Wire is sized by the load amperage. The formula for amperage when the HP is known is I = HP x 746/1.73 x E X %eff x pf.

A standard motor's efficiency between 5 to 100 HP is .84 to .91.

A standard motor's power factor between 10 to 100 HP is .86 to .92.

I = 60 x 746 = 44760/ 1.73 x 480 x .89 x .89 = 44760/658 = 68 amps.

Motor feeders have to be sized to 125% of the motors full load amps. 68 x 125% = 85 amps

A #3 copper conductor will limit the voltage drop to3% or less when supplying 85 amps for 220 feet on a 480 volt system.

User Avatar

Wiki User

11y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size wire for a 480 volt 60 hp motor 220 feet away?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What is the start up amps on a 200 hp 3 phase 480 volt motor?

i have 200 hp motor what i need cable size in 100 feet distance


What size battery do you need for a 4.5 volt DC motor?

4.5 volt battery sold only in Russo


What kind and length of electrical wire do you need for a 2 hp single phase 220 volt motor 50 feet away?

The motor would take 10-12 amps which would need wire of 1.5 mm2 or larger. For a permanent installation use the next size, 2.5 mm2 cross section.


What the the correct size capacitor for a three quarter horsepower 110 volt motor?

110v 40 uf


What size wire for 240 volts 200 amp service 200 feet away?

A 3/0 copper conductor will limit the voltage drop to 3% or less when supplying 200 amps for 200 feet on a 240 volt system.


What size wire do you need for 20 amp 220 volt electric motor?

12 AWG in most circumstances.


Can you use a 3 volt battery to run an 8 volt motor?

You can but the motor may not run, however you will not burn the motor.


Can you run 22 kw 600v 3 phase induction motor?

Yes this size motor can be operated by bringing a 600 volt three phase supply to it.


Can a put a Receiver from a lower Volt motor to a Higher Volt motor so i can control it with the transmitter i have?

NO


How do you connect a small LED light to a 3 volt watch battery 1.5 feet away?

sucka dick?


What size wire needed for 200 amp service 400 feet away direct buried single phase 240 volt 3 wire?

Assuming you are working with 240v, you need 4/0 copper conductors.


Can you run a 570 volt motor on 480 volt three phase power supply?

No, the voltage difference is too much. A 570 volt motor falls in the 600 volt range which is separate from the 480 volt range of three phase systems.