At that distance the current would be limited by the acceptable voltage drop. As the load consists of lights a 3% drop should be the starting point, which means a voltage drop of 4.5 volts. 700 ft of 16-2 wire (copper) has a resistance of 1.4 ohms therefore the current allowed is 4.5/1.4 amps or 3.2 amps.
The total power is 150x3.2 watts, or 480 watts, so the number of lamps is 480/7 or 68 lamps.
AWG # 10 wire on 30 amp circuit.
For a 1500 watt 120 volt heater located 400 feet away, you would need to use at least 10-gauge wire to minimize voltage drop and ensure efficient power transmission. It is recommended to install a 240 volt sub panel near the heater location to account for the distance and potential power requirements for additional lights or equipment.
If your light bulb voltage rating is under 300 volts then yes it can use 300 volt wire. The voltage rating of the wire is the maximum voltage that the wire can safely carry. The three common insulation groups is 300 volts, 600 volts and 1000 volts.
Yes, armored cable can be used to wire 277 volt lights. However, be sure to select the appropriate type and size of armored cable rated for the voltage and current requirements of the lighting system to ensure safety and compliance with electrical codes and regulations.
10 gauge will suffice.
The recommended wire size for a 220 volt circuit according to the 220 volt wire size chart is typically 10 gauge wire for a circuit with a maximum of 30 amps.
No, 14-2 wire is not suitable for two 1500-watt baseboard heaters on a 240-volt circuit. Each 1500-watt heater draws approximately 6.25 amps, totaling about 12.5 amps for both. However, 14-gauge wire is rated for a maximum of 15 amps, which is close to the limit and does not provide a safe margin. It is recommended to use 12-gauge wire, which is rated for 20 amps, to ensure safety and compliance with electrical codes.
get a 12 volt tester light and turn the lights on and poke each wire until your tester light lights up and then you'll know what wire you need.
A #8 conductor is rated at 40 amps. Wattage is the product of amps x volts. As you can see the voltage is needed in this question to answer it. In the electrical trade I have never come across the terminology watt amp. Volt amp, yes.
For a 100 watt 12 volt lamp, you should use a wire gauge size of at least 18 AWG to ensure it can handle the current without overheating. It's always best to refer to the manufacturer's recommendations for the specific lamp you are using.
i wld like to put lightson my motorbike but lights r 240v and bike is 9v how do i do it
Yes, a 230 volt motor is generally more efficient and cheaper to run compared to a 115 volt motor. Higher voltage motors are more energy efficient because they draw less current, resulting in lower energy costs over time.