answersLogoWhite

0


Best Answer

The circuit that the GFI controls has a current leak on it. The leakage could be anywhere in the circuit.

To trouble shoot the circuit first shut off the GFI breaker to the circuit in question. Then remove the load (pool light) from the circuit. Isolate the feeder wires with wire nuts on both the "hot" and neutral conductors.

Turn the GFI breaker back on. If the GFI breaker does not trip when it is turned back on, the problem is not in the feeder wires. The tripping problem is caused by the light fixture. If the breaker does trip you will have to find where the moisture is getting into the underground conduit system.


Remove the light fixture and try to completely dry the unit. This can be done with a heat gun by blowing hot air on the fixture to dry it out.


Once you think the fixture is completely dry, without placing the fixture back in its placement in the pool, temporarily connect it to the feeder wires and check to see if the breaker trips. If it does not trip then you have corrected the problem.


What is left to do now is to find out where the leak is that is letting the moisture into the fixture. Once found and completely sealed the fixture can be placed back into service.

User Avatar

Wiki User

8y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

19y ago

Most likely the light has a leak around the cord, allowing water to get to the wires inthe socket

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What is the most likely cause of an underwater pool light continually tripping GFI if it does not appear to be an overloaded circuit?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

What is the solution to reducing a circuit breaker from tripping in 1956 home?

The circuit breaker trips when the circuit it is protecting is overloaded. That happens when the wire is at its limit for carrying current. The solution might be to instal an additional power circuit in the house and to make sure the supply from the street is adequate. In both cases an electrician can advise.


Why does plugging too many appilances into the same circuit cause too much current to flow through the circuit what will happen as a result?

Each appliance has its own amperage. This can be shown by looking at the label of each appliance. A circuit is protected by a breaker which has a trip limit. By continually adding more amperage from different appliances, the circuit becomes overloaded. When the circuits limit is reached because of the additive effect of more appliances to the circuit the breaker will trip. This disconnects the appliance loads from the distribution panel supply and prevents over loading of the conductors of that circuit. Without removing some of the load amperage, the breaker will keep tripping when reset.


How does a circuit breaker use an electromagnet?

The electromagnet in the circuit breaker is used for instantaneous tripping if short-circuit condition arises. At defined current level the electromagnet develops the force high enough to cause the tripping of the mechanism.


The role of the circuit breaker is what?

to prevent a circuit from overloading if too much current flow safely interrupt the circuit if it becomes overloaded


What protects equipment from too much current by tripping a switch that breaks the circuit and stops the flow of electricity?

Circuit Breaker

Related questions

What would cause the engine fuse to continually blow in a 1983 Mazda 626?

Short to ground or overloaded circuit


What is the solution to reducing a circuit breaker from tripping in 1956 home?

The circuit breaker trips when the circuit it is protecting is overloaded. That happens when the wire is at its limit for carrying current. The solution might be to instal an additional power circuit in the house and to make sure the supply from the street is adequate. In both cases an electrician can advise.


What type of failure might blow the fuses?

A dead short to ground or an overloaded circuit.A dead short to ground or an overloaded circuit.


What does tripping off means?

In an electrical context, 'tripping off' means the circuit breaker breaking the circuit because of a fault.


Why would a computer wire melt?

Short in the circuit or the circuit was overloaded.


What is designed to open an overloaded circuit and prevent overheating?

A circuit breaker or a fuse.


What is cascade tripping?

It's when a failure of one circuit leads to another circuit to fail. This can be intentional,for protection purpose, or it may not be intentional. Cascade tripping is common in sequenced circuit.


Why does plugging too many appilances into the same circuit cause too much current to flow through the circuit what will happen as a result?

Each appliance has its own amperage. This can be shown by looking at the label of each appliance. A circuit is protected by a breaker which has a trip limit. By continually adding more amperage from different appliances, the circuit becomes overloaded. When the circuits limit is reached because of the additive effect of more appliances to the circuit the breaker will trip. This disconnects the appliance loads from the distribution panel supply and prevents over loading of the conductors of that circuit. Without removing some of the load amperage, the breaker will keep tripping when reset.


Why does your circuit breaker trip when your heater comes on?

That circuit is overloaded. Call an electrician to fix it for you.


What makes a time delay fuse burn out?

Short in circuit wiring or circuit overloaded.


Cause of a circuit breaking tripping?

Tripping is caused by excessive current, which is usually the result of a fault in cable or equipment. The circuit breaker is there for safety and it trips to prevent a possible fire starting.


What is the function of the fuse or circuit breaker in a circuit?

A circuit breaker/fuse is designed to protect the wiring from getting overloaded.