take your gages and put them on the beginning of the evaporator (afte metering device or txv) and look at saturation temp then get your temp at the suction line (before the compressor)

User Avatar

Wiki User

15y ago

What else can I help you with?

Related Questions

How do you mesure superheat?

take your gages and put them on the beginning of the evaporator (afte metering device or txv) and look at saturation temp then get your temp at the suction line (before the compressor) then take you first temp and your second temp and subtract you highest temp from you lowest temp and that would be your superheat


How can calculate super heat?

To calculate superheat, subtract the actual temperature of the refrigerant from its saturation temperature at the current pressure. This will give you the superheat value, indicating how much the refrigerant has increased in temperature above its saturation point. Superheat is important in ensuring optimal functioning of air conditioning and refrigeration systems.


What is the superheat?

17 to 20 degrees is normal.you should always check dry bulb at return air and outside temp to determine the correct reading


What is the ideal superheat?

17 to 20 degrees is normal.you should always check dry bulb at return air and outside temp to determine the correct reading


Do you add freon on a low superheat or high superheat?

add


When was Superheat created?

Superheat was created on 2000-01-25.


How do you calculate the temperature range?

just subtract the highest temp. - lowest temp


Why is the degree of superheat of refrigerant does not exceed 5 degree centigrade?

We require to superheat the refrigerant to ensure that no liquid enters in the compressor.So in most of the cases degree of superheat is kept 2 to 3 deg c


What are the right temperature on superheat and sub cool?

The right temperature to superheat and sub cool a substance varies greatly. Water for example takes temperatures above 212 degrees to superheat and temperatures below 32 degrees to sub cool.


How do you calculate the temperature change without knowing the initial or finish temp?

You cant.


What amount of superheat is recommended for R-22?

Superheat depends on the type of metering device you are using in the equipment as well as the current state of the load. With a fixed orifice, the superheat will be high, about 20 to 30 degrees when the box is warm, down around 10-15 when the box is cold. With a txv, the superheat should be constant, normally between 10-15 degrees. It is best to check the superheat at the outlet of the evaporator. this will ensure that the compressor does not slug with liquid refrigerant.


How do you record superheat in an HVAC unit?

a pencil