The best rule of thumb I have found is:

Length X Width / 144 * 288 = Max. CFM

I have used this formula to size many HVAC systems. It has always worked. For example, a 5 ton unit should have a 30x36 grille(2-18X30 filters). (30x36)/144*288=2160 max cfm.

Return Air should be sized at 200 square inches per ton according to AirMate and other filter grille manufacturers to achieve 2.0 static pressure. The Return Air Duct should have an unobstructed 6 square inches per 1000 BTU of cooling.

User Avatar

Wiki User

15y ago

What else can I help you with?

Related Questions

What size should the return air grill be for a 5 ton ac unit?

Your ac contractor or engineer will determine the correct size.


If you are using a 20X20 AC filter and need to use a 20X25 where can you find the grate or register for the new filter and what is it called?

What you are refering to is called a return filter grill and there are tons to chose from, ( from ) tons of places. Home Depot, Lowes, and the likes of these places or your Heating Air/Conditioner Wholesaler close to your area. Also try typing in Central Air Return Air Filter Grills in your search bar. The Bigger the better is the rule of thumb with return air filter grills to a reasonable point . 600 cubic feet a minute is what I design air flow quantity for on my basic stuff. It is my opinion you are better off with a less expensive filter and a slower flow rate design through your return air filter grill than to use a expensive but usually highly restrictive filter in a smaller return air filter grill that is already restrictive in itself. Don't take me wrong here!!!!! ( Those Super High Quality Return Air Filters are Wonderful , usually ), Just make sure you have plenty big enough filter grill return area size to accomadate them in your system. Hope this helps: Jimiwane


How big should an air return be how many square inches per square foot of house?

Air return duct and filter grille size is dictated by the size of the unit (CFM) not the size of the house.


How do you change an AC filter?

the filter is easy to change. it should be in one or two places, the return grill which will be in a hallway near the thermostat. this is the most common location if your furnace is located someplace not easily gotten to. the return grill should have a small latch(es) or screws/nuts keeping it closed, the grill is hinged to allow it to swing open for easy filter changes. simply remove old filter check the size that's written on it and replace with same size assuming it fit right. lil trick if it's high up turn on the fan this will hold the filter when you have your hands full balancing on a ladder/chair. replace it every 2 to 3 months depending how it looks. If your furnace is in the garage or a closet and you only have a flat return grill the filter will be in the bottom of the furnace, just open the bottom door and you will see it, pull it out and replace. the filter needs to have some kind of support in it, checkerboarded thread at least to keep it from being sucked into the blower motor when it starts collecting dust. they only cost a couple of bucks at walmart or a do it yourself store. pleated ones have more surface area and work great. hope i helped. viking40


What size return air grill for a 36000 BTU heating system?

The size of the return air grill depends on the size of the forced air fan. The return air grid to reduce noise should be 5 to 8 times the size of the fan outlet. A 36000 btu heating system often has between a 500 to 1500 CFM fan the outlets on these fans are often between 30 and 80 square inches so the grid should be between 150 and 600 square inches (depending on the fan), the bigger you can fit the better. If you can fit it I'd put in a 12 x36 grill (432 sq in) but a 12 x 24" (288 sq inch)grill should work well too.


What size return air grill for a 60000 BTU heating system?

The size is determined by the ac contractor or engineer.


What size return air grill for a 48000 BTU heating system?

48,000 btus is equal to 4 tons of air flow, 12,000 btus per ton. You need 144 sq in per ton. Return grill should be 24x24. 48,000 btus is equal to 4 tons of air flow, 12,000 btus per ton. You need 144 sq in per ton. Return grill should be 24x24. 48,000 btus is equal to 4 tons of air flow, 12,000 btus per ton. You need 144 sq in per ton. Return grill should be 24x24.


What size should the return air grill be for a 3.5 ton ac unit?

For a 3.5-ton AC unit, the return air grill should typically be sized to allow for adequate airflow. A general guideline is to allow about 400-450 CFM (cubic feet per minute) of airflow per ton of cooling. Therefore, for a 3.5-ton unit, you would want a return grill that can accommodate around 1,400 to 1,575 CFM. It's important to consult with an HVAC professional for precise sizing based on your specific system and home layout.


Where can I find a high-quality return air grill for my HVAC system?

You can find a high-quality return air grill for your HVAC system at home improvement stores, HVAC supply stores, or online retailers specializing in HVAC equipment. Be sure to look for a grill that is the right size for your system and made of durable materials for long-lasting performance.


What size return grill do you need for a 15' x 17' downstairs master bedroom - Two story 4100 sq ft two units 5 ton down 4 ton up?

What size supply register are you using? The return register should match the supply. If the return is too small you will have positive air pressure in the room, and if too large you will negative air pressure.


What size lens filter do I need for my camera?

To determine the size of the lens filter you need for your camera, look for the diameter measurement on the front of your camera lens. This measurement is usually in millimeters and indicates the size of the filter you should purchase.


How do you calculate the amount of DE filter for a specific filter size?

The label on the Filter or the Manual should tell you. Otherwise you should be able to contact the manufacturer, perhaps via their website, to find out. It can vary depending on make and model, not just size.