230 v 6 amps is 1380 VA which equals about 1 kW, so a 3 kW motor implies it's a 3 phase motor. It would turn over on a single phase supply in whatever direction it was first spun in, but the performance would be poor and the motor or generator could get damaged.
I think you mean a 240 V to 110 V (volts, not watts) transformer! Providing your power tool is rated at 110 V, the answer is yes, because its power rating of 1500 W is well within the capacity of a 3-kV.A transformer.
If the transformer is three phase the calculation is I = 30,000 / 1.73 E. If the transformer is single phase the calculation is I = 30,000 / E. (Where I = current and E = secondary voltage) It is important to note the voltage in the first formula is line to line (typically how it is specified in three phase power systems), and the second formula it is line to neutral.
what is meaning of concrete 10
What is meaning of Transformer sensitivity?
yes
21.4 amps, 2100 wattsManoj
To calculate an answer a voltage must be stated.
The 3 kVA transformer will weigh double the 1.5 kVA transformer.
200V / 240V 5 / 6
230 v 6 amps is 1380 VA which equals about 1 kW, so a 3 kW motor implies it's a 3 phase motor. It would turn over on a single phase supply in whatever direction it was first spun in, but the performance would be poor and the motor or generator could get damaged.
I think you mean a 240 V to 110 V (volts, not watts) transformer! Providing your power tool is rated at 110 V, the answer is yes, because its power rating of 1500 W is well within the capacity of a 3-kV.A transformer.
If the transformer is three phase the calculation is I = 30,000 / 1.73 E. If the transformer is single phase the calculation is I = 30,000 / E. (Where I = current and E = secondary voltage) It is important to note the voltage in the first formula is line to line (typically how it is specified in three phase power systems), and the second formula it is line to neutral.
what is the meaning of FPTODA? what is the meaning of FPTODA? what is the meaning of FPTODA? what is the meaning of FPTODA? what is the meaning of FPTODA? what is the meaning of FPTODA? what is the meaning of FPTODA? what is the meaning of FPTODA? what is the meaning of FPTODA? what is the meaning of FPTODA? what is the meaning of FPTODA?
Writing VA is just another way of writing watts, as watts = volts x amps, so 3kva means 3000 watts. Divide by 210, and the answer is 100/7 = 14 to the nearest whole number, but you could make it 15 to be sure, then you would have a 5 by 3 array.
plz tell me the full form of name - PARAMJEET (word meaning) meaning of p - ? meaning of A - ?meaning of R - ? meaning of A - ? meaning of M - ? meaning of J - ? meaning of E - ? meaning of E - ? meaning of T - ? And full meaning of paramjeet
'MEANING' in other words can be the 'vocabulary' of a word or the 'essence' of the word as to what the word precisely means. OR meaning is the meaning of meaning what you just said meaning