A loss of excitation will cause the generator to start drawing more and more reactive power over time. Over the first few seconds, and until about thirty seconds after the LOE (depending on the load on the generator before the loss of excitation occurred), active power will stay relatively constant, but reactive power will continue to be absorbed from the rest of the system, and voltage levels will drop. Eventually, the magnetic field between the stator and rotor degrades too much, pole slipping and loss of synchronism will occur. At this point, catastrophic damage will likely have been done to the generator.

User Avatar

Wiki User

∙ 15y ago
User Avatar

What else can I help you with?

Continue Learning about Electrical Engineering

What are the major causes of loss of excitation on generators?

The major causes of loss of excitation on generators are due to an open circuit or a short circuit in the field winding. This may also be caused by a breakdown of the insulation system.


Which relay is used to detect the loss of excitation in generator?

A loss of field relay.


What happens if excitation fails in parallel oprating generator?

when excitation fails,Reactive power will be supplied by the system to which the generator is connected and generator will work as induction generator and its speed will rise a little. generator which was in over excitation mode will work in underexcitation.but there is under excitation limit which should not be reached so we should detect loss of excitation and trip generator


Why loss of field-protection is important?

loss of field protection is important because when a synchronous generator looses field excitation its acts as an induction generator and draws reactive power from the system which heats and damages rotor so as soon as the loss of field excitation is sensed the generator breaker should be opened as the rotor and the stator would both heat up and could damage. Best Regards, Ayaz Ahmed


What components comprise the excitation current of a transformer?

A transformer's excitation current can be resolved into two components. The first is in phase with the primary voltage, and is responsible for the losses. The second lags the supply voltage by 90 degrees, and is responsible for magnetising the core.

Related Questions

What are the major causes of loss of excitation on generators?

The major causes of loss of excitation on generators are due to an open circuit or a short circuit in the field winding. This may also be caused by a breakdown of the insulation system.


Difference between static excitation system?

It is called static excitation when you make use of solid state components like diode and thyristors to convert to pure dc and to use this dc for field excitation of synchronous generators. The field winding of synchronous generators can be excited by dc source only. It is called brushless excitation because use of carbon brushes are not made here.It is called dynamic excitation is when you make use of rotating brushes. Excitation is necessary to produce reactive power and also to regulate the voltage of synchronous generators.


Which relay is used to detect the loss of excitation in generator?

A loss of field relay.


How the DC generator are classified according to field excitation?

on the basis of field excitation, dc generators are classified into the following types:-1- separetly excited dc generators2-self excited dc generatorsthe behaviour of a dc generator on load depends upon the method of field excitation adopted


How the KVAR supplied by synchronous generator?

Synchronous generators supply reactive power (measured in kilovolt-amperes reactive or KVAR) by adjusting their excitation level. When the excitation is increased, the generator can produce more reactive power, which is essential for voltage regulation in the power system. Conversely, if the excitation is decreased, the generator can absorb reactive power. This ability to control reactive power makes synchronous generators crucial for maintaining system stability and voltage levels in electrical grids.


What happens if excitation fails in parallel oprating generator?

when excitation fails,Reactive power will be supplied by the system to which the generator is connected and generator will work as induction generator and its speed will rise a little. generator which was in over excitation mode will work in underexcitation.but there is under excitation limit which should not be reached so we should detect loss of excitation and trip generator


When excitation failure?

Excitation failure occurs when a generator or synchronous machine fails to maintain its magnetic field, leading to a loss of voltage and stability. This can result from issues such as a malfunctioning excitation system, loss of a power supply to the exciter, or mechanical failure. The consequences can include decreased system performance, potential damage to equipment, and disruptions in power supply. Proper monitoring and maintenance of the excitation system are crucial to prevent such failures.


What is the effect of a increasing the excitation current?

Increasing the excitation current in an electrical machine, such as a generator or motor, typically raises the magnetic field strength. This can lead to an increase in output voltage for generators or enhance the torque and performance in motors. However, excessive excitation can cause saturation of the magnetic core, leading to diminished returns and potential overheating. Proper management of excitation current is essential for optimal machine performance and longevity.


What is over excitation of field windings?

Over-excitation of field windings refers to a condition in synchronous machines, such as generators, where the field current exceeds the rated value, leading to an excessive magnetic field. This can result in increased voltage output and potential overheating of the machine. Prolonged over-excitation can damage the windings and other components due to overheating and insulation breakdown. It is critical to monitor and control the excitation levels to maintain safe and efficient operation.


What rhymes with ovation?

Nation, automation, celebration, excitation, deliberation, excitation, penetrationcelebration, excitation, deliberation, excitation, penetration


Why 3 phase diesel generators run undervoltage?

The excitation voltage is too low. Turn the field voltage "pot" to raise the field voltage while watching the output generator voltage.


How do you calculate excitation frequency?

Excitation frequency can be calculated as the reciprocal of the excitation period, which is the time interval between two consecutive excitations. The formula is: Excitation frequency = 1 / Excitation period. Alternatively, if you know the excitation waveform (e.g., sine wave), you can determine the excitation frequency from the period of that waveform.