(electricity) Process of transferring electric energy from one point to another in an electric power system.
| Sci-Tech Dictionary: electric power transmission |
(electricity) Process of transferring electric energy from one point to another in an electric power system.
| 5min Related Video: Electric power transmission |
| Sci-Tech Encyclopedia: Electric power transmission |
The transport of generator-produced electric energy to loads. An electric power transmission system interconnects generators and loads and generally provides multiple paths among them. Multiple paths increase system reliability because the failure of one line does not cause a system failure. Most transmission lines operate with three-phase alternating current (ac). The standard frequency in North America is 60 Hz; in Europe, 50 Hz. The three-phase system has three sets of phase conductors. Long-distance energy transmission occasionally uses high-voltage direct-current (dc) lines. See also Alternating current; Direct current; Direct-current transmission.
The electric power system can be divided into the distribution, subtransmission, and transmission systems. With operating voltages less than 34.5 kV, the distribution system carries energy from the local substation to individual households, using both overhead and underground lines. With operating voltages of 69-138 kV, the subtransmission system distributes energy within an entire district and regularly uses overhead lines. With operating voltage exceeding 230 kV, the transmission system interconnects generating stations and large substations located close to load centers by using overhead lines. See also Transmission lines.
Overhead alternating-current transmission
Overhead transmission lines distribute the majority of the electric energy in the system. A typical high-voltage line has three phase conductors to carry the current and transport the energy, and two grounded shield conductors to protect the line from direct lightning strikes. The usually bare conductors are insulated from the supporting towers by insulators attached to grounded towers or poles. Lower-voltage lines use post insulators, while the high-voltage lines are built with insulator chains or long-rod composite insulators. The normal distance between the supporting towers is a few hundred feet.
Transmission lines use ACSR (aluminum cable, steel reinforced) and ACAR (aluminum cable, alloy reinforced) conductors. In an ACSR conductor, a stranded steel core carries the mechanical load, and layers of stranded aluminum surrounding the core carry the current. An ACAR conductor is a stranded cable made of an aluminum alloy with low resistance and high mechanical strength. ACSR conductors are usually used for high-voltage lines, and ACAR conductors for subtransmission and distribution lines. Ultrahigh-voltage (UHV) and extrahigh-voltage (EHV) lines use bundle conductors. Each phase of the line is built with two, three, or four conductors connected in parallel and separated by about 1.5 ft (0.5 m). Bundle conductors reduce corona discharge. See also Conductor (electricity).
Transmission lines are subject to environmental adversities, including wide variations of temperature, high winds, and ice and snow deposits. Typically designed to withstand environmental stresses occurring once every 50–100 years, lines are intended to operate safely in adverse conditions.
Variable weather affects line operation. Extreme weather reduces corona inception voltage, leading to an increase in audible noise, radio noise, and telephone interference. Load variation requires regulation of line voltage. A short circuit generates large currents, overheating conductors and producing permanent damage.
The power that a line can transport is limited by the line's electrical parameters. Voltage drop is the most important factor for distribution lines; where the line is supplied from only one end, the permitted voltage drop is about 5%.
Conductor temperature must be lower than the temperature which causes permanent elongation. A typical maximum steady-state value for ACSR is 212°F (100°C), but in an emergency temperatures 10–20% higher are allowed for a short period of time (10 min to 1 h).
Corona discharge is generated when the electric field at the surface of the conductor becomes larger than the breakdown strength of the air. The oscillatory nature of the discharge generates high-frequency, short-duration current pulses, the source of corona-generated radio and television interference. Surface irregularities such as water droplets cause local field concentration, enhancing corona generation. Thus, during bad weather, corona discharge is more intense and losses are much greater. Corona discharge also generates audible noise with two components: a broad-band, high-frequency component, which produces crackling and hissing, and a 120-Hz pure tone. See also Corona discharge; Electrical interference.
Transmission-line conductors are surrounded by an electric field which decreases as distance from the line increases, and depends on line voltage and geometry. At ground level, this field induces current and voltage in grounded bodies, causes corona in grounded objects, and can induce fuel ignition. Utilities limit the electric field at the perimeter of right-of-ways to about 1000 V/m. An ac magnetic field around the transmission line also decreases with distance from the line. See also
Lightning strikes produce high voltages and traveling waves on transmission lines, causing insulator flashovers and interruption of operation. Steel grounded shield conductors at the tops of the towers significantly reduce, but do not eliminate, the probability of direct lightning strikes to phase conductors. See also Lightning and surge protection.
The operation of circuit breakers causes switching surges that can result in interruption of inductive current, energization of lines with trapped charges, and single-phase ground fault. Modern circuit breakers, operating in two steps, reduce switching surges to 1.5–2 times the 60-Hz voltage. See also Circuit breaker.
Line current induces a disturbing voltage in telephone lines running parallel to transmission lines. Because the induced voltage depends on the mutual inductance between the two lines, disturbance can be reduced by increasing the distance between the lines and shielding the telephone lines. See also Electrical shielding; Inductive coordination.
Underground power transmission
Most cities use underground cables to distribute electrical energy. These cables virtually eliminate negative environmental effects and reduce electrocution hazards. However, they entail significantly higher construction costs.
Underground cables are divided into two categories: distribution cables (less than 69 kV) and high-voltage power-transmission cables (69–500 kV).
Extruded solid dielectric cables dominate in the 15–33-kV urban distribution system. In a typical arrangement, the stranded copper or aluminum conductor is shielded by a semiconductor layer, which reduces the electric stress on the conductor's surface. Oil-impregnated paper-insulated distribution cables are used for higher voltages and in older installations.
Cable temperatures vary with load changes, and cyclic thermal expansion and contraction may produce voids in the cable. High voltage initiates corona in the voids, gradually destroying cable insulation. Low-pressure oil-filled cable construction reduces void formation. A single-phase concentric cable has a hollow conductor with a central oil channel. Three-phase cables have three oil channels located in the filler.
Submarine cables
High-voltage cables are frequently used for crossing large bodies of water. Water provides natural cooling, and pressure reduces the possibility of void formation. A typical submarine cable has cross-linked polyethylene insulation, and corrosion-resistant aluminum alloy wire armoring that provides tensile strength and permits installation in deep water. See also Electric power systems.
| Wikipedia: Electric power transmission |
Electric power transmission is the bulk transfer of electrical energy, a process in the delivery of electricity to consumers. A power transmission network typically connects power plants to multiple substations near a populated area. The wiring from substations to customers is referred to as electricity distribution, following the historic business model separating the wholesale electricity transmission business from distributors who deliver the electricity to the homes.[1] Electric power transmission allows distant energy sources (such as hydroelectric power plants) to be connected to consumers in population centers, and may allow exploitation of low-grade fuel resources such as coal that would otherwise be too costly to transport to generating facilities.
Usually transmission lines use three phase alternating current (AC). Single phase AC current is sometimes used in a railway electrification system. High-voltage direct current systems are used for long distance transmission, or some undersea cables, or for connecting two different AC networks.
Electricity is transmitted at high voltages (110 kV or above) to reduce the energy lost in transmission. Power is usually transmitted as alternating current through overhead power lines. Underground power transmission is used only in densely populated areas because of its higher cost of installation and maintenance when compared with overhead wires,and the difficulty of voltage control on long cables.
A power transmission network is referred to as a grid. Multiple redundant lines between points on the network are provided so that power can be routed from any power plant to any load center, through a variety of routes, based on the economics of the transmission path and the cost of power. Much analysis is done by transmission companies to determine the maximum reliable capacity of each line, which, due to system stability considerations, may be less than the physical or thermal limit of the line. Deregulation of electricity companies in many countries has led to renewed interest in reliable economic design of transmission networks. However, in some places the gaming of a deregulated energy system has led to disaster, such as that which occurred during the California electricity crisis of 2000 and 2001.[2]
Overhead conductors are not covered by insulation. The conductor material is nearly always an aluminium alloy, made into several strands and possibly reinforced with steel strands. Copper was sometimes used for overhead transmission but aluminium is lower in weight for equivalent performance, and much lower in cost. Overhead conductors are a commodity supplied by several companies worldwide. Improved conductor material and shapes are regularly used to allow increased capacity and modernize transmission circuits. Conductor sizes range from 12 mm2 (#6 American wire gauge) to 750 mm2 (1,590,000 circular mils area), with varying resistance and current-carrying capacity. Thicker wires would lead to a relatively small increase in capacity due to the skin effect, that causes most of the current to flow close to the surface of the wire.
Today, transmission-level voltages are usually considered to be 110 kV and above. Lower voltages such as 66 kV and 33 kV are usually considered sub-transmission voltages but are occasionally used on long lines with light loads. Voltages less than 33 kV are usually used for distribution. Voltages above 230 kV are considered extra high voltage and require different designs compared to equipment used at lower voltages.
Since overhead transmission lines are uninsulated, design of these lines requires minimum clearances to be observed to maintain safety. Adverse weather conditions of high wind and low temperatures can lead to power outages: wind speeds as low as 23 knots (43 km/h) can permit conductors to encroach operating clearances, resulting in a flashover and loss of supply.[3] Oscillatory motion of the physical line can be termed gallop or flutter depending on the frequency and amplitude of oscillation.
Electric power can also be transmitted by underground power cables instead of overhead power lines. They can assist the transmission of power across:
Some other advantages of underground power cables:
Some disadvantages of underground power cables:
The advantages can in some cases outweigh the disadvantages of the higher investment cost, and more expensive maintenance and management.
Most high voltage cables for power transmission that are currently sold on the market are insulated by a sheath of cross-linked polyethylene (XLPE). Some cable may have a lead or aluminium jacket in conjunction with XLPE insulation to allow for fiber optics to be seamlessly integrated within the cable.[clarification needed] Before 1960, underground power cables were insulated with oil and paper and ran in a rigid steel pipe, or a semi-rigid aluminium or lead jacket or sheath. The oil was kept under pressure to prevent formation of voids that would allow partial discharges within the cable insulation. There are still many of these oil-and-paper insulated cables in use worldwide. Between 1960 and 1990, polymers became more widely used at distribution voltages, mostly EPDM (ethylene propylene diene M-class); however, their relative unreliability, particularly early XLPE, resulted in a slow uptake at transmission voltages. While cables of 330 kV are commonly constructed using XLPE, this has occurred only in recent decades.
In the early days of commercial use of electric power, transmission of electric power at the same voltage as used by lighting and mechanical loads restricted the distance between generating plant and consumers. In 1882, generation was with direct current, which could not easily be increased in voltage for long-distance transmission. Different classes of loads (for example, lighting, fixed motors, and traction/railway systems) required different voltages, and so used different generators and circuits.[8]
Due to this specialization of lines and because transmission was so inefficient that generators needed to be close by their loads, it seemed at the time that the industry would develop into what is now known as a distributed generation system with large numbers of small generators located nearby their loads.[9]
In 1886 in Great Barrington, Massachusetts, a 1 kV AC distribution system was installed. That same year, AC power at 2 kV, transmitted 30 km, was installed at Cerchi, Italy. At an AIEE meeting on May 16, 1888, Nikola Tesla delivered a lecture entitled A New System of Alternating Current Motors and Transformers, describing the equipment which allowed efficient generation and use of polyphase alternating currents. The transformer, and Tesla's polyphase and single-phase induction motors, were essential for a combined AC distribution system for both lighting and machinery. Ownership of the rights to the Tesla patents was a key commercial advantage to the Westinghouse Company in offering a complete alternating current power system for both lighting and power.
Regarded as one of the most influential innovations for the use of electricity, the universal system used transformers to step-up voltage from generators to high-voltage transmission lines, and then to step-down voltage to local distribution circuits or industrial customers[10]. By a suitable choice of utility frequency, both lighting and motor loads could be served. Rotary converters and later mercury-arc valves and other rectifier equipment allowed DC load to be served by local conversion where needed. Even generating stations and loads using different frequencies could be interconnected using rotary converters. By using common generating plants for every type of load, important economies of scale were achieved, lower overall capital investment was required, load factor on each plant was increased allowing for higher efficiency, a lower cost for the consumer and increased overall use of electric power.
By allowing multiple generating plants to be interconnected over a wide area, electricity production cost was reduced. The most efficient available plants could be used to supply the varying loads during the day. Reliability was improved and capital investment cost was reduced, since stand-by generating capacity could be shared over many more customers and a wider geographic area. Remote and low-cost sources of energy, such as hydroelectric power or mine-mouth coal, could be exploited to lower energy production cost.[10]
The first transmission of three-phase alternating current using high voltage took place in 1891 during the international electricity exhibition in Frankfurt. A 25 kV transmission line, approximately 175 km long, connected Lauffen on the Neckar and Frankfurt.
Voltages used for electric power transmission increased throughout the 20th century. By 1914, fifty-five transmission systems each operating at more than 70 kV were in service. The highest voltage then used was 150 kV.[11]
The rapid industrialization in the 20th century made electrical transmission lines and grids a critical part of the economic infrastructure in most industrialized nations. Interconnection of local generation plants and small distribution networks was greatly spurred by the requirements of World War I, where large electrical generating plants were built by governments to provide power to munitions factories; later these plants were connected to supply civil load through long-distance transmission.[12]
Engineers design transmission networks to transport the energy as efficiently as feasible, while at the same time taking into account economic factors, network safety and redundancy. These networks use components such as power lines, cables, circuit breakers, switches and transformers.
Transmission efficiency is improved by increasing the voltage using a step-up transformer, which reduces the current in the conductors, while keeping the power transmitted nearly equal to the power input. The reduced current flowing through the conductor reduces the losses in the conductor and since, according to Joule's Law, the losses are proportional to the square of the current. Halving the current makes the transmission loss one quarter the original value.
A transmission grid is a network of power stations, transmission circuits, and substations. Energy is usually transmitted within the grid with three-phase AC. DC systems require relatively costly conversion equipment which may be economically justified for particular projects. Single phase AC is used only for distribution to end users since it is not usable for large polyphase induction motors. In the 19th century, two-phase transmission was used but required either three wires with unequal currents or four wires. Higher order phase systems require more than three wires, but deliver marginal benefits.
The capital cost of electric power stations is so high, and electric demand is so variable, that it is often cheaper to import some portion of the needed power than to generate it locally. Because nearby loads are often correlated (hot weather in the Southwest portion of the United States might cause many people there to turn on their air conditioners), electricity must often come from distant sources. Because of the economics of load balancing, wide area transmission grids now span across countries and even large portions of continents. The web of interconnections between power producers and consumers ensures that power can flow, even if a few links are inoperative.
The unvarying (or slowly varying over many hours) portion of the electric demand is known as the base load and is generally served best by large facilities (which are therefore efficient due to economies of scale) with low variable costs for fuel and operations. Such facilities might be nuclear or coal-fired power stations, or hydroelectric, while other renewable energy sources such as concentrated solar thermal and geothermal power have the potential to provide base load power. Renewable energy sources such as solar photovoltaics, wind, wave, and tidal are, due to their intermittency, not considered "base load" but can still add power to the grid. Smaller and higher cost sources, such as combined cycle or combustion turbine plants fueled by natural gas are then added as needed.
Long-distance transmission of electricity (thousands of kilometers) is cheap and efficient, with costs of US$0.005–0.02/kWh (compared to annual averaged large producer costs of US$0.01–0.025/kWh, retail rates upwards of US$0.10/kWh, and multiples of retail for instantaneous suppliers at unpredicted highest demand moments).[13] Thus distant suppliers can be cheaper than local sources (e.g., New York City buys a lot of electricity from Canada). Multiple local sources (even if more expensive and infrequently used) can make the transmission grid more fault tolerant to weather and other disasters that can disconnect distant suppliers.
Long distance transmission allows remote renewable energy resources to be used to displace fossil fuel consumption. Hydro and wind sources can't be moved closer to populous cities, and solar costs are lowest in remote areas where local power needs are minimal. Connection costs alone can determine whether any particular renewable alternative is economically sensible. Costs can be prohibitive for transmission lines, but various proposals for massive infrastructure investment in high capacity, very long distance super grid transmission networks could be recovered with modest usage fees.
At the generating plants the energy is produced at a relatively low voltage between about 2.3 kV and 30 kV, depending on the size of the unit. The generator terminal voltage is then stepped up by the power station transformer to a higher voltage (115 kV to 765 kV AC, varying by country) for transmission over long distances.
Transmitting electricity at high voltage reduces the fraction of energy lost to resistance. For a given amount of power, a higher voltage reduces the current and thus the resistive losses in the conductor. For example, raising the voltage by a factor of 10 reduces the current by a corresponding factor of 10 and therefore the
losses by a factor of 100, provided the same sized conductors are used in both cases. Even if the conductor size (cross-sectional area) is reduced 10-fold to match the lower current the
losses are still reduced 10-fold. Long distance transmission is typically done with overhead lines at voltages of 115 to 1,200 kV. At extremely high voltages, more than 2 MV between conductor and ground, corona discharge losses are so large that they can offset the lower resistance loss in the line conductors.
Transmission and distribution losses in the USA were estimated at 7.2% in 1995 [14]
As of 1980, the longest cost-effective distance for electricity was 7,000 km (4,300 mi), although all present transmission lines are considerably shorter.[15]
In an alternating current circuit, the inductance and capacitance of the phase conductors can be significant. The currents that flow in these components of the circuit impedance constitute reactive power, which transmits no energy to the load. Reactive current flow causes extra losses in the transmission circuit. The ratio of real power (transmitted to the load) to apparent power is the power factor. As reactive current increases, the reactive power increases and the power factor decreases. For systems with low power factors, losses are higher than for systems with high power factors. Utilities add capacitor banks and other components (such as phase-shifting transformers; static VAR compensators; physical transposition of the phase conductors; and flexible AC transmission systems, FACTS) throughout the system to control reactive power flow for reduction of losses and stabilization of system voltage.
At the substations, transformers reduce the voltage to a lower level for distribution to commercial and residential users. This distribution is accomplished with a combination of sub-transmission (33 kV to 115 kV, varying by country and customer requirements) and distribution (3.3 to 25 kV). Finally, at the point of use, the energy is transformed to low voltage (100 to 600 V, varying by country and customer requirements—see mains power systems).
High voltage direct current (HVDC) is used to transmit large amounts of power over long distances or for interconnections between asynchronous grids. When electrical energy is required to be transmitted over very long distances, it is more economical to transmit using direct current instead of alternating current. For a long transmission line, the lower losses and reduced construction cost of a DC line can offset the additional cost of converter stations at each end. Also, at high AC voltages, significant (although economically acceptable) amounts of energy are lost due to corona discharge, the capacitance between phases or, in the case of buried cables, between phases and the soil or water in which the cable is buried.
HVDC is also used for long submarine cables because over about 30 km length AC can no longer be applied. In that case special high voltage cables for DC are built. Many submarine cable connections - up to 600 km length - are in use nowadays.
HVDC links are sometimes used to stabilize against control problems with the AC electricity flow. In other words, to transmit AC power as AC when needed in either direction between Seattle and Boston would require the (highly challenging) continuous real-time adjustment of the relative phase of the two electrical grids. With HVDC instead the interconnection would: (1) Convert AC in Seattle into HVDC. (2) Use HVDC for the three thousand miles of cross country transmission. Then (3) convert the HVDC to locally synchronized AC in Boston, and optionally in other cooperating cities along the transmission route. One prominent example of such a transmission line is the Pacific DC Intertie located in the Western United States.
The amount of power that can be sent over a transmission line is limited. The origins of the limits vary depending on the length of the line. For a short line, the heating of conductors due to line losses sets a thermal limit. If too much current is drawn, conductors may sag too close to the ground, or conductors and equipment may be damaged by overheating. For intermediate-length lines on the order of 100 km (62 mi), the limit is set by the voltage drop in the line. For longer AC lines, system stability sets the limit to the power that can be transferred. Approximately, the power flowing over an AC line is proportional to the sine of the phase angle of the voltage at the receiving and transmitting ends. Since this angle varies depending on system loading and generation, it is undesirable for the angle to approach 90 degrees. Very approximately, the allowable product of line length and maximum load is proportional to the square of the system voltage. Series capacitors or phase-shifting transformers are used on long lines to improve stability. High-voltage direct current lines are restricted only by thermal and voltage drop limits, since the phase angle is not material to their operation.
Up to now, it has been almost impossible to foresee the temperature distribution along the cable route, so that the maximum applicable current load was usually set as a compromise between understanding of operation conditions and risk minimization. The availability of industrial Distributed Temperature Sensing (DTS) systems that measure in real time temperatures all along the cable is a first step in monitoring the transmission system capacity. This monitoring solution is based on using passive optical fibers as temperature sensors, either integrated directly inside a high voltage cable or mounted externally on the cable insulation. A solution for overhead lines is also available. In this case the optical fiber is integrated into the core of a phase wire of overhead transmission lines (OPPC). The integrated Dynamic Cable Rating (DCR) or also called Real Time Thermal Rating (RTTR) solution enables not only to continuously monitor the temperature of a high voltage cable circuit in real time, but to safely utilize the existing network capacity to its maximum. Furthermore it provides the ability to the operator to predict the behavior of the transmission system upon major changes made to its initial operating conditions.
To ensure safe and predictable operation the components of the transmission system are controlled with generators, switches, circuit breakers and loads. The voltage, power, frequency, load factor, and reliability capabilities of the transmission system are designed to provide cost effective performance for the customers.
The transmission system provides for base load and peak load capability, with safety and fault tolerance margins. The peak load times vary by region largely due to the industry mix. In very hot and very cold climates home air conditioning and heating loads have an effect on the overall load. They are typically highest in the late afternoon in the hottest part of the year and in mid-mornings and mid-evenings in the coldest part of the year. This makes the power requirements vary by the season and the time of day. Distribution system designs always take the base load and the peak load into consideration.
The transmission system usually does not have a large buffering capability to match the loads with the generation. Thus generation has to be kept matched to the load, to prevent overloading failures of the generation equipment.
Multiple sources and loads can be connected to the transmission system and they must be controlled to provide orderly transfer of power. In centralized power generation, only local control of generation is necessary, and it involves synchronization of the generation units, to prevent large transients and overload conditions.
In distributed power generation the generators are geographically distributed and the process to bring them online and offline must be carefully controlled. The load control signals can either be sent on separate lines or on the power lines themselves. To load balance the voltage and frequency can be used as a signaling mechanism.
In voltage signaling, the variation of voltage is used to increase generation. The power added by any system increases as the line voltage decreases. This arrangement is stable in principle. Voltage based regulation is complex to use in mesh networks, since the individual components and setpoints would need to be reconfigured every time a new generator is added to the mesh.
In frequency signaling, the generating units match the frequency of the power transmission system. In droop speed control, if the frequency decreases, the power is increased. (The drop in line frequency is an indication that the increased load is causing the generators to slow down.)
Wind turbines, v2g and other distributed storage and generation systems can be connected to the power grid, and interact with it to improve system operation.
Under excess load conditions, the system can be designed to fail gracefully rather than all at once. Brownouts occur when the supply power drops below the demand. Blackouts occur when the supply fails completely.
Rolling blackouts, or load shedding, are intentionally-engineered electrical power outages, used to distribute insufficient power when the demand for electricity exceeds the supply.
Operators of long transmission lines require reliable communications for control of the power grid and, often, associated generation and distribution facilities. Fault-sensing protection relays at each end of the line must communicate to monitor the flow of power into and out of the protected line section so that faulted conductors or equipment can be quickly de-energized and the balance of the system restored. Protection of the transmission line from short circuits and other faults is usually so critical that common carrier telecommunications are insufficiently reliable, and in remote areas a common carrier may not be available. Communication systems associated with a transmission project may use:
Rarely, and for short distances, a utility will use pilot-wires strung along the transmission line path. Leased circuits from common carriers are not preferred since availability is not under control of the electric power transmission organization.
Transmission lines can also be used to carry data: this is called power-line carrier, or PLC. PLC signals can be easily received with a radio for the long wave range.
Optical fibers can be included in the stranded conductors of a transmission line, in the overhead shield wires. These cables are known as optical ground wire (OPGW). Sometimes a standalone cable is used, all-dielectric self-supporting (ADSS) cable, attached to the transmission line cross arms.
Some jurisdictions, such as Minnesota, prohibit energy transmission companies from selling surplus communication bandwidth or acting as a telecommunications common carrier. Where the regulatory structure permits, the utility can sell capacity in extra dark fibers to a common carrier, providing another revenue stream.
Some regulators regard electric transmission to be a natural monopoly[16][17] and there are moves in many countries to separately regulate transmission (see electricity market).
Spain was the first country to establish a regional transmission organization. In that country transmission operations and market operations are controlled by separate companies. The transmission system operator is Red Eléctrica de España (REE) and the wholesale electricity market operator is Operador del Mercado Ibérico de Energía - Polo Español, S.A. (OMEL) [2]. Spain's transmission system is interconnected with those of France, Portugal, and Morocco.
In the United States and parts of Canada, electrical transmission companies operate independently of generation and distribution companies.
Merchant transmission is an arrangement where a third party constructs and operates electric transmission lines through the franchise area of an unrelated utility. Advocates of merchant transmission[who?] claim that this will create competition to construct the most efficient and lowest cost additions to the transmission grid. Merchant transmission projects typically involve DC lines because it is easier to limit flows to paying customers.
Operating merchant transmission projects in the United States include the Cross Sound Cable from Long Island, New York to New Haven, Connecticut, Neptune RTS Transmission Line from Sayreville, N.J., to Newbridge, N.Y, ITC Holdings, Inc. transmission system in the midwest, and Path 15 in California. Additional projects are in development or have been proposed throughout the United States.
There is only one unregulated or market interconnector in Australia: Basslink between Tasmania and Victoria. Two DC links originally implemented as market interconnectors Directlink and Murraylink have been converted to regulated interconnectors. NEMMCO
A major barrier to wider adoption of merchant transmission is the difficulty in identifying who benefits from the facility so that the beneficiaries will pay the toll. Also, it is difficult for a merchant transmission line to compete when the alternative transmission lines are subsidized by other utility businesses.[18]
The preponderance of evidence suggests that the low-power, low-frequency, electromagnetic radiation associated with household current does not constitute a short or long term health hazard. There are statistical correlations between various diseases and living or working near power lines.
Historically, local governments have exercised authority over the grid and have significant disincentives to take action that would benefit states other than their own. Localities with cheap electricity have a disincentive to making interstate commerce in electricity trading easier, since other regions will be able to compete for local energy and drive up rates. Some regulators in Maine for example do not wish to address congestion problems because the congestion serves to keep Maine rates low.[19] Further, vocal local constituencies can block or slow permitting by pointing to visual impact, environmental, and perceived health concerns. In the US, generation is growing 4 times faster than transmission, but big transmission upgrades require the coordination of multiple states, a multitude of interlocking permits, and cooperation between a significant portion of the 500 companies that own the grid. From a policy perspective, the control of the grid is balkanized, and even former energy secretary Bill Richardson refers to it as a third world grid. There have been efforts in the EU and US to confront the problem. The US national security interest in significantly growing transmission capacity drove passage of the 2005 energy act giving the Department of Energy the authority to approve transmission if states refuse to act. However, soon after using its power to designate two National Interest Electric Transmission Corridors, 14 senators signed a letter stating the DOE was being too aggressive[20].
In some countries where electric trains run on low frequency AC (e.g., 16.7 Hz and 25 Hz) power, there are separate single phase traction power networks operated by the railways. These grids are fed by separate generators in some traction powerstations or by traction current converter plants from the public three phase AC network.
Radio and television broadcasters use specialized transmission lines to carry the output of high-power transmitters to the antenna.
High-temperature superconductors promise to revolutionize power distribution by providing lossless transmission of electrical power. The development of superconductors with transition temperatures higher than the boiling point of liquid nitrogen has made the concept of superconducting power lines commercially feasible, at least for high-load applications.[21] It has been estimated that the waste would be halved using this method, since the necessary refrigeration equipment would consume about half the power saved by the elimination of the majority of resistive losses. In one hypothetical future system called a SuperGrid, the cost of cooling would be eliminated by coupling the transmission line with a liquid hydrogen pipeline.
Superconducting cables are particularly suited to high load density areas such as the business district of large cities, where purchase of an easement for cables would be very costly.[22]
Single wire earth return (SWER) or single wire ground return is a single-wire transmission line for supplying single-phase electrical power for an electrical grid to remote areas at low cost. It is principally used for rural electrification, but also finds use for larger isolated loads such as water pumps, and light rail. Single wire earth return is also used for HVDC over submarine power cables.
Every radio transmitter emits power wirelessly. Both Nikola Tesla and Hidetsugu Yagi attempted to devise systems for large scale wireless power transmission. Tesla claimed to have succeeded.[23][24][25][26][27][28] Yagi also proposed a similar concept, but the engineering problems proved to be more onerous than conventional systems. His work, however, led to the invention of the Yagi antenna.
Another form of wireless power transmission has been studied for transmission of power from solar power satellites to the earth. A high power array of microwave transmitters would beam power to a rectenna. Major engineering and economic challenges face any solar power satellite project.
Another form is the operation of a crystal radio powered by the radio station it is tuned to; however, the energetic efficiency is extremely low. Small scale wireless power was demonstrated as early as 1831 by Michael Faraday. By 1888, Heinrich Rudolf Hertz had proven that natural radio waves exist and can be captured.
The Federal government of the United States admits that the power grid is susceptible to cyber-warfare.[29][30] The United States Department of Homeland Security works with industry to identify vulnerabilities and to help industry enhance the security of control system networks, the federal government is also working to ensure that security is built in as we develop the next generation of 'smart grid' networks.[31] On April 8, 2009, it is believed that China or Russia have infiltrated the U.S. electrical grid and left behind software programs that could be used to disrupt the system, according to current and former national-security officials.[32][33] China denies intruding into the U.S. electrical grid.[34][35] The North American Electric Reliability Corporation (NERC) has issued a public notice that warns that the electrical grid is not adequately protected from cyber attack.[36] One counter measure the U.S. should consider is disconnecting the power grid from the Internet to decrease the likelihood of attack.[37][38] Massive power outages caused by a cyber attack, would cause a crisis making it difficult for the government and emergency workers to respond to critical concerns leading to national trauma.[39]
| Look up grid electricity in Wiktionary, the free dictionary. |
|
|||||||||||||||||||||||||
This entry is from Wikipedia, the leading user-contributed encyclopedia. It may not have been reviewed by professional editors (see full disclaimer)
| Best of the Web: Electric power transmission |
Some good "Electric power transmission" pages on the web:
Math mathworld.wolfram.com |
| trunk feeder (electricity) | |
| coronal mass ejection | |
| cryoresistive transmission line (electricity) |
Copyrights:
![]() | Sci-Tech Dictionary. McGraw-Hill Dictionary of Scientific and Technical Terms. Copyright © 2003, 1994, 1989, 1984, 1978, 1976, 1974 by McGraw-Hill Companies, Inc. All rights reserved. Read more | |
![]() | Sci-Tech Encyclopedia. McGraw-Hill Encyclopedia of Science and Technology. Copyright © 2005 by The McGraw-Hill Companies, Inc. All rights reserved. Read more | |
![]() | Wikipedia. This article is licensed under the Creative Commons Attribution/Share-Alike License. It uses material from the Wikipedia article "Electric power transmission". Read more |
Mentioned in