Assumption:
F= 60Hz
V= 1v is equal also to I=1amp.
PF= 0.85
Single Phase: Three Phase:
S = IV pf / 1000 S = 1.73 x I x V x PF/1000
= 1 x 1 x 0.85/1000 = 1.73 x 1 x 1 x 0.85 /1000
S = 0.00085KVA S = 0.0014705KVA
You can't determine the output voltage of a transformer by knowing kva. Transformers will be marked as to input and output voltages. Some will have multiple input and output voltages. The output voltage depends on the ratio of coil turns between input and output.
Power requirements are measured in KVA, which stands for Kilo-Volt-Amperes. To calculate the amount of power you require you would use the following formula. KVA = Volts * Amps / 1000
KVA is a measurement of power; kV is a measurement of voltage. You're asking "What is the power for voltage?", which makes no sense. Power = Voltage times current.
200 amps is equal to zero kva. To answer this question a voltage is needed.
Transformer capacity (kvA) shall be identical, Both transformer impedance, secondary voltage and frequency shall be identical.
At what voltage? If you know the voltage then, to get the amps those kilovolt-amps contain, you simply divide the kilovolt-amps by the voltage.
Use the link below and scroll down.
The voltage is not 'calculated', it's determined from the specifications of the unit you are going to use.
You can't determine the output voltage of a transformer by knowing kva. Transformers will be marked as to input and output voltages. Some will have multiple input and output voltages. The output voltage depends on the ratio of coil turns between input and output.
Power requirements are measured in KVA, which stands for Kilo-Volt-Amperes. To calculate the amount of power you require you would use the following formula. KVA = Volts * Amps / 1000
Wire sizing of a feed conductor is based on the amperage that a device draws. To calculate amperage from KVA a voltage of the supply has to be stated. Without this voltage and whether the transformer is single or three phase an answer can not be given.
Rated voltage is the voltage at primary side. Rated current can be found from the equation, Rated Current= Output KVA / Output rated voltage
KVA is a measurement of power; kV is a measurement of voltage. You're asking "What is the power for voltage?", which makes no sense. Power = Voltage times current.
200 amps is equal to zero kva. To answer this question a voltage is needed.
Transformer capacity (kvA) shall be identical, Both transformer impedance, secondary voltage and frequency shall be identical.
Input and output voltages, maximum current rating, often expressed in VA or kVA as the voltage rating times the current rating. Operating frequency is the next important parameter because if the frequency is lower, the voltage must be reduced in proportion.
2.5 kVA means 2500 VA (volt-ampere). To calculate the amperes you need the voltage. 2.5 kVA x cos (phi) = 2.5 kW (kilowatts) if phi is 0 or power factor (phi) is unity.