circuit breakers are usually able to terminate all current very quickly: typically the arc is extinguished between 30 ms and 150 ms after the mechanism has been tripped, depending upon age and construction of the device.

Short circuit current

A circuit breaker must incorporate various features to divide and extinguish the arc.

The maximum short-circuit current that a breaker can interrupt is determined by testing. Application of a breaker in a circuit with a prospective short-circuit current higher than the breaker's interrupting capacity rating may result in failure of the breaker to safely interrupt a fault. In a worst-case scenario the breaker may successfully interrupt the fault, only to explode when reset.

Miniature circuit breakers used to protect control circuits or small appliances may not have sufficient interrupting capacity to use at a panelboard; these circuit breakers are called "supplemental circuit protectors" to distinguish them from distribution-type circuit breakers.

Types of circuit breaker

Front panel of a 1250 A air circuit breaker manufactured by ABB. This low voltage power circuit breaker can be withdrawn from its housing for servicing. Trip characteristics are configurable via DIP switches on the front panel.

Many different classifications of circuit breakers can be made, based on their features such as voltage class, construction type, interrupting type, and structural features.

Low voltage circuit breakers

Low voltage (less than 1000 VAC) types are common in domestic, commercial and industrial application, include:

  • MCB (Miniature Circuit Breaker)—rated current not more than 100 A. Trip characteristics normally not adjustable. Thermal or thermal-magnetic operation. Breakers illustrated above are in this category.
  • MCCB (Molded Case Circuit Breaker)—rated current up to 1000 A. Thermal or thermal-magnetic operation. Trip current may be adjustable in larger ratings.
  • Low voltage power circuit breakers can be mounted in multi-tiers in LV switchboards or switchgear cabinets.

The characteristics of LV circuit breakers are given by international standards such as IEC 947. These circuit breakers are often installed in draw-out enclosures that allow removal and interchange without dismantling the switchgear.

Large low-voltage molded case and power circuit breakers may have electrical motor operators, allowing them to be tripped (opened) and closed under remote control. These may form part of an automatic transfer switch system for standby power.

Low-voltage circuit breakers are also made for direct-current (DC) applications, for example DC supplied for subway lines. Special breakers are required for direct current because the arc does not have a natural tendency to go out on each half cycle as for alternating current. A direct current circuit breaker will have blow-out coils which generate a magnetic field that rapidly stretches the arc when interrupting direct current.

Small circuit breakers are either installed directly in equipment, or are arranged in a breaker panel.

Photo of inside of a circuit breaker

The 10 ampere DIN rail-mounted thermal-magnetic miniature circuit breaker is the most common style in modern domestic consumer units and commercial electrical distribution boards throughout Europe. The design includes the following components:

  1. Actuator lever - used to manually trip and reset the circuit breaker. Also indicates the status of the circuit breaker (On or Off/tripped). Most breakers are designed so they can still trip even if the lever is held or locked in the "on" position. This is sometimes referred to as "free trip" or "positive trip" operation.
  2. Actuator mechanism - forces the contacts together or apart.
  3. Contacts - Allow current when touching and break the current when moved apart.
  4. Terminals
  5. Bimetallic strip
  6. Calibration screw - allows the manufacturer to precisely adjust the trip current of the device after assembly.
  7. Solenoid
  8. Arc divider / extinguisher

Magnetic circuit breaker

Magnetic circuit breakers use a solenoid (electromagnet) whose pulling force increases with the current. Certain designs utilize electromagnetic forces in addition to those of the solenoid. The circuit breaker contacts are held closed by a latch. As the current in the solenoid increases beyond the rating of the circuit breaker, the solenoid's pull releases the latch which then allows the contacts to open by spring action. Some types of magnetic breakers incorporate a hydraulic time delay feature using a viscous fluid. The core is restrained by a spring until the current exceeds the breaker rating. During an overload, the speed of the solenoid motion is restricted by the fluid. The delay permits brief current surges beyond normal running current for motor starting, energizing equipment, etc. Short circuit currents provide sufficient solenoid force to release the latch regardless of core position thus bypassing the delay feature. Ambient temperature affects the time delay but does not affect the current rating of a magnetic breaker.

Thermal magnetic circuit breaker

Thermal magnetic circuit breakers, which are the type found in most distribution boards, incorporate both techniques with the electromagnet responding instantaneously to large surges in current (short circuits) and the bimetallic strip responding to less extreme but longer-term over-current conditions.

Rated circuits

Circuit breakers are rated both by the normal current that are expected to carry, and the maximum short-circuit current that they can safely interrupt.

Under short-circuit conditions, a current many times greater than normal can exist (see prospective short circuit current). When electrical contacts open to interrupt a large current, there is a tendency for an arc to form between the opened contacts, which would allow the current to continue. Therefore, circuit breakers must incorporate various features to divide and extinguish the arc. In air-insulated and miniature breakers an arc chute structure consisting (often) of metal plates or ceramic ridges cools the arc, and magnetic blowout coils deflect the arc into the arc chute. Larger circuit breakers such as those used in electrical power distribution may use vacuum, an inert gas such as sulphur hexafluoride or have contacts immersed in oil to suppress the arc.

The maximum short-circuit current that a breaker can interrupt is determined by testing. Application of a breaker in a circuit with a prospective short-circuit current higher than the breaker's interrupting capacity rating may result in failure of the breaker to safely interrupt a fault. In a worst-case scenario the breaker may successfully interrupt the fault, only to explode when reset, injuring the technician.

International Standard IEC 60898-1 and European Standard EN 60898-1 define the rated current In of a circuit breaker for low voltage distribution applications as the current that the breaker is designed to carry continuously (at an ambient air temperature of 30 °C). The commonly-available preferred values for the rated current are 6 A, 10 A, 13 A, 16 A, 20 A, 25 A, 32 A, 40 A, 50 A, 63 A, 80 A and 100 A[3] (Renard series, slightly modified to include current limit of British BS 1363 sockets). The circuit breaker is labeled with the rated current in ampere, but without the unit symbol "A". Instead, the ampere figure is preceded by a letter "B", "C" or "D" that indicates the instantaneous tripping current, that is the minimum value of current that causes the circuit-breaker to trip without intentional time delay (i.e., in less than 100 ms), expressed in terms of In:

Type Instantaneous tripping current
B above 3 In up to and including 5 In
C above 5 In up to and including 10 In
D above 10 In up to and including 20 In
K above 8 In up to and including 12 In

For the protection of loads that cause frequent short duration (approximately 400 ms to 2 s) current peaks in normal operation.

Z above 2 In up to and including 3 In for periods in the order of tens of seconds.

For the protection of loads such as semiconductor devices or measuring circuits using current transformers.

Common trip breakers

Three pole common trip breaker for supplying a three-phase device. This breaker has a 2 A rating

When supplying a branch circuit with more than one live conductor, each live conductor must be protected by a breaker pole. To ensure that all live conductors are interrupted when any pole trips, a "common trip" breaker must be used. These may either contain two or three tripping mechanisms within one case, or for small breakers, may externally tie the poles together via their operating handles. Two pole common trip breakers are common on 120/240 volt systems where 240 volt loads (including major appliances or further distribution boards) span the two live wires. Three-pole common trip breakers are typically used to supply three-phase electric power to large motors or further distribution boards.

Two and four pole breakers are used when there is a need to disconnect the neutral wire, to be sure that no current can flow back through the neutral wire from other loads connected to the same network when people need to touch the wires for maintenance. Separate circuit breakers must never be used for disconnecting live and neutral, because if the neutral gets disconnected while the live conductor stays connected, a dangerous condition arises: the circuit will appear de-energized (appliances will not work), but wires will stay live and RCDs will not trip if someone touches the live wire (because RCDs need power to trip). This is why only common trip breakers must be used when switching of the neutral wire is needed.

Medium-voltage circuit breakers

Medium-voltage circuit breakers rated between 1 and 72 kV may be assembled into metal-enclosed switchgear line ups for indoor use, or may be individual components installed outdoors in a substation. Air-break circuit breakers replaced oil-filled units for indoor applications, but are now themselves being replaced by vacuum circuit breakers (up to about 35 kV). Like the high voltage circuit breakers described below, these are also operated by current sensing protective relays operated through current transformers. The characteristics of MV breakers are given by international standards such as IEC 62271. Medium-voltage circuit breakers nearly always use separate current sensors and protection relays, instead of relying on built-in thermal or magnetic overcurrent sensors.

Medium-voltage circuit breakers can be classified by the medium used to extinguish the arc:

  • Vacuum circuit breaker—
File:AMVAC.jpg
15 kV Medium Voltage Vacuum Circuit Breaker manufactured by ABB.

With rated current up to 3000 A, these breakers interrupt the current by creating and extinguishing the arc in a vacuum container. These are generally applied for voltages up to about 35,000 V,[4] which corresponds roughly to the medium-voltage range of power systems. Vacuum circuit breakers tend to have longer life expectancies between overhaul than do air circuit breakers.

  • Air circuit breaker—Rated current up to 10,000 A. Trip characteristics are often fully adjustable including configurable trip thresholds and delays. Usually electronically controlled, though some models are microprocessor controlled via an integral electronic trip unit. Often used for main power distribution in large industrial plant, where the breakers are arranged in draw-out enclosures for ease of maintenance.
  • SF6 circuit breakers extinguish the arc in a chamber filled with sulfur hexafluoride gas.

Medium-voltage circuit breakers may be connected into the circuit by bolted connections to bus bars or wires, especially in outdoor switchyards. Medium-voltage circuit breakers in switchgear line-ups are often built with draw-out construction, allowing the breaker to be removed without disturbing the power circuit connections, using a motor-operated or hand-cranked mechanism to separate the breaker from its enclosure.

High-voltage circuit breakers

400 kV SF6 live tank circuit breakers
115 kV bulk oil circuit breaker

Electrical power transmission networks are protected and controlled by high-voltage breakers. The definition of high voltage varies but in power transmission work is usually thought to be 72.5 kV or higher, according to a recent definition by the International Electrotechnical Commission (IEC). High-voltage breakers are nearly always solenoid-operated, with current sensing protective relays operated through current transformers. In substations the protection relay scheme can be complex, protecting equipment and busses from various types of overload or ground/earth fault.

High-voltage breakers are broadly classified by the medium used to extinguish the arc.

  • Bulk oil
  • Vacuum Circuit Breaker
  • Minimum oil
  • Air blast
  • SF6

Some of the manufacturers are ABB, AREVA, Mitsubishi Electric, Pennsylvania Breaker, Siemens, Toshiba, Končar HVS, BHEL and others.

Due to environmental and cost concerns over insulating oil spills, most new breakers use SF6 gas to quench the arc.

Circuit breaker can be classified as "live tank", where the enclosure that contains the breaking mechanism is at line potential, or dead tank with the enclosure at earth potential. High-voltage AC circuit breakers are routinely available with ratings up to 765 kV.

High-voltage circuit breakers used on transmission systems may be arranged to allow a single pole of a three-phase line to trip, instead of tripping all three poles; for some classes of faults this improves the system stability and availability.

Sulfur hexafluoride (SF6) high-voltage circuit-breakers

Other breakers

The following types are described in separate articles.

  • Breakers for protections against earth faults too small to trip an over-current device:
    • Residual-current device (RCD, formerly known as a residual current circuit breaker) — detects current imbalance, but does not provide over-current protection.
    • Residual current breaker with over-current protection (RCBO) — combines the functions of an RCD and an MCB in one package. In the United States and Canada, panel-mounted devices that combine ground (earth) fault detection and over-current protection are called Ground Fault Circuit Interrupter (GFCI) breakers; a wall mounted outlet device providing ground fault detection only is called a GFI.
    • Earth leakage circuit breaker (ELCB) — This detects earth current directly rather than detecting imbalance. They are no longer seen in new installations for various reasons.
  • Autorecloser — A type of circuit breaker which closes again after a delay. These are used on overhead power distribution systems, to prevent short duration faults from causing sustained outages.
  • Polyswitch (polyfuse) — A small device commonly described as an automatically resetting fuse rather than a circuit breaker.

See also

References

  1. ^ Robert Friedel and Paul Israel, Edison's Electric Light: Biography of an Invention, Rutgers University Press, New Brunswick New Jersey USA,1986 ISBN 0-8135-1118-6 pp.65-66
  2. ^ B. M. Weedy, Electric Power Systems Second Edition, John Wiley and Sons, London, 1972, ISBN 0471924458 pp. 428-430
  3. ^ http://bonle.en.alibaba.com/product/50348671/51680889/Switch/MCB___MCCB.html
  4. ^ Few manufacturers offer now a single-bottle vacuum breaker rated up to 72.5 kV and even 145kV. See http://www3.interscience.wiley.com/journal/113307491/abstract?CRETRY=1&SRETRY=0 Electrical Engineering in Japan, vol 157 issue 4 pages 13-23
  • BS EN 60898-1. Electrical accessories — Circuit breakers for over-current protection for household and similar installations. British Standards Institute, 2003.

External links


Best of the Web: circuit breaker
Top

Some good "circuit breaker" pages on the web:


How?
home.howstuffworks.com
 
Shopping: circuit breaker
Top
 
 

 

Copyrights:

Dictionary. The American Heritage® Dictionary of the English Language, Fourth Edition Copyright © 2007, 2000 by Houghton Mifflin Company. Updated in 2009. Published by Houghton Mifflin Company. All rights reserved.  Read more
Sci-Tech Encyclopedia. McGraw-Hill Encyclopedia of Science and Technology. Copyright © 2005 by The McGraw-Hill Companies, Inc. All rights reserved.  Read more
Computer Desktop Encyclopedia. THIS COPYRIGHTED DEFINITION IS FOR PERSONAL USE ONLY.
All other reproduction is strictly prohibited without permission from the publisher.
© 1981-2009 Computer Language Company Inc.  All rights reserved.  Read more
Investment Dictionary. Copyright ©2000, Investopedia.com - Owned and Operated by Investopedia Inc. All rights reserved.  Read more
Financial & Investment Dictionary. Dictionary of Finance and Investment Terms. Copyright © 2006 by Barron's Educational Series, Inc. All rights reserved.  Read more
Architecture. McGraw-Hill Dictionary of Architecture and Construction. Copyright © 2003 by McGraw-Hill Companies, Inc. All rights reserved.  Read more
Columbia Encyclopedia. The Columbia Electronic Encyclopedia, Sixth Edition Copyright © 2003, Columbia University Press. Licensed from Columbia University Press. All rights reserved. www.cc.columbia.edu/cu/cup/ Read more
Electronics Dictionary. Copyright 2001 by Twysted Pair. All rights reserved.  Read more
Wikipedia. This article is licensed under the Creative Commons Attribution/Share-Alike License. It uses material from the Wikipedia article "Circuit breaker" Read more