Automotive style miniature relay
A relay is an electrical switch that opens and closes under the control of another
electrical circuit. In the original form, the switch is operated by an
electromagnet to open or close one or many sets of contacts. It was invented by Joseph Henry in 1835. Because a relay is able to control an output circuit of
higher power than the input circuit, it can be considered, in a broad sense, to be a form of an electrical amplifier.
Operation
When a current flows through the coil, the resulting
magnetic field attracts an armature that is mechanically linked to a moving contact. The movement either makes or
breaks a connection with a fixed contact. When the current to the coil is switched off, the armature is returned by a force
approximately half as strong as the magnetic force to its relaxed position. Usually this is a spring, but gravity is also used commonly in industrial motor starters. Most relays are manufactured to
operate quickly. In a low voltage application, this is to reduce noise. In a high voltage or high current application, this is to
reduce arcing.
If the coil is energized with DC, a diode is frequently installed across the coil, to
dissipate the energy from the collapsing magnetic field at deactivation, which would otherwise generate a spike of voltage and
might cause damage to circuit components. Some automotive relays already include that diode inside the relay case. Alternatively
a contact protection network, consisting of a capacitor and resistor in series, may absorb the surge. If the coil is designed to
be energized with AC, a small copper ring can be crimped to the end of the solenoid. This "shading ring" creates a small
out-of-phase current, which increases the minimum pull on the armature during the AC cycle.[1]
By analogy with the functions of the original electromagnetic device, a solid-state relay is made with a thyristor or other solid-state switching device. To achieve electrical isolation an optocoupler can be used
which is a light-emitting diode (LED) coupled with a photo transistor.
Types of relay
Small relay as used in electronics
Latching relay
A latching relay has two relaxed states (bistable). These are also called 'keep' relays. When the current is switched
off, the relay remains in its last state. This is achieved with a solenoid operating a ratchet and cam mechanism, or by having
two opposing coils with an over-center spring or permanent magnet to hold the armature and contacts in position while the coil is
relaxed, or with a remnant core. In the ratchet and cam example, the first pulse to the coil turns the relay on and the second
pulse turns it off. In the two coil example, a pulse to one coil turns the relay on and a pulse to the opposite coil turns the
relay off. This type of relay has the advantage that it consumes power only for an instant, while it is being switched, and it
retains its last setting across a power outage.
Reed relay
A reed relay has a set of contacts inside a vacuum
or inert gas filled glass tube, which protects the contacts against atmospheric
corrosion. The contacts are closed by a magnetic field generated when current passes through a
coil around the glass tube. Reed relays are capable of faster switching speeds than conventional
relays. See also reed switch.
Mercury-wetted relay
A mercury-wetted reed relay is a form of reed relay in which the contacts are wetted with mercury. Such relays are used to switch low-voltage signals (one volt or less) because of its low
contact resistance, or for high-speed counting and timing applications where the mercury eliminates contact bounce. Mercury
wetted relays are position-sensitive and must be mounted vertically to work properly. Because of the toxicity and expense of
liquid mercury, these relays are rarely specified for new equipment. See also mercury
switch.
Polarized relay
A Polarized Relay placed the armature between the poles of a permanent magnet to increase sensitivity. Polarized relays
were used in middle 20th Century telephone exchanges to detect faint pulses and correct
telegraphic distortion. The poles were on screws, so a technician could first adjust them for maximum sensitivity and then apply
a bias spring to set the critical current that would operate the relay.
Machine tool relay
A machine tool relay is a type standardized for industrial control of machine tools, transfer machines, and other
sequential control. They are characterized by a large number of contacts (sometimes extendable in the field) which are easily
converted from normally-open to normally-closed status, easily replaceable coils, and a form factor that allows compactly
installing many relays in a control panel. Although such relays once were the backbone of automation in such industries as
automobile assembly, the programmable logic controller mostly displaced
the machine tool relay from sequential control applications.
Contactor relay
A contactor is a very heavy-duty relay used for switching electric motors and lighting loads. With high current, the contacts are made with pure silver. The
unavoidable arcing causes the contacts to oxidize and silver oxide is still a good conductor. Such devices are often used for
motor starters. A motor starter is a contactor with overload protection devices attached. The overload sensing devices are a form
of heat operated relay where a coil heats a bi-metal strip, or where a solder pot melts, releasing a spring to operate auxiliary
contacts. These auxiliary contacts are in series with the coil. If the overload senses excess current in the load, the coil is
de-energized. Contactor relays can be extremely loud to operate, making them unfit for use where noise is a chief concern.
Solid state contactor relay
25 amp or 40 amp solid state contactors
A solid state contactor is a very heavy-duty solid state relay, including
the necessary heat sink, used for switching electric heaters, small electric motors and
lighting loads; where frequent on/off cycles are required. There are no moving parts to wear out and there is no contact bounce
due to vibration. They are activated by AC control signals or DC control signals from Programmable logic controller (PLCs), PCs, Transistor-transistor logic (TTL) sources, or other microprocessor controls.
Buchholz relay
A Buchholz relay is a safety device sensing the accumulation of gas in large
oil-filled transformers, which will alarm on slow accumulation of gas or shut down the
transformer if gas is produced rapidly in the transformer oil.
Forced-guided contacts relay
A forced-guided contacts relay has relay contacts that are mechanically linked together, so that when the relay coil is
energized or de-energized, all of the linked contacts move together. If one set of contacts in the relay becomes immobilized, no
other contact of the same relay will be able to move. The function of forced-guided contacts is to enable the safety circuit to
check the status of the relay. Forced-guided contacts are also known as "positive-guided contacts", "captive contacts", "locked
contacts", or "safety relays".
Solid-state relay
A solid state relay (SSR) is a solid state electronic component that provides a similar function to an electromechanical relay but does not have any moving components, increasing long-term reliability. With
early SSR's, the tradeoff came from the fact that every transistor has a small voltage drop across it. This collective voltage
drop limited the amount of current a given SSR could handle. As transistors improved, higher current SSR's, able to handle 100 to
1,200 amps, have become commercially available. Compared to electromagnetic
relays, they may be falsely triggered by transients.
Overload protection relay
One type of electric motor overload protection relay is operated by a heating element
in series with the electric motor . The heat generated by the motor current operates a
bi-metal strip or melts solder, releasing a spring to operate contacts. Where the overload relay
is exposed to the same environment as the motor, a useful though crude compensation for motor ambient temperature is
provided.
Pole & Throw
Circuit symbols of relays.
"C" denotes the common terminal in SPDT and DPDT types.
Since relays are switches, the terminology applied to switches is also applied to relays. A
relay will switch one or more poles, each of whose contacts can be thrown by energizing the coil in one of three
ways:
- Normally-open (NO) contacts connect the circuit when the relay is activated; the circuit is disconnected when the
relay is inactive. It is also called a Form A contact or "make" contact.
- Normally-closed (NC) contacts disconnect the circuit when the relay is activated; the circuit is connected when the
relay is inactive. It is also called a Form B contact or "break" contact.
- Change-over, or double-throw, contacts control two circuits: one normally-open contact and one normally-closed contact with a
common terminal. It is also called a Form C contact or "transfer" contact. If this type of contact utilizes a "make before
break" functionality, then it is called a Form D contact.
The following types of relays are commonly encountered:
- SPST - Single Pole Single Throw. These have two terminals which can be connected or
disconnected. Including two for the coil, such a relay has four terminals in total. It is ambiguous whether the pole is normally
open or normally closed. The terminology "SPNO" and "SPNC" is sometimes used to resolve the ambiguity.
- SPDT - Single Pole Double Throw. A common terminal connects to either of two others.
Including two for the coil, such a relay has five terminals in total.
- DPST - Double Pole Single Throw. These have two pairs of terminals. Equivalent to two SPST
switches or relays actuated by a single coil. Including two for the coil, such a relay has six terminals in total. It is
ambiguous whether the poles are normally open, normally closed, or one of each.
The diagram on the package of a DPDT AC coil relay
- DPDT - Double Pole Double Throw. These have two rows of change-over terminals. Equivalent
to two SPDT switches or relays actuated by a single coil. Such a relay has eight terminals, including the coil.
- QPDT - Quadruple Pole Double Throw. Often referred to as Quad Pole Double Throw, or 4PDT.
These have four rows of change-over terminals. Equivalent to four SPDT switches or relays actuated by a single coil, or two DPDT
relays. In total, fourteen terminals including the coil.
Applications
Relays are used:
- to control a high-voltage circuit with a low-voltage signal, as in some types of modems,
- to control a high-current circuit with a low-current signal, as in the
starter solenoid of an automobile,
- to detect and isolate faults on transmission and distribution lines by opening and closing circuit breakers (protection relays),
A DPDT AC coil relay with "ice cube" packaging
- to isolate the controlling circuit from the controlled circuit when the two are at different potentials, for example when
controlling a mains-powered device from a low-voltage switch. The latter is often applied to control office lighting as the low
voltage wires are easily installed in partitions, which may be often moved as needs change. They may also be controlled by room
occupancy detectors in an effort to conserve energy,
- to perform logic functions. For example, the boolean AND function is realised by connecting NO relay contacts in series, the
OR function by connecting NO contacts in parallel. The change-over or Form C contacts perform the XOR (exclusive or) function.
Similar functions for NAND and NOR are accomplished using NC contacts. The Ladder programming
language is often used for designing relay logic networks.
- Early computing. Before vacuum tubes and transistors, relays were used as logical elements in digital computers. See ARRA (computer), Harvard Mark II, Zuse Z2, and Zuse Z3.
- Safety-critical logic. Because relays are much more resistant than semiconductors to nuclear radiation, they are widely used
in safety-critical logic, such as the control panels of radioactive waste-handling machinery.
- to perform time delay functions. Relays can be modified to delay opening or delay closing a set of contacts. A very short (a
fraction of a second) delay would use a copper disk between the armature and moving blade assembly. Current flowing in the disk
maintains magnetic field for a short time, lengthening release time. For a slightly longer (up to a minute) delay, a dashpot is
used. A dashpot is a piston filled with fluid that is allowed to escape slowly. The time period can be varied by increasing or
decreasing the flow rate. For longer time periods, a mechanical clockwork timer is installed.
Relay application considerations
A large relay with two coils and many sets of contacts, used in an old telephone switching system.
Selection of an appropriate relay for a particular application requires evaluation of many different factors:
- Number and type of contacts - normally open, normally closed, changeover (double-throw)
- In the case of changeover, there are two types. This style of relay can be manufactured two different ways. "Make before
Break" and "Break before Make". The old style telephone switch required Make-before-break so that the connection didn't get
dropped while dialing the number. The railroad still uses them to control railroad crossings.
- Rating of contacts - small relays switch a few amperes, large contactors are rated for up to 3000 amperes, alternating or
direct current
- Voltage rating of contacts - typical control relays rated 300 VAC or 600 VAC, automotive types to 50 VDC, special
high-voltage relays to about 15,000 V
- Coil voltage - machine-tool relays usually 24 VAC or 120 VAC, relays for switchgear may have 125 V or 250 VDC coils,
"sensitive" relays operate on a few milliamperes
- Package/enclosure - open, touch-safe, double-voltage for isolation between circuits, explosion proof, outdoor,
oil-splashresistant
- Mounting - sockets, plug board, rail mount, panel mount, through-panel mount, enclosure for mounting on walls or
equipment
- Switching time - where high speed is required
- "Dry" contacts - when switching very low level signals, special contact materials may be needed such as gold-plated
contacts
- Contact protection - suppress arcing in very inductive circuits
- Coil protection - suppress the surge voltage produced when switching the coil current
- Isolation between coil circuit and contacts
- Aerospace or radiation-resistant testing, special quality assurance
- Expected mechanical loads due to acceleration - some relays used in aerospace applications are designed to function in shock loads of
50 g or more
- Accessories such as timers, auxiliary contacts, pilot lamps, test buttons
- Regulatory approvals
- Stray magnetic linkage between coils of adjacent relays on a printed circuit board.
Protective relay
A protective relay is
a complex electromechanical apparatus, often with more than one coil, designed to calculate operating conditions on an electrical
circuit and trip circuit breakers when a fault was found. Unlike switching type relays with fixed and usually ill-defined
operating voltage thresholds and operating times, protective relays had well-established, selectable, time/current (or other
operating parameter) curves. Such relays were very elaborate, using arrays of induction disks, shaded-pole magnets, operating and
restraint coils, solenoid-type operators, telephone-relay style contacts, and phase-shifting networks to allow the relay to
respond to such conditions as over-current, over-voltage, reverse power flow, over- and
under- frequency, and even distance relays that would trip for faults up to a certain distance away from a substation but not
beyond that point. An important transmission line or generator unit would have had cubicles dedicated to protection, with a score
of individual electromechanical devices. The various protective functions available on a given relay are denoted by standard
ANSI Device Numbers. For example, a relay including function 51 would be a timed
overcurrent protective relay.
These protective relays provide various types of electrical protection by detecting abnormal conditions and isolating them
from the rest of the electrical system by circuit breaker operation. Such relays may be located at the service entrance or at
major load centers.
Design and theory of these protective devices is an important part of the education of an electrical engineer who specializes in power systems. Today these devices are nearly entirely replaced
(in new designs) with microprocessor-based instruments (numerical relays) that emulate their electromechanical ancestors with
great precision and convenience in application. By combining several functions in one case, numerical relays also save capital
cost and maintenance cost over electromechanical relays. However, due to their very long life span, tens of thousands of these
"silent sentinels" are still protecting transmission lines and electrical apparatus all over the world.
Top, middle: reed switches, bottom: reed relay
Overcurrent relay
An "Overcurrent Relay" is a type of protective relay. The ANSI Device Designation Number is 50 for an Instantaneous
OverCurrent (IOC), 51 for a Time OverCurrent (TOC). In a typical application the overcurrent relay is used for overcurrent
protection, connected to a current transformer and calibrated to operate at or above a specific current level. When the relay
operates, one or more contacts will operate and energize a trip coil in a Circuit Breaker and trip (open) the Circuit
Breaker.
See also
References
1. Vladimir Gurevich "Electrical Relays: Principles and Applications", CRC Press (Taylor & Francis group), London - New
York, 2005, 704 pp.
2. Westinghouse Corporation, Applied Protective Relaying, 1976, Westinghouse Corporation, no ISBN, Library of Congress
card no. 76-8060 - a standard reference on electromechanical protection relays (out of print - current edition published by
ABB)
3. Terrell Croft and Wilford Summers (ed), American Electricians' Handbook, Eleventh Edition, McGraw Hill, New York
(1987) ISBN 0-07-013932-6
- ^ Mason, C. R., Art & Science of Protective Relaying, Chapter 2,
GE Consumer & Electrical [1],
External links
This entry is from Wikipedia, the leading user-contributed encyclopedia. It may not have been reviewed by professional editors (see full disclaimer)