The answer is just that: the voltage that the outlet has available. The issue is when you plug a 110 volt appliance into a 220 volt outlet (or vica verca) you are either under powering or over powering the device and can (and probably will) ruin it either way.
<<>>
You should not be able to plug a 110 volt device into a 220 volt outlet due to the different blade configurations. This is why different voltages have different plug ends and receptacles have different blade configurations.
The higher the voltage, the less the current, which allows you to use smaller wire sizes, circuit breaker rating, etc. For example a 1500w/120v hair dryer may draw close to 13 amps, while at 240v the current is around 6.25 amps. The running/operating costs remain roughly the same.
Note
Nowadays the voltages supplied to homes are nominally 120 volts and 240 volts + or - 10%. The actual variation from nominal at any instant in time will depend partly on the distance you are from the power station and partly on the overall load being drawn by the population using the same power service.
However many people still call their home voltages "110" volts and "220" volts and it really doesn't matter because the actual voltage you get could vary from 132 V down to 108 V in the case of the nominal 120 V, and from 264 V down to 216 V in the case of the nominal 240 V.
For more information click on the links to the Related Questions shown below.
Different appliances run on different voltages.If you want to use 110v over here (most USA appliances run on 110) you will need a step down transformer or you will blow the appliance. Other countries (Japan) also use 110v it'salways best to check the appliance or its handbook.
Apart from wire insulation colors, the only difference to wiring something for 120 volts vs 240 volts is the current draw/power factor of the appliance. The larger the power requirement the more beneficial a higher voltage rating becomes in as far as installation costs are concerned.
The higher the voltage, the less the current, which allows you to use smaller wire sizes, circuit breaker rating, etc. For example a 1500w/120v hair dryer may draw close to 13 amps, while at 240v the current is around 6.25 amps. The running/operating costs remain roughly the same.
Please click on the links to the Related Questions shown below.
In North America the standard voltage ratings for conductors are 300 volts, 600 volts and 1000 volts. As you can see the 120 and 240 volts drop into the class of 300 volt wire. This is a great asset to electricians that wire homes, not having to worry about changing insulation ratings when wiring circuits for 120 volts and 240 volts. Most industrial and commercial wiring is done with 600 volt rated wire.
Voltage is nominally between 110 and 120 volts. There is no real difference in terms of the outlet specifications.
The level of insulation would need to be higher for a 240-V wire. It's cross-sectional area would depend on its current-carrying capacity.
No adapter is needed, 110 and 115 volt are interchangeable.
Probably not, but I have yet to see a 150 volt appliance as this is a non-standard voltage. If you are referring to a 115 volt appliance then the answer is yes you can as 110/115/120 volts tend to be used interchangeably in practice and are close enough together to not affect operation of the appliance.
No a 230 volt appliance should not be pluuged into a 110 volt socket (And vice versa) you need to buy a converter that can be plugged into the 110 volt outlet then the appliance can be plugged into the converter.
Yes, a 110 volt device can be plugged into a 125 volt receptacle. The voltage rating on the receptacle is only there as the highest voltage supply that the manufacturer recommends their equipment be connected to.
No, the plugs are different to prevent this and even if you could the lamp would be very dim.
no
Yes.
No adapter is needed, 110 and 115 volt are interchangeable.
zzzzzzzzzzzAAAAAAAAAAAAAAAPPPPPPPPPP !!!!!
Probably not, but I have yet to see a 150 volt appliance as this is a non-standard voltage. If you are referring to a 115 volt appliance then the answer is yes you can as 110/115/120 volts tend to be used interchangeably in practice and are close enough together to not affect operation of the appliance.
No, the applied 110 volt is too high for a 3 volt appliance. The appliance would burn out right away.
Yes - a hair-dryer rated at 120 volts will work in a 110 volt outlet.
Nominally 110 to 120 volt power strip is okay to connect to a standard outlet.
No conversion needed. These are nominal voltages which range from 110 to 120 volts. It will operate fine on the outlet.
Because a toaster does not pull near the current that a cloths dryer does.
Because a toaster does not pull near the current that a cloths dryer does.
No a 230 volt appliance should not be pluuged into a 110 volt socket (And vice versa) you need to buy a converter that can be plugged into the 110 volt outlet then the appliance can be plugged into the converter.