answersLogoWhite

0

You shouldn't have to clean the contacts. If they aren't working, it's often due to damage from arcing. However, you can use compressed air, air in a can, or electrical contact cleaner, only after the main bus is de-energized and the breaker is removed from the panel. Contact cleaner is a liquid, and should not be sprayed into a live bus or breaker.

User Avatar

Wiki User

16y ago

What else can I help you with?

Continue Learning about Electrical Engineering

What is a reusable safety switch that breaks the circuit when the current gets too high?

In the electrical trade, this device is known as a circuit breaker.


What can happen if the gas pressure in SF6 CB is dropped below the specified level?

SF6 is used to increase the dielectric strength of the gap in the circuit breaker. If the gas pressure is too low, the dielectric strength will be inadequate to break the voltage applied across the breaker contacts. This means electricity will continue to arc across the contacts when opened, causing the breaker to heat up and likely fail catastrophically (explode). Most gas breakers have low gas alarms and trip contacts. If there is no way to bypass the breaker, a low gas trip contact can be used to open the breaker before the gas pressure gets too low to allow openning.


Why does an electrical breaker trip when you use a lot of appliances in the house?

since circuit breaker consists of coils they get heated up when high current flows, when this happens the coil get energised and pull the moving contacts to open thus the circuit breaker opens when high current flows.


Can a circuit breaker go bad just by turning it off and on?

A breaker is a mechanical device and certainly would wear some with manual on and off usage, but it should be minimal and should not cause a problem unless it were defective. There are many commercial applications where the breaker is used for daily on/off use for lighting and other functions. The breaker can fail by having a mechanical part malfunction or perhaps arcing between contacts that would corrode or fuse mechanical contacts.


What electrical safety devices can be reset and used again?

An electrical safety device that can be reset and used again fits the description of an electrical circuit breaker.

Related Questions

Vacuum bottle in vacuum circuit breaker?

Is a breaker whose contacts are in vacum cylinder. this done so the contacts will not be burnt and destroyed by the electrical arc draw while opening under load.Used in high voltage and high amp conditions.


What are Breaker point contacts are made of?

Breaker point contacts are typically made of a tungsten alloy or platinum for durability and to withstand the high temperatures and electrical arcing that occur during operation. These materials have good conductivity and resistance to erosion, making them suitable for the challenging conditions within an ignition system.


Why do cars light sockets have a goop in them?

To keep the electrical contacts clean and corrosion free.


What should be used to clean electrical contacts?

if they are pitted you can use emery cloth and a can of contact clea.ner


Were is the platinum in a circuit breaker?

There isn't, the contacts in a circuit breaker are plated with silver.


Where is the silver in curcuit breakers?

Silver is typically found in circuit breakers as a component of the contacts. Silver is a good conductor of electricity and is used in the contacts to efficiently carry the electrical current, allowing the circuit breaker to function effectively.


What is a breaker and what is it used for?

An electrical breaker is a safety device used to open a circuit that has an electrical fault on it.


Is the breaker switch loose in your electrical system?

It is important to check if the breaker switch in your electrical system is loose.


Is the circuit breaker switch loose in your electrical system?

Is the circuit breaker switch loose in your electrical system?


Can a breaker be bad and not trip when there is an electrical overload?

Yes, a breaker can be faulty and fail to trip when there is an electrical overload.


What is the recommended range breaker size for a circuit breaker in a residential electrical panel?

The recommended range breaker size for a circuit breaker in a residential electrical panel is typically between 15 to 20 amps.


What is air circuit?

You may be referring to an air circuit breaker or, more accurately, and air-blast circuit breaker. This is a type of high-voltage circuit breaker in which the electrical arc, drawn when it opens, is stretched and snapped by a blast of air directed between the separating contacts -so the air is used as a method of extinguishing the arc. Often, these breaker's mechanisms are also driven by compressed air.