A transformer gets hot if it is run at excessive voltage or excessive current. Either of those two would cause it to overheat.

<<>>

It sounds like the load on the secondary is greater that what the transformer can supply. A transformer is wound for a specific amperage output at a specific voltage. This is stated on the transformer as a VA or in larger Transformers as KVA. If you divide the 24 volts into the VA listed on the transformer you will get the maximum amperage value of the transformer. If the device that you are connecting to the transformer is greater in amperage draw that what the transformer can supply, this will cause the heating effect and if left connected eventually burn the transformer out. A fuse should be installed in the secondary 24 volt output, rated at the maximum output of the transformer. This will limit the transformer to its manufacturer's recommended current output.

User Avatar

Wiki User

10y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Why does your 24 volts transformer get hot then burn out?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Electrical Engineering

What class is a transformer that converts 110 volts to 24 volts?

A transformer that reduces voltage is classed as a step down transformer.


What is 50VA?

50 VA means about 50 watts. Transformers usually use VA instead of watts because a transformer has very little wasted power, and watts measure power. A 50 va transformer that is 120v. on the primary side will use about .41 amps at 120 volts. On the secondary side, (if it's 24 volts) it will support about 2.08 amps.


What is the equivalent of 36 amps at 12 volts at 24 volts?

36 is to 12 as 18 is to 24.


How to Wire a low voltage thermostat for a 220v baseboard heater?

You will need a relay with a low-voltage coil and 220v contacts rated for the current load of the baseboard heater. If you have a low-voltage transformer, see what its output is rated at (typically 24 volts or less). Then go to an electronics parts store or call some place like Digikey (phone 800-344-4539) and tell them you need (for example) a double-pole single-throw normally-open relay with a 24 volt coil and contacts rated at 30 amps at 240 volts (change these numbers to match your situation). If you do not already have a low-voltage transformer the parts store call sell you one to match the relay coil voltage (be sure to specify if you are connecting the transformer input to 120 volts or 240 volts). Then wire it up as follows: connect the transformer output (24 volts in the example above) in series with the thermostat contacts and the relay coil. Connect the 240 volt supply to the moving arms on the relay, and connect the contacts the arms touch when the relay operates to your heater. Now when the temperature drops below its setting the thermostat contacts will close and connect the relay coil to the 24 volts, the relay will operate, and the 240 volts will be connected to the heater. When the temperature rises above the thermostat's setting, its contacts open, the relay contacts open, and the heater is disconnected. Depending on where you live there may also need to be circuit breakers, protective ground wires, etc.--ask an electrician.


What could cause a 24 volt transformer on a house heater to burn up?

On the 24vac side, this would include any load attached or powered by the transformer. A wire than has gone to ground (shorted), or rubbed into the ductwork (stat wire). The transformer will be rated at xxva, meaning volts X amps aka(watts). Most residential equip. will have a 40va fitted. 40 / 24= 1.66 amps. Any load in excess of this should cause a failure. If you are trying to fix this yourself, put a 2amp automotive fuse in series with one of the 24vac "out" leads and go one by one, isolating the gas valve, wiring to the thermostat, etc, till the fuse quits blowing. Otherwise, call a tech. lc

Related questions

What class is a transformer that converts 110 volts to 24 volts?

A transformer that reduces voltage is classed as a step down transformer.


How do you convert 12 volt trailer lights to 24 volts?

Change the trailer light bulbs to 24 volts and supply a 24 volt source to power them, in that order.


What would the control voltage be for a transformer marked 240v 24vac?

A control transformer marked 240V - 24Vac would have a control voltage of 24 volts.


How transformer get burn?

Current overload from whatever circuit draws current from the transformer? Proper fusing of its supply might protect a transformer from this cause. Or it could have developed a shorted turn fault because the insulation on a winding got old and perished? Or maybe the transformer got damaged if the appliance it is mounted in was dropped?


Is it safe to use a step down transformer rated 16 Volts and 40 VAC in place of required transformer rated 24 Volts and 40 VAC?

Transformers that operate specific devices should be matched to the specific voltage on the device that the manufacturer specifies.


Step down transformer of a specs of 110 primary to 24 v 12va CAn you used a 110v primary to 24v 20 va What is the difference between them?

Yes. The Va numbers indicate the rating of the transformer (12VA indicates that you can draw upto 12/24 = 1/2 Amps at 24 volts and 20VA indicates that you can draw about 20/24 = 0.83 Amps). Usually 20va transformer will cost more than the 12va transformer. So, unless a higher power output is required, it is adequate to use the lower rating transformer. However, you cannot go the other way - if you use a 12va transformer in-lieu of the 20va one, if the application needs more power, then you have a reliability problem. The transformer will have more loss, heat-up and then eventually burn out.


What happens if I plug 24 volts to 220 volts?

If you mean connecting two different voltages in parallel, you would have a "short circuit" where the 196-volt differential is dissipated in any high-resistance point in the circuit, creating a lot of heat for a very short time (as something suffers thermal runaway and catastrophic breakdown). You could get an explosion and fire. On the other hand, if you have a 24-volt DEVICE and plug it into 220 volts, the result would depend upon what kind of device it is. For instance, if it's a 120/24-volt step-down transformer and you plug in the 24 volts to 220, you will be running the transformer "backward" and create 1,100 volts at the "output". If the transformer's design does not include adequate insulation for 1,100 volts, you would have dielectric breakdown, and another possible "short circuit" when things melt and conductors touch each other.


What are 3 reasons why there are not 24 volts at the thermostat when heat or air is called for?

F.A.U turned off Bad transformer Blown low voltage fuse


Can you use a 9volt 500 milliamp transformer for a door bell?

The key is the door bell specification. They typically run on a 24 VAC transformer. You can certainly hook it up and try it with 9 volts, but it probably won't work as intended. 24 Volt transformers are relatively cheap.


How many amps does a 120 Volt irrigation controller draw?

Different controllers have different outputs depending on how many valves are on each zone. In the device there is a control transformer. Look for the VA output of the transformer's secondary side. Mine states 20 VA at 24 volts. To find the amperage use the following equation. I = W/V. Amps = Watts or VA/Volts. Mine can output 20 divided by 24 = .83 amps. This amperage will be the maximum output in amps that the controller can produce to operate the zone valves. To find the current draw of the primary side of the transformer divide the transformers VA by 120 volts.


What is 50VA?

50 VA means about 50 watts. Transformers usually use VA instead of watts because a transformer has very little wasted power, and watts measure power. A 50 va transformer that is 120v. on the primary side will use about .41 amps at 120 volts. On the secondary side, (if it's 24 volts) it will support about 2.08 amps.


How do you convert 230 volts to 12 volt system?

With a Step Down transformer. But you will probably have a hard time finding a 240 volt unit. 120 volts units are readily available. &lt;&lt;&gt;&gt; It depends on how big of a transformer that you are looking for. There are many control transformers in the 50 to 500 VA range that have dual primary and dual secondary. The primary side can be connected to 240 volt or 120 volt and the secondary can be connected for either 12 or 24 volts.