answersLogoWhite

0


Best Answer

Not a whole lot. Assuming that is 120 volt power, 1200 watts would be 10 amps. A standard breaker is 15 amps.

User Avatar

Wiki User

6y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How much 1200 watts on one breaker?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

Why will too many electrical devices operating at one time after blow a fuse or trip a circuit breaker?

The load exceeds the limit of the breaker or fuse. For example a 20 amp breaker on a 120 volt circuit will handle 2400 watts. Exceed that wattage and the breaker will trip or the fuse will blow.


For a 15 amp breaker - suppose I have 8 or 12 outlets - what if on one outlet I use iron box which draws 1500 watts 12.5 amps and on another outlet a floor heater?

If there is any additional load on the outlets greater than 2.5 amps the breaker will trip. Loads of 1500 watts should be on a dedicated breaker. If the total load exceeds 15 amps the breaker will operate. However many of the outlets might supply only lights, TVs or nothing at all, so in those conditions it's OK.


How many watts will a 20 amp douple pole breaker handle?

The formulae for calculating watts to amps is Watts divided by Voltage. Therefore to get from Amps to Watts the calculation is Amps × Voltage. Therefore if you are working on a 240 volt supply the calculation is 20 (Amps) × 240 (Volts) which = 4800 watts.


How many watts does a 15 amp breaker provide?

In a residence assume you are referring to 120 volt supply. Watts = amps x volts x Power Factor. Now Power factor is one for resistive loads like incandescent light bulbs. Power Factor can vary from zero to one when inductive loads like motors are added. So the maximum theoretical wattage would be about 15 A x 120 V. However, you de-rate a breaker to 80% of capacity so as not to continually trip breaker. Therefore, the answer you are looking for in a practical sense is 120 x 15 x .8 = 1440 watts or 1.44 kilowatts.


How many watts does a water pump use?

It would depend on how deep your well is, and how efficient the pump.

Related questions

How much can a 15W circuit breaker handle?

Answer for the US: Breakers are rated in amps, not watts. However, a 15A breaker can handle 15 amps, or about 1800 watts (using 120V), or 3600 watts (using 240V). However, this is only rated for noncontinuous loads (those not lasting for more than three hours). For continuous loads (loads lasting three hours or more), one must derate the circuit breaker by 80%. So for continuous loads, that same breaker should only have 1440 watts (using 120V), or 2880 watts (using 240V) on it.


If installing several base board heaters with various watts what is the max number of watts you can put on one 20 amp 240v breaker?

For safety reasons ( and the National Electric Code) never put more than 75% load on a breaker, so for you case, 20 amp breaker x 75% = 15 amps 15 amps x 240 volts = 3600 watts 3600 watts


Can multiple circuits be connected on one breaker?

Multiple wires can be connected to one breaker but the one breaker IS a circuit. As long as the load is not more than 80% of the breaker capacity (example: a 20 amp breaker can only have 16 amps or 1920 watts at 120 volts) then by code as long as the load is not a specialty outlet of some sort, you can have as many outlets you want.


Why will too many electrical devices operating at one time after blow a fuse or trip a circuit breaker?

The load exceeds the limit of the breaker or fuse. For example a 20 amp breaker on a 120 volt circuit will handle 2400 watts. Exceed that wattage and the breaker will trip or the fuse will blow.


How much watts in one ampere?

Since the equation for watts is: Volts * Amps = Watts that would mean 12 Volts * 1 Amp = 12 Watts


Should a hot water heater be put on a 30 single or 30 double amp breaker?

What governs the type of breaker is the voltage and wattage of the heater elements. If the tank is 120V then you would only use one breaker. The size of the breaker you use will depend on the watts of the element. Watts = amps x volts, Amps = Watts/ volts. Once you establish the amperage then size the wire and the breaker to fit. If the tank is 240V the same rules apply only you would use a 2 pole breaker. IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOBSAFELY AND COMPETENTLYREFER THIS WORK TO QUALIFIED PROFESSIONALS. If you do this work yourself, always turn off the power at the breaker box/fuse panel BEFORE you attempt to do any work AND always use a meter or voltage indicatorto insure the circuit is, in fact, de-energized.


How much kilowatt hours would a clothes iron with 1200watt and 120volts uses in 2 hours?

The iron uses 1.2 kilowatts (1200 watts) in one hour, so it uses 2.4 kilowatt hours in two hours.


If you have a 200A supply with 10 breakers totaling 160A on one leg and 10 totaling 205A on the other can you install a dual 15A breaker on the first leg to add a heated floor with 800 watts?

breaker values aren't additive


How much watt is equal to one ton?

cooling capacty one ton is how much watts


How much is one of the 2012 Olympic medals worth?

£1200


For a 15 amp breaker - suppose I have 8 or 12 outlets - what if on one outlet I use iron box which draws 1500 watts 12.5 amps and on another outlet a floor heater?

If there is any additional load on the outlets greater than 2.5 amps the breaker will trip. Loads of 1500 watts should be on a dedicated breaker. If the total load exceeds 15 amps the breaker will operate. However many of the outlets might supply only lights, TVs or nothing at all, so in those conditions it's OK.


How many watts will a 20 amp douple pole breaker handle?

The formulae for calculating watts to amps is Watts divided by Voltage. Therefore to get from Amps to Watts the calculation is Amps × Voltage. Therefore if you are working on a 240 volt supply the calculation is 20 (Amps) × 240 (Volts) which = 4800 watts.