answersLogoWhite

0

It is wise to start thinking of power in DC circuit. If a load is connected to a power source in a DC circuit, the corresponding VOLT CURRENT plot both will be in the positive quadrant. Of course, polarity must be correct. Now if the CURRENT (in the same polarity arrangement) happens to be in the negative quadrant, the power is said to be reversed.

The same can be thought in an AC circuit. Taking a half wave cycle of both VOLT and CURRENT, one can apply the same understanding as in the DC circuit.

If the AC circuit is capacitive or inductive, VOLT and CURRENT waves will be shifted according to the value of the capacitive or inductive load, and here one has to be aware.

Adel Aljassar

adel@al-jassar.net

User Avatar

Wiki User

∙ 17y ago
User Avatar

What else can I help you with?

Continue Learning about Electrical Engineering
Related Questions

What is reverse power in generator and what happens in couse of reverse power?

2 or more generators are run in parallel supplying power to the common bus. When one of them drag behind due to any reason, instead of delivering electric power to the bus, it takes power from the bus acting like a motor and trying to drive the engine, when it happens like this the circuit breaker trips immediately.


How reverse power will occur during synchronizing?

Reverse power flow into a generator can occur during synchronization if the generator is spinning too slowly, or the voltage phase angle is lagging relative to the power system. If the generator is spinning too slowly, power from the system is used by the generator to increase its' speed. If the phase angle is lagging, an initial spike of power will flow into the generator to force it into sync with the system. Typically generator's will match system frequency very closesly, and force the phase angle to leading slightly between the generator and the system. When synchronized, an extra bump of power will flow out while the generator is torqued into phase with the system. This will avoid tripping any reverse power devices.


What is the Operation of reverse power relay in a substation?

Reverse power relays are often used in generator protection to trip breakers if generators are "sucking in" power (since this shouldn't occur, it is a BAD thing when it does). I'm not sure there is a use for reverse power relays beyond this; directional relays looking in a reverse direction are often used in pilotting schemes, though (not "reverse power").


How control the reverspower for diesel generator?

I guess you're thinking that reverse power is a generation error, but it is a change in flow direction. When two generator are running in parallel nd of sudden a generator2 prime is dropped nd due to circuit breaker2 is still in on state Gen2 draws power from Gen1 and acts as a motor. this action will damage the prime mover(engine) nd AVR too. Of course upto 10 amp of reverse current is allowed into a generator as of considering as back emf (while running as generator). So in order to stop thing reverse power, a relay is used which senses the directional flow of power nd immediately turns off the circuit breaker of off prime mover unmatched droop also develops this reverse power flow because of change in voltage nd load sharing


How many times per second does the alternating current generated at large power generator reverse directions?

120


What is difference between reverse power relay and directional relay in electrical protection?

A reverse power relay is a directional overcurrent relay. Directional relays are relays that sense power flow in one direction, and include (directional) overcurrent relays, reverse power, and impedance based relays. So a reverse power relay is a directional relay, but a directional relay is not necessarily a reverse power relay.


What is a reverse KVAR relay?

The reverse KVAR relay protects a generator from a loss of excitation. When the excitation system is lost, reactive power will flow from the system back into the generator. When this happens, induced currents at twice the system frequency will flow in the rotor windings and rotor structure.


Why does the synchroscope need to be rotating clockwise if it is turning slowly counterclockwise won't that work the same?

because the incoming generator has be connected as a source and not a load to the grid. if the frequency of the incoming generator is lower than the grid frequency then ... it will behave as a motor drawing power from the grid and generator will trip in reverse power protection.


What is reverse power tripping on board ship?

Reverse power tripping on a ship occurs when there is an unintended reversal of power flow in the electrical system, typically caused by a generator running in parallel with other generators or the grid. This situation can lead to damage or instability in the electrical equipment. To prevent this, protective relays are used to detect reverse power conditions and automatically disconnect the affected generator from the system, ensuring safe operation and protecting machinery. Proper monitoring and maintenance are essential to avoid such occurrences.


How do you test generator reverse power?

To test the generators reverse power relay to make sure the generator is spinning at the right speed and a fuel issue is not involved. If it is not a fuel issue you need to check the frequency of the electronic load and frequency. If both of these issues are okay check the diesel electronic control unit for dirt and dust. This unit needs to be clean.


An electric motor is a generator in reverse meaning that it can turn electricity into?

An electrical motor generator in reverse means that it can turn the electrical energy to mechanical and kinetic energy.


What is a reversing relay?

A reverse current relay prevents a generator from discharging the battery when generator output is less than battery voltage. When generator output is greater than battery voltage, the reverse current relay closes and connects generator to electrical bus.