If the primary side of the transformer is 480 volts 3 phase, this transformer can be supplied from a breaker as big as 180 amps. If 480 volts 3 phase is your secondary then you can supply up to 180 amps to your loads.

User Avatar

Wiki User

12y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How many amps do you need to supply a 150kva transformer to get 118amps 480 volts?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How many volts does a mini connector have?

Depends on use,supply,AC,DC .Voltage,transformer ???


How you get 5.6 volts 12 ma from 230 volts supply in current transfomer?

You would not connect a current transformer to a 230 v supply. To get 5.6 v 12 mA you could get a 230 to 6 volt transformer, then drop the supply from 6 to 5.6 using a 33-ohm resistor.


Will a switching power supply work on 277 volts?

Not unless it is rated for that voltage. You can likely find a step down transformer from 277 volt sto 120 volts.


What class is a transformer that converts 110 volts to 24 volts?

A transformer that reduces voltage is classed as a step down transformer.


How do you convert 12 volt trailer lights to 24 volts?

Change the trailer light bulbs to 24 volts and supply a 24 volt source to power them, in that order.


How do you grade up micro volts to volts which can operate any small devices?

The voltage can be changed by a transformer, but the power remains constant. So if you have a supply of 1 microvolt, it would have to supply 1 million amps to give a power of 1 watt (power = volts times amps).


Can you get 110 volts from 277volts?

The voltage of 277 is the wye connection of a 480 volt three phase supply. The only way to reduce 277 to 120 volts is with a step down transformer.


What remains unchanged in transformer action?

In a standard transformer, the ratio of input volts to output volts remains constant.


Why does your 24 volts transformer get hot then burn out?

A transformer gets hot if it is run at excessive voltage or excessive current. Either of those two would cause it to overheat. <<>> It sounds like the load on the secondary is greater that what the transformer can supply. A transformer is wound for a specific amperage output at a specific voltage. This is stated on the transformer as a VA or in larger transformers as KVA. If you divide the 24 volts into the VA listed on the transformer you will get the maximum amperage value of the transformer. If the device that you are connecting to the transformer is greater in amperage draw that what the transformer can supply, this will cause the heating effect and if left connected eventually burn the transformer out. A fuse should be installed in the secondary 24 volt output, rated at the maximum output of the transformer. This will limit the transformer to its manufacturer's recommended current output.


How do you convert 480v to 120v?

to derive 120 volts from 480 volts you have to use a transformer, based on your needs. If you needed 100 amps at 120 volt single phase you would need a 12kva transformer. This is just an example.


Would 230 volt item applicance work on 220 volt in south Africa?

A step-up transformer would be required to supply 230 volts from a 220 volts source from South Africa.


If we have 13 volts on earth and neutral so?

The neutral and earth are connected at the supply transformer, so 13 volts on the neutral means that you are far enough from the transformer to have a 13 volt drop on the neutral. You probably have the same drop on the live, so the total volt drop could be 26 volts, which may be excessive. It could indicate a fault somewhere.