Related questions

What size amp circuit breaker should be used for a home entertainment system?

You use the correct size breaker depending on the size wire in the circuit. If the circuit is wired with AWG #12 wire use a 20 amp breaker. If it is wired with AWG #14 wire then use a 15 amp breaker.


Can a circuit breaker be tripped by using 20 amp sockets instead of 15 amp sockets?

A circuit breaker protects the wires that the devices are connected to. If the devices that are connected to the circuit are 20 amps the wire size should be #12 wire fed from a 20 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. If the devices that are connected to the circuit are15 amps the wire size should be #14 wire fed from a15 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. Putting 20 amp sockets on this 15 amp circuit will work but the circuit is limited to the amount of load that can be plugged in. You will not get the full capacity of the 20 socket because the breaker will trip at 15 amps.


Can you upgrade a 15 Amps circuit breaker for a 40 Amp for a 8.5 Watt shower?

Not unless you change the wiring for that circuit. The breaker protects the wiring and if you install a 40 amp breaker on a 15 amp wire circuit you will have a fire in your home.


What size amp circuit breaker should be used for 110 outlet?

The size breaker you use is determined by the size wire used in the circuit. If you use AWG #12/2 wire then use a 20 amp breaker. If you use AWG # 14/2 then use a 15 amp breaker.


What is the smallest breaker for a 25 amp circuit?

30 amp wired with AWG # 10 wire.


Should 25 amps breaker be replaced by 20 amps?

For typical residential house wiring 12 AWG wire is required for a 20 Amp breaker. If you change out the breaker for a 25 A breaker you would have to rewire the circuit with 10 AWG. In that case you could up the breaker to 30 Amps. All outlets and switches should be rated at the same voltage and current as the breaker.


Can you replace a 20 amp circuit breaker with a 25 amp circuit breaker?

No. The breaker must protect the circuit components such as wiring, outlets and switches that are connected to the breaker. Therefore if you have a 30 amp circuit as dictated by its components you need to protect it with a 30 amp or less breaker.


What size circuit breaker for GFCI circuit in a normal size bath?

Normally it is a 20 amp using AWG 12/2 gauge wire. But it really depends on what size wire is on that circuit. If it is white AWG 14 gauge then use a 15 amp breaker. If it is yellow AWG 12 gauge then use a 20 amp breaker.


Is it safe to use 10 gauge wire on a 20 amp breaker for a microwave?

No, 10 gauge wire requires the use of a 30 amp breaker. A 20 amp breaker is only used on 12 gauge wire.


What size wire and breaker do you need for a 5000 watt garage heater?

Look on the heater and see what amps it is pulling. That will determine the wire size and breaker size. It must be on a dedicated circuit. 15 amps = AWG # 14 wire with 15 amp breaker 20 amps = AWG # 12 wire with 20 amp breaker 30 amps = AWG # 10 wire with 30 amp breaker 40 amps = AWG # 8 wire with 40 amp breaker


How big of breaker do you use for 115 volt?

Depends on the wire size used in the circuit. If you use AWG # 14 wire you must use a 15 amp breaker. If it is wired with AWG # 12 wire then you use a 20 amp breaker. If a AWG # 10 wire is used then a 30 amp breaker is required. The breaker protects the wiring from overheating so you must use the proper size breaker for the wire used.


Is a 40 amp circuit breaker ok for a 30 amp air conditioner?

Yes. You should use 8 AWG wire from breaker to AC unit.