Star delta starting is used to reduce the dip in voltage which can feed back to the primary line which makes other customers unhappy when their lights dim each time a high HP motor is started on the same circuit they are connected to. By starting in a wye connection there is less disruption of voltage on the system that the motor is connected to, by starting the motor at a lower voltage and hence lower inrush current. Some utility companies will not allow across the line starting on motors above 30 HP.

This type of motor starting circuit is used less and less, now that VFDs and Soft Starters are becoming cheaper to purchase and more readily available in lower HP ratings

2 people found this useful

User Avatar

Wiki User

10y ago

What else can I help you with?

Related Questions

Why star delta timer required for motor?

The timer is used to give the motor time to reach its running speed at the star voltage. Once the timer times out the star contactor drops out and the delta contactor pulls in.


Can you reverse the motor if it is running in star or delta?

YES!!!


IWant to see the connection of the daigram Star and Delta connections?

Google star delta motor connections. If a motor is wired in star-delta (Yd), it starts up with lots of torque and then switches over to delta for normal "running". This is because the start-up current per phase when delta connected is much larger than star.


What is the difference between a Y - delta starter and a star - delta starter?

No difference. Y is used as a symbol to indicate the star connection.


How many contactors are used in a star-delta starter?

3 contactors are used: one for the main incoming service lines, one to make the star connection and one for the delta connection. Auxiliary to the contactors, a delay timer, adjustable from 500-1000 seconds, is used to shift from star to delta configuration.


Why timer can be used in star delta starter?

delay timer


When was The Delta Star created?

The Delta Star was created in 1983.


Star delta starter for 3 phase induction motor?

A star-delta starter is a method used to reduce the starting current drawn by a 3-phase induction motor. It involves initially connecting the motor windings in a star configuration for starting, and then switching to a delta configuration for running. This helps to minimize voltage drops and prevents excessive current flow during start-up.


What type of star is the delta star?

A delta star is a mathematical technique to simplify the analysis of an electrical network, not a "real" star.A delta star is not a its a mathematical formulasee related link


What applications are star delta starters used for?

Star Delta starters are used for AC motors with higher rating (generally more than 11 KW) and with high initial torque load.