It stands for 40 volt-amperes (Volts times amps) and is a measure of power. It is equivalent to watts for a resistive load.

User Avatar

Wiki User

13y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What does 40 VA mean in a transformer?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Electrical Engineering

What is the amperage of a 40 va 240 volt by 24 volt control transformer?

The formula for amps is I = W/E. Amps = 40/240 = .17 primary amperage. For the secondary amperage I = W/E. Amps = 40/24 = 1.7 amps.


Rating of transformer?

It's the apparent power (VA) it can deal with.


Does a transformer convert the current from 240 volts to 120 volt?

Transformers are rated in KVA or VA (volt-amps). They transform voltages from one value to another. The current in a transformer is inverse to the voltage. This is why transformers are rated in KVA and smaller ones in VA.


Why does your 24 volts transformer get hot then burn out?

A transformer gets hot if it is run at excessive voltage or excessive current. Either of those two would cause it to overheat. <<>> It sounds like the load on the secondary is greater that what the transformer can supply. A transformer is wound for a specific amperage output at a specific voltage. This is stated on the transformer as a VA or in larger transformers as KVA. If you divide the 24 volts into the VA listed on the transformer you will get the maximum amperage value of the transformer. If the device that you are connecting to the transformer is greater in amperage draw that what the transformer can supply, this will cause the heating effect and if left connected eventually burn the transformer out. A fuse should be installed in the secondary 24 volt output, rated at the maximum output of the transformer. This will limit the transformer to its manufacturer's recommended current output.


Can a 20 VA rated transformer be used in place of a 10VA?

Yes provided the voltages are the same.

Related questions

Can I use a 120 v 24 v 75 VA transformer instead of a 120 v 24 v 40 VA transformer?

Yes that would work. It's all about the ratio. As long as the rated voltage is not exceeded, as there will be a limit to what the insulation can stand, before breaking down. Lower voltages than rated will be safe.


What does the term VA mean when applied to a control transformer?

VA refers to the effective load that is placed upon the Control Transformer (also known as Selection Inrush VA).


What size transformer is generally used on a heating only gas furnace?

usually 40 va


What mean by va in current transformer?

Its simply multiplication of voltage applied and current.


Do you have parts for a wall furnance Transformer part no AT30 Model s7035st wr62?

A generic 115vac/ 40 VA 24 volt transformer will work fine. Mars or Honeywell are the most common.


Does the primary winding VA equal the secondary winding VA when a transformer is loaded?

no becouse transformer function depends on no of coil in primary and secondry coil


What is the efficiency of a transformer that has an input of 600 VA and an output to a load of 580 VA?

96%


Transformer rating is expressed in?

VA or KVA or MVA


Rating of transformer?

It's the apparent power (VA) it can deal with.


What is the amperage of a 40 va 240 volt by 24 volt control transformer?

The formula for amps is I = W/E. Amps = 40/240 = .17 primary amperage. For the secondary amperage I = W/E. Amps = 40/24 = 1.7 amps.


How do you Convert va to kva?

a kva is 1000 vaK is kilo, which means 1000 similar to how a kilometer is 1000 metersTransformers are usually rated in KVA, so a 45 KVA Transformer is a 45 000 VA Transformer


How many 240 volt 4.9 amp draw lights can be run on a 15 kva 2 phase transformer?

The lamp uses 240 x 4.9 VA, that is 1176 VA, so a 15 kVA transformer, which is 15,000 VA, could feed 12 lamps.