Psychrometrics

A study of the physical and thermody-namic properties of the atmosphere. The properties of primary concern in air conditioning are (1) dry-bulb temperature, (2) wetbulb temperature, (3) dew-point temperature, (4) absolute humidity, (5) percent humidity, (6) sensible heat, (7) latent heat, (8) total heat, (9) density, and (10) pressure.

The dry-bulb temperature is the ambient temperature of the air and water vapor as measured by a thermometer or other temperature-measuring device in which the thermal element is dry and shielded from radiation. See also Air temperature.

If the bulb of a dry-bulb thermometer is covered with a silk or cotton wick saturated with distilled water and the air is drawn over it at a velocity not less than 1000 ft/min (5 m/s), the resultant temperature will be the wet-bulb temperature. Where the dry-bulb and wet-bulb temperatures are the same, the atmosphere is saturated.

The dew-point temperature is the temperature at which the water vapor in the atmosphere begins to condense. This is also the temperature of saturation at which the dry-bulb, wet-bulb, and dew-point temperatures are all the same. See also Dew point.

The actual quantity of water vapor in the atmosphere is designated as the absolute humidity. Percentage or relative humidity is the ratio of the actual water vapor in the atmosphere to the quantity of water vapor the atmosphere could hold if it were saturated at the same temperature. See also Humidity.

Sensible heat, or enthalpy of dry air, is heat which manifests itself as a change in temperature. See also Enthalpy.

Latent heat, or enthalpy of vaporization, is the heat required to change a liquid into a vapor without change in temperature. Latent heat is sometimes referred to as the latent heat of vaporization and varies inversely as the pressure.

The total heat, or enthalpy, of the atmosphere is the sum of the sensible heat, latent heat, and superheat of the vapor above the saturation or dew-point temperature. Total heat is relatively constant for a constant wet-bulb temperature, deviating only about 1.5–2% low at relative humidities below 30%.

The density of the atmosphere varies with both altitude and percentage humidity. The higher the altitude the lower the density, and the higher the moisture content the lower the density. See also Density.

Atmospheric pressure is usually referred to as barometric pressure. Pressure varies inversely as elevation, as temperature, and as percentage saturation. See also Moisture-content measurement; Psychrometer.


 
 
Wikipedia: psychrometrics

Psychrometrics or psychrometry are terms used to describe the field of engineering concerned with the determination of physical and thermodynamic properties of gas-vapor mixtures.

Common applications

The principles of psychrometry apply to any physical system consisting of gas-vapor mixtures. The most common system of interest, however, are mixtures of water vapor and air because of its application in heating, ventilating, and air-conditioning and meteorology.

Psychrometric ratio

The psychrometric ratio is an important property in the area of psychrometrics as it relates the absolute humidity and saturation humidity to the difference between the dry bulb temperature and the adiabatic saturation temperature.

Mixtures of air and water vapor are the most common systems encountered in psychrometry. The psychrometric ratio of air-water vapor mixtures is approximately unity which implies that the difference between the adibatic saturation temperature and wet bulb temperature of air-water vapor mixtures is small. This property of air-water vapor systems simplifies drying and cooling calculations often performed using psychrometic relationships.

Psychrometric chart

A simple psychrometric chart.
Enlarge
A simple psychrometric chart.

A psychrometric chart is a graph of the physical properties of moist air at a constant pressure (often equated to an elevation relative to sea level). The chart graphically expresses how various properties relate to each other, and is thus a graphical equation of state. The thermophysical properties found on most psychrometric charts are:

Dry-bulb temperature (DBT) is that of an air sample, as determined by an ordinary thermometer, the thermometer's bulb being dry. It is typically the abscissa, or horizontal axis of the graph. The SI units for temperature are Celsius; other units are Fahrenheit.
Wet-bulb temperature (WBT) is that of an air sample after it has passed through a constant-pressure, ideal, adiabatic saturation process, that is, after the air has passed over a large surface of liquid water in an insulated channel. In practice, this is the reading of a thermometer whose sensing bulb is covered with a wet sock evaporating into a rapid stream of the sample air. The WBT is the same as the DBT when the air sample is saturated with water. The slope of the line of constant WBT reflects the heat of vaporization of the water required to saturate the air of a given relative humidity.
Dew point temperature (DPT) is that temperature at which a moist air sample at the same pressure would reach water vapor saturation. At this saturation point, water vapor would begin to condense into liquid water fog or (if below freezing) solid hoarfrost, as heat is removed. The dewpoint temperature is measured easily and provides useful information, but is normally not considered an independent property. It duplicates information available via other humidity properties and the saturation curve.
Relative Humidity (RH) is the ratio of the mole fraction of water vapor to the mole fraction of saturated moist air at the same temperature and pressure. RH is dimensionless, and is usually expressed as a percentage. Lines of constant RH reflect the physics of air and water: they are determined via experimental measurement. Note: the notion that air "holds" moisture, or that moisture dissolves in dry air and saturates the solution at some proportion, is an erroneous (albeit widespread) concept (see Relative_humidity for further details).
Humidity Ratio (also known as Moisture Content, Mixing Ratio, or Specific Humidity) is the proportion of mass of water vapour per unit mass of dry air at the given conditions (DBT, WBT, DPT, RH, etc.). It is typically the ordinate, or vertical axis of the graph. For a given DBT there will be a particular humidity ratio for which the air sample is at 100% relative humidity: the relationship reflects the physics of water and air and must be measured. Humidity Ratio is dimensionless, but is sometimes expressed as grams of water per kilogram of dry air or grains of water per pound of air.
Specific Enthalpy symbolized by h, also called heat content per unit mass, is the sum of the internal (heat) energy of the moist air in question, including the heat of the air and water vapor within. In the approximation of ideal gasses, lines of constant enthalpy are parallel to lines of constant WBT. Enthalpy is given in (SI) Joules per kilogram of air or BTU per pound of air.
Specific Volume, also called Inverse Density, is the volume per unit mass of the air sample. The SI units are cubic meters per kilogram of air; other units are cubic feet per pound of dry air.

The versatility of the psychrometric chart lies in the fact that by knowing three independent properties of some moist air (one of which is the pressure), the other properties can be determined. Changes in state, such as when two air streams mix, can be modeled easily and somewhat graphically using the correct psychrometric chart for the location's air pressure or elevation relative to sea level. For locations at or below 2000 ft (600 m), a common assumption is to use the sea level psychrometric chart.

The relationship between DBT, WBT, and RH is given by the Mollier (pressure-enthalpy) diagram for water in air, developed by Richard Mollier. Willis Carrier, considered the 'father' of modern air-conditioning, rearranged the Mollier diagram for moist air (its T-s chart) to allow such graphical solutions. Many variations and improvements to the psychrometric charts have occurred since, and most charts do not show the specific entropy (s) like the Mollier diagram. ASHRAE now publishes what are considered the modern, standard psychrometric charts, in both I-P and SI units, for a variety of elevations or air pressures.

How to read the chart

The most common chart used by practitioners and students alike is the "ω-t" (omega-t) chart in which the Dry Bulb Temperature (DBT) appears horizontally as the abscissa and the humidity ratios (ω) appear as the ordinates.

In order to use a particular chart, for a given air pressure or elevation, at least two of the six independent properties must be known (DBT, WBT, RH, Humidity Ratio, Specific Enthalpy, and Specific Volume). This gives rise to \left({6 \atop 2}\right) = 15 possible combinations.

DBT : This can be determined from the abscissa

DPT : Follow the horizontal line from the point where the line from the horizontal axis arrives at 100% RH, also known as the saturation curve.

WBT : Line inclined to the horizontal and intersects saturation curve at DBT point.

RH : Hyperbolic lines drawn asymptotically with respect to the saturation curve which corresponds to 100% RH.

Humidity Ratio : Marked on Ordinate axis.

Specific Enthalpy : lines of equal values, or hash marks for, slope from the upper left to the lower right.

Specific Volume : Equally spaced parallel family of lines.

Dry-bulb temperature

Common thermometers measure what is known as the dry-bulb temperature. Electronic temperature measurement, via thermocouples, thermistors, and resistance temperature devices (RTDs), for example, have been widely used too since they became available.

Wet-bulb temperature

A hygrometer is an instrument used to measure the amount of moisture in the air. If a moist wick is placed over a thermometer bulb the evaporation of moisture from the wick will lower the thermometer reading (temperature). If the air surrounding a wet-bulb thermometer is dry, evaporation from the moist wick will be more rapid than if the air is moist. When the air is saturated no water will evaporate from the cloth wick and the temperature of the wet-bulb thermometer will be the same as the reading on the dry-bulb thermometer. However, if the air is not saturated water will evaporate from the wick causing the temperature reading to be lower. The accuracy of the wet-bulb temperature depends on how fast air passes over the bulb. Speeds up to 5,000 ft/min (60 mph) are best but dangerous to move a thermometer at that speed. Errors up to 15% can occur if the air movement is too slow or if there is too much radiant heat present (sunlight, for example).

A wet bulb temperature taken with air moving at about 1-2 m/s is referred to as a screen temperature, whereas a temperature taken with air moving about 3.5 m/s or more is referred to as sling temperature.

A psychrometer is a device that includes both a dry-bulb and a wet-bulb thermometer. A sling psychrometer requires manual operation to create the airflow over the bulbs, but a powered psychrometer includes a fan for this function.

See also

External links


 
 

Join the WikiAnswers Q&A community. Post a question or answer questions about "psychrometrics" at WikiAnswers.

 

Copyrights:

Sci-Tech Encyclopedia. McGraw-Hill Encyclopedia of Science and Technology. Copyright © 2005 by The McGraw-Hill Companies, Inc. All rights reserved.  Read more
Wikipedia. This article is licensed under the GNU Free Documentation License. It uses material from the Wikipedia article "Psychrometrics" Read more

Search for answers directly from your browser with the FREE Answers.com Toolbar!  
Click here to download now. 

Get Answers your way! Check out all our free tools and products.

On this page:   E-mail   print Print  Link  

 

Keep Reading

Mentioned In: