answersLogoWhite

0

No, the voltage gap between the two voltages is too large.

User Avatar

Riley Glover

Lvl 10
2y ago

What else can I help you with?

Continue Learning about Electrical Engineering

Can you collect one 220 volt phase from a 380 volt three phase plug?

Answer for UK and countries running a 50 Hz supply service.The voltage potential of 380 volts is not common to North America.It will probably be difficult to tap into the plug to get the voltage.If you have a three phase 380 volt supply from a source then you can obtain a single phase voltage of 220 volts from it. 220/380 is a wye voltage connection. 380 divided by 1.73 will give you 220 volts. L1 - N = 220V, L2 - N =220V, L3 - N = 220V. L1 - L2 = 380, L2 - L3=380, L3 - L1 = 380.


Why 380 volts line to line if connect line to neutral is 220 volts?

A voltage of 380 volts is a three phase voltage. On a three phase four wire system, each phase leg to neutral (grounded) will give you 220 volts. This voltage is obtained by dividing the phase voltage by 1.73, as the phase legs are generated 120 degrees from each other. Square root of three is 1.73 divided into 380 equals 220 volts.


How many amps drawn a 110KW motor?

Watts = Volts times Amps. Therefore, if the voltage was 220 volts, the motor would draw 500 amps. If the voltage was 4,000 volts, the motor would draw 27.5 amps. The voltages for large powerful motors tend to be relatively high, for example in the 380 Volts to 11,500 Volts range.


What is the Amperage of a 20 HP motor at 380 VAC 3 phase 50 Hertz?

20 HP Three phase 360 volt what is the amps


What is voltage phase to phase 380 3 phase?

Voltage phase to phase in a 380V 3-phase system refers to the voltage measured between any two of the three live conductors in the system. In a balanced 3-phase system, the phase to phase voltage is equal to the line voltage, which is 380V in this case. This voltage is commonly used in industrial and commercial applications to power heavy machinery and equipment. It is important to note that the phase to phase voltage is higher than the phase to neutral voltage in a 3-phase system.

Related Questions

Is it safe to connect 380 volts 3 phase supply to 220 volts 3 phase supply?

No.


Is 380 volts electric motor a single phase or 3 Phase?

It is probably a three phase 50 Hz motor.


How do you convert 3 phase star configuration 380 volts supply into 220 volts supply?

The process of obtaining 220 volts from 380 volts is quite simple. 380 volts is a three phase four wire system voltage. The 220 volts is obtained by taking the sq. root of 3 which equals 1.73 and dividing it into the phase voltage. 380/1.73 = 220 volts. This holds true with any three phase four wire voltage system. 208/1.73 = 120 volts, 415/1.73 = 230 volts, 480/1.73 = 277 volts and 600/1.73 = 347 volts. This lower voltage is present on any of the three phase legs of the three phase system to the neutral which is grounded on a wye connection.


How can I use 380v 3 phase to power 220v 3phase motor?

f your supply is a Y connected transformer (4 wires COM) with a phase to phase voltage of 380 volts (voltage between any two of the hot wires) , utilizing a true Y connection to your load (connections of one hot lead and neutral for each phase to your load will give a voltage of 380 ÷ sqrt 3 = 380 ÷ 1.732 = 220 volts.


Can you collect one 220 volt phase from a 380 volt three phase plug?

Answer for UK and countries running a 50 Hz supply service.The voltage potential of 380 volts is not common to North America.It will probably be difficult to tap into the plug to get the voltage.If you have a three phase 380 volt supply from a source then you can obtain a single phase voltage of 220 volts from it. 220/380 is a wye voltage connection. 380 divided by 1.73 will give you 220 volts. L1 - N = 220V, L2 - N =220V, L3 - N = 220V. L1 - L2 = 380, L2 - L3=380, L3 - L1 = 380.


Can you run 220 volt motor compressor a 380 volt supply using power inverter?

No 380 volts is too wide a spread to use a 220 volt motor on.


How do you run 220v from 380 fuse panel Ship Supply is 380 and I need to operate 220 motor.?

You can get a buck / boost transformer which will step down the voltage. What will be important is phase supply.


What is the size of XL PE cable for 380 Volts in 125 KW motor?

If it's a 380 v 3-phase supply, the current is up to 300 amps which could be supplied over a short distance by XLPE cable with 70 sq. mm cross-section conductors.


Why 380 volts line to line if connect line to neutral is 220 volts?

A voltage of 380 volts is a three phase voltage. On a three phase four wire system, each phase leg to neutral (grounded) will give you 220 volts. This voltage is obtained by dividing the phase voltage by 1.73, as the phase legs are generated 120 degrees from each other. Square root of three is 1.73 divided into 380 equals 220 volts.


What is the simplest way to run a 3 phase 380 V motor of about 1 KW directly on 220 V single phase supply without resorting to rewinding or frequency converters?

You cannot run a three phase motor on single phase power. You'll burn the motor up within minutes. By the way, I've never seen or heard of a 380 volt motor. Do you mean a 480 volt motor? If so, the only way you can power it is with the correct full voltage and a 3 phase power supply.


How do you calculate starting current of 380 volts 3phase 50 hertz AC motor?

Dear Sir,I want to know that how much draw starting current of 380 volts 3 phase 50 hertz AC motors as per rating values?


How do you get a 220 volt single phase from 380 volt 3phase synchrounos generator?

220 volt single phase from 480 volt 3 phase that one wire taken one phase and second wire connected in earth point. we get 220 v The above answer is incorrect, one phase from a three phase 480 volt system will give you 277 volts to ground. You must use a transformer to get the voltage you need.