To answer this question, wire size is rated in the amount of amperage that it can legally carry. The formula to find amperage when the HP is known is I = HP x 746/1.73 x E x %eff x pf.
A standard motor's efficiency between 5 to 100 HP is .84 to .91.
A standard motor's power factor between 10 to 100 HP is .86 to .92.
Amps = 30 x 746 = 22380 = 22380/ 1.73 x 480 x .87 x .87 = 22380/629 = 35.6 amps.
The electrical code states that a motor conductor has to be rated at 125% of the motors full load amperage. 35.6 x 125% = 44.5
A #8 copper conductor with an insulation factor of 75 or 90 degrees C is rated at 50 and 55 amps respectively.
SOOJW is limited to 300 volts and should not be used on 480 volts
Yes the rated voltage is a maximum. A 250 v cord might be slightly thicker than one for 125 v. <<>> The voltage rating of an electrical extension cord is the insulation factor of the cord. These cords come in two insulation ratings, 300 volts and 600 volts. If the voltage rating is within the parameters of the cord maximums then it is safe to use it on that voltage. The amperage of the cord is based on the wire size of the cord's conductor. The rating of 10 amps will fall within the #14 cord size. Remember the longer the cord the larger the wire size should be to prevent voltage drop at the connected load end.
Power is the product of amps x volts, it has nothing to do with wire size.
Need to know the voltage of the motor. Use this formula, I = W/E, Amps = Watts/Volts. Once you have the amperage then ask, what size wire is needed for (your amperage) at (your voltage).
Need motor voltage, amperage and phase to give you an anwer.
SOOJW is limited to 300 volts and should not be used on 480 volts
With that size of load and a voltage of up to 300 or 600 volts, any extension cord can be used.
With that size of load and a voltage of up to 300 or 600 volts, any extension cord can be used.
The starter motor of a diesel generator is a DC motor. Depending on the size of the diesel engine the starter motor could be 12 volts or 24 volts. Sometimes more that one battery is used at the specific voltage. These batteries are connected in parallel to create more amp hour cranking power.
12/2 with ground.
I would go with 20 amp 3 pole 15 amp will also do
Yes the rated voltage is a maximum. A 250 v cord might be slightly thicker than one for 125 v. <<>> The voltage rating of an electrical extension cord is the insulation factor of the cord. These cords come in two insulation ratings, 300 volts and 600 volts. If the voltage rating is within the parameters of the cord maximums then it is safe to use it on that voltage. The amperage of the cord is based on the wire size of the cord's conductor. The rating of 10 amps will fall within the #14 cord size. Remember the longer the cord the larger the wire size should be to prevent voltage drop at the connected load end.
No they don't
It depends on what you need the power cord for. Usually you will have a manual that can tell you exactly what is needed. If not, just look carefully at the connecting points and see what the shape/size of the power cord needed is. Depending on the appliance, you need to pick out the right cord it tells you it needs.
Power is the product of amps x volts, it has nothing to do with wire size.
Power is the product of amps x volts, it has nothing to do with wire size.
depends what the source voltage isone horsepower equals to 746watts (assuming 100% efficiency)746 watts divided by voltage source equals current (amps)AnswerIn countries, such as the USA, where the horsepower is still used as a means of measuring power, it is always used to measure the output power of a motor.So, in order to determine the current drawn by the motor, you will first need to find out its input power. The input power is the output power divided by the machine's efficiency. Once you know its input power, then you can find its current by dividing the input power by the supply voltage. In practise, you will need to use a wattmeter to determine its input power.