answersLogoWhite

0

Yes. The 125V is the rating of the bulb, which indicates the voltage it was manufactured to withstand. The voltage it is actually operated at does not have to be precisely 125V; As a matter of fact the voltage coming from your wall socket can vary from as low as 100VAC all the way to above 125 VAC.

So, screw that bulb in and light up your world!

User Avatar

Wiki User

16y ago

What else can I help you with?

Continue Learning about Natural Sciences

What size circuit breaker is needed for a 300 watt bulb?

A 300 watt bulb requires a circuit breaker of at least 2.5 amps. This can be determined by dividing the power (300 watts) by the voltage (120 volts). However, considering normal breaker sizes, a 5 amp breaker would be sufficient for a 300 watt bulb.


What is the maximum number of 100-W bulbs you can connwct in parallel in a 120-V home circuit without tripping the 20-A breaker?

You can connect a maximum of 24 100-W bulbs in parallel on a 120-V home circuit without tripping the 20-A breaker. This is calculated by dividing the total circuit wattage (2400 W) by the wattage of each bulb (100 W) to find the number of bulbs that can be safely connected.


What is the requirement for energizing a 120 volt circuit breaker?

Before energizing a breaker for a circuit, the circuit has to be clear of any short circuits or grounds. This can be accomplished by the use of a megger on the correct voltage setting.


Can you use a 2 pole breaker for a 120 volt single phase circuit?

No, a 2 pole breaker is designed for a 240-volt circuit or for two separate 120-volt circuits that are out of phase with each other. For a 120-volt single-phase circuit, you would typically use a single-pole breaker.


How many lights can run off a 6 amp breaker?

To determine how many lights can run off a 6 amp breaker, you need to know the wattage of each light. For example, if each light consumes 60 watts, you can calculate the total wattage by dividing the breaker's amperage by the voltage (typically 120 volts in residential settings). Therefore, with a 6 amp breaker and 120-volt system, you can run approximately 720 watts worth of lights (6 amps x 120 volts). To find out how many lights can run off this breaker, divide the total wattage by the wattage of each light.

Related Questions

What size circuit breaker is needed for a 300 watt bulb?

A 300 watt bulb requires a circuit breaker of at least 2.5 amps. This can be determined by dividing the power (300 watts) by the voltage (120 volts). However, considering normal breaker sizes, a 5 amp breaker would be sufficient for a 300 watt bulb.


A circuit has 25 ohm light bulb and t 120 volts what is the current?

I = E/R = 120/25 = 4.8 amperes


When compared in a given time interval with other light bulbs connected to a 120 V circuit a 60 W lightbulb?

A 60 W light bulb consumes more power (produces more light) than a 40 W light bulb in a given time interval when both are connected to a 120 V circuit. This is because power is directly proportional to the wattage rating of the light bulb.


Can you use 220 volt light bulb on 120 volt system - I know the reverse would probably blow the bulb so wouldn't European 220 Volt do ok in 120 volt socket or would it be dimmer than it normally would?

Yes a 220 volt light bulb will run on a 120 volt circuit but at 1/4 of the wattage that the light bulb is rated at. A 100 watt light bulb on 220 would would be equal to a 25 watt light bult on 120 volt system.


What is the current in an ac circuit with 120-volts and a 60 -watt light bulb?

Current or amperage, is wattage divided by voltage. 60 / 120 = .5 amp.


What is the current in a AC circuit with 120-volts and a 60- watt light bulb?

Current or amperage, is wattage divided by voltage. 60 / 120 = .5 amp.


What is the current in an ac circuit with 120- volts and a 60-watt light bulb?

Current or amperage, is wattage divided by voltage. 60 / 120 = .5 amp.


What is the current in an AC circuit with 120 volts and a 60-watt light bulb?

Power = (voltage) x (current) 60 = 120 x I I = 60/120 = 1/2 Amp.


How many light cans can a circuit hold?

you just have to do some math. if the can lights are the only thing on the circuit then times the wattage of each bulb by the total bulbs and only put 80% of the circuit breaker max on the line. ie 20 amp breaker and 120 volt power equals 2400 watts max. 80% of that is 1920 watts. 15 amp breaker and 120 volt power equal 1800 watts max. 80% of that is 1440 watts. if there are already other item on the circuit then you should test the line fully loaded with an amp clamp to see what its carrying already, and then deduct that from your totals


What is the maximum number of 100-W bulbs you can connwct in parallel in a 120-V home circuit without tripping the 20-A breaker?

You can connect a maximum of 24 100-W bulbs in parallel on a 120-V home circuit without tripping the 20-A breaker. This is calculated by dividing the total circuit wattage (2400 W) by the wattage of each bulb (100 W) to find the number of bulbs that can be safely connected.


What is the requirement for energizing a 120 volt circuit breaker?

Before energizing a breaker for a circuit, the circuit has to be clear of any short circuits or grounds. This can be accomplished by the use of a megger on the correct voltage setting.


Can you use a 2 pole breaker for a 120 volt single phase circuit?

No, a 2 pole breaker is designed for a 240-volt circuit or for two separate 120-volt circuits that are out of phase with each other. For a 120-volt single-phase circuit, you would typically use a single-pole breaker.