A three phase panel will not give you 110 and 220 volts. A three phase four wire panel will, but not at these voltages. The nearest voltages will be 120 and 208 volts. The 120 volt is the wye voltage of 208 volts. 208/1.73 = 120 volts.
A single phase three wire panel will give you 110 and 220 volts.
Power = volts times amps, so an appliance drawing 10 amps at a line voltage of 110 volts is consuming 1,100 watts. Keep in mind, however, that in a non purely resistive load, the phase angle of amps to volts might not be zero degrees, so the calculation becomes more complex, and depends on power factor, or phase angle.
AC voltage conversions are usually done with transformers. Most commonly, a 3 phase 277/480v system is transformed to a 3 phase 120/208v system. You can, however transform to anything you like with the proper transformer. If you are trying to convert 480v single phase to 240v single phase, such as for home use, then ask for that type transformer. It would use only 2 phases of the 3 phase system. Using 2 phases is called single phase and there are reasons for this that are beyond the scope of this answer. 220v and 110v are field measurements of what is considered 240v and 120v when ordering equipment or applying code.
It is a reference to let an electrician know what voltages can be applied to the distribution panel. Along with this data will be the amperage that the distribution panel can legally handle. It lets the electrician know that the distribution is to be used in North America and to be used on a single phase, split phase secondary supply.
You need to rewire to a lower voltage at panel or get a transformer that steps down 277 to 110 volts. Make sure wire is sized for new load as well as breaker.
Depending on what you're trying to charge, if it doesn't require too much power, you might want to look into a 220 to 110 volt `stepdown' transformer. What? I want to raise the voltage, not lower it! Ok, so use the transformer in reverse. All of a sudden, 110 volts in, will give you 220 volts out. Just make sure the transformer has enough current carrying capacity to handle the load. An electrical supply outlet should be able to help you get what you need.
Yes, the standard single-phase electrical system in the US is 110/120 volts at 60 Hertz.
Your incoming 208V 3 phase power supply will also need an incoming neutral of the same conductor size. Then any single pole breaker installed in the panel will have 110 volts to the neutral. That is you can run 208V 3 phase motor circuits from a three phase breakers in the panel and any number of 110V circuits from single pole breakers.
With a voltmeter Keep volt meter terminal on phase and neutral wire and it will show the exact volatage
To convert 110 kVA at 440 volts to amperes, you can use the formula: Amperes = kVA / (Volts x 1.73) for three-phase systems. In this case, 110 kVA / (440 volts x 1.73) ≈ 143.37 amperes.
There are small water heaters that run on 110 volts. However if yours is a large 240 volt heater and you only have 110 volts going to it, then it is fused and one on the fuses has blown in the service panel.
Answer for USA and Canada power supply service. Electrical panel layout might explain where the two numbers come from on a single phase installation On a electrical panel boards the wiring numbers go from left to right, top to bottom. There are 2 hot legs coming into the panel. L1 and L2. Breakers on L1 are 1,2,5,6,9,10. Breakers on L2 are 3,4,7,8,11,12. This is a 12 circuit board. This configuration allows every two adjacent breakers to connect to 240 volts. Example 1 and 3, 3 and 5, 5 and 7, 7 and 9, 9 and 11. Same with the even number side. So you see that a two pole breaker connects across the two hot legs L1 and L2 no matter where it is on the panel board. Any of these breakers on a panel board to the neutral will give you 120 volts no matter if the supply leg is L1 or L2. Just remember L1 to Neutral equals 120 volts, L2 to Neutral equals 120 volts, L1 to L2 equals 240 volts. The amperage of a breaker is a limit of the amount of amperage it will allow to pass before it will trip. The wire has to be the right size for the breaker. Under sized wire will heat up if more current is applied to it that its rating will allow.
The voltage of 277 is the wye connection of a 480 volt three phase supply. The only way to reduce 277 to 120 volts is with a step down transformer.
To calculate watts, you need to multiply the voltage (in volts) by the current (in amps). For the 208 volts, 8 amps heating element: Watts = 208 volts * 8 amps = 1664 watts For the 110 volts, 8 amps heating element: Watts = 110 volts * 8 amps = 880 watts
Power = volts times amps, so an appliance drawing 10 amps at a line voltage of 110 volts is consuming 1,100 watts. Keep in mind, however, that in a non purely resistive load, the phase angle of amps to volts might not be zero degrees, so the calculation becomes more complex, and depends on power factor, or phase angle.
The United States is one country that uses 110 volts. Also, Mexico and Canada are also other countries that use 110 volts.
Answer 1: TV's use single-phase power. Answer 2: TV's use single phase power of 220 or 110 volts ac power depending on what part of the world you live in.
AC voltage conversions are usually done with transformers. Most commonly, a 3 phase 277/480v system is transformed to a 3 phase 120/208v system. You can, however transform to anything you like with the proper transformer. If you are trying to convert 480v single phase to 240v single phase, such as for home use, then ask for that type transformer. It would use only 2 phases of the 3 phase system. Using 2 phases is called single phase and there are reasons for this that are beyond the scope of this answer. 220v and 110v are field measurements of what is considered 240v and 120v when ordering equipment or applying code.