US NEC:

You can connect two air conditioners on a single phase power supply, but...

The correct question is probably, "Can you connect two air conditioners to a single distribution circuit?". The answer is no - any substantial load requires its own distribution circuit.

User Avatar

Wiki User

15y ago

What else can I help you with?

Continue Learning about Engineering

How can you connect single phase generator in three phase supply system in house lighting system?

First house lighting systems are single phase not three phase. To connect a generator to the house lighting system for emergency power, it would take an electrician to do the job properly. The biggest concern would be to isolate the rest of the service from the main distribution supply service and then isolate the rest of the distribution panel loads from the lighting loads.


Is air conditioner works on 1 phase and how it works on 3 phase also?

If an air condition is single phase, then it can only be connected to a single phase source. Since any two legs of a three phase source are considered single phase, there is no conflict, except to note that the individual phases of the three phase source match the voltage requirement of the air conditioner.


How do you connect 3 phase inverter to single phase supply?

It depends on the 3 phase inverter. If it is a 3 phase input then you will first need to get a single phase to 3 phase converter to simulate a 3 phase supply, if that is what this particular inverter is intended for then you will have a label saying 230v primary with a L & N connection point, and the output will be labelled as secondary, giving you the inverted power rating. This is a very expensive way of running machinery as the inverted power is no different in conumption to the single phase.


Is there a difference between three phase and single phase electrical supplies?

Yes, there a difference between three phase and single phase electrical supply services.


Can 3 phase be changed to single phase on the Hobart mixers?

You will need a phase converter. Avaliable at an industrial supply company like granger supply

Related Questions

How do you connect single phase supply to a two capacitor motor?

See Discuss Question below.


Is it safe to connect 380 volts 3 phase supply to 220 volts 3 phase supply?

No.


When would a three phase supply be preferred over a single phase supply?

Bcoz in single phase if supply is interrupt or any trouble there is no power .but in 3 phase if 1phase supply gone we can manage it by other 2 phases


Can you give single phase supply to three phase device?

No.


How do you you connect a 4-prong appliance to a 3-prong outlet?

Sounds like you want to connect a three-phase machine to a single-phase supply. Very inefficiently, a three-phase motor can be ran on single phase by electrically displacing the windings with a capacitor. Other than that, you will need to either look at getting yourself a phase change converter, or having a three-phase outlet installed.


How can you connect single phase generator in three phase supply system in house lighting system?

First house lighting systems are single phase not three phase. To connect a generator to the house lighting system for emergency power, it would take an electrician to do the job properly. The biggest concern would be to isolate the rest of the service from the main distribution supply service and then isolate the rest of the distribution panel loads from the lighting loads.


Is air conditioner works on 1 phase and how it works on 3 phase also?

If an air condition is single phase, then it can only be connected to a single phase source. Since any two legs of a three phase source are considered single phase, there is no conflict, except to note that the individual phases of the three phase source match the voltage requirement of the air conditioner.


How do you connect 3 phase inverter to single phase supply?

It depends on the 3 phase inverter. If it is a 3 phase input then you will first need to get a single phase to 3 phase converter to simulate a 3 phase supply, if that is what this particular inverter is intended for then you will have a label saying 230v primary with a L & N connection point, and the output will be labelled as secondary, giving you the inverted power rating. This is a very expensive way of running machinery as the inverted power is no different in conumption to the single phase.


Does single phase power damage air conditioners?

If the air conditioner is designed for three phase, then it will not run, and could be damaged, by single phase power. Otherwise, no.


What is typical single phase voltage in Canada?

The standard nominal voltage in Canada for a single-phase residential supply is 240/120-V split-phase supply.


Can a single phase supply be used in a three phase supply?

No, a single-phase supply cannot be directly used in a three-phase system. The voltages and phases are different, so additional equipment such as a phase converter or transformer would be needed to convert the single-phase supply to match the requirements of the three-phase system.


Is line to line fault a 3 phase fault?

'Line conductors' are the three 'hot' conductors (A-B-C) that connect a three-phase supply to a three-phase load. In some cases, a pair of line conductors (e.g. A-B, B-C, or C-A) is used to supply a single-phase load. A 'line fault' can be a short-circuit fault between all three, or any two, of these line conductors -whether they supply a three-phase load or a single-phase load.