30 amp breaker with #10 gauge copper wire
LRA (locked rotor amps) is not used to calculate the breaker size. Breaker's are used to protect the size of the conductor that is connected to it. Motor calculations are based on the motor's FLA (full load amps).Conductor size is 125% of the motor's FLA.Breaker size is 250% of the motor's FLA.This is the only occasion when the breaker is sized larger that the conductors maximum amperage rating. This is due to the motor drawing up to 300 to 600% of its FLA when starting.If you state the motor's wattage, voltage or amperage this calculation can be calculated here.
This is determined by the size motor and the amount of amps the motor draws, be on the safe side and consult the owners manual or an Electrician. <<>> The sizing of the breaker and feeder wire is based on the amperage of the compressor. Look on the name plate and find the amperage. The amperage on the nameplate then has to be multiplied by the motors full load amperage and that value is used for the wire size. Because the load is a motor the FLA is again multiplied by 250% to size the breaker. This takes into allowance the high starting current of a motor from 0 to 100% RPM.
running wire 12-2 300ft w/9ea. 27watt lights what size breaker should be used
50 amp breaker wired with AWG # 6 wire.
The size breaker you use is determined by the size wire used in the circuit. If you use AWG #12/2 wire then use a 20 amp breaker. If you use AWG # 14/2 then use a 15 amp breaker.
The circuit breaker is used to protect the conductor that is connected to it from an overload condition. On a motor load the breaker has to be sized 250% of the motors full load amperage. Some circuits can be only loaded to 80% capacity and this is governed by the sizing of the breaker. Without knowing what the load amperage is, this question can not be answered.
A 15 amp dedicated circuit breaker should be used for the dishwasher. The disposal can be wired to the general kitchen 15 amp circuit.
A breaker is based on the amount of current that the motor draws. This amperage should be taken off of the motors nameplate. In motors of a specific horsepower the amperage is proportional to the voltage the motor uses. Without the motors voltage this question can not be answered.
You use the correct size breaker depending on the size wire in the circuit. If the circuit is wired with AWG #12 wire use a 20 amp breaker. If it is wired with AWG #14 wire then use a 15 amp breaker.
Depends on how many amps it pulls and the size of the wire in the circuit.
A 1/2 HP 115volt motor draws 9.8 amps. This is a nominal book amperage for a 1/2 HP motor, check the nameplate for an accurate value. A breaker, to protect this size motor, has to be rated at 250% of the motors full load amps. In this case a 25 amp breaker in needed. If using the actual nameplate amperage, multiply it by 250% to find the size of the breaker to use. If the motor used 230 volts as a supply a two pole 15 amp breaker would work.
YES ALL CONECTIONS MUST BE SQUEAKY CLEAN AND THE PROPER SIZE POWER CORD MUST BE USED..