KVA is very simple, it is the Volts x Amps of an AC circuit in units of 1000. For a single phase AC circuit VA = E x I. KVA = (ExI)/1000 So if you have 120 VAC and 15 A then: VA = 120 x 15 = 1800; KVA = 1800/1000 = 1.8 For 3 phase circuits we need to add the square of 3 (= 1.732) as a factor. VA = 1.732 x E x I and KVA = (1.732 x E x I)/1000 So if you have 480 VAC and 23 A then: VA = 1.732 x 480 x 23 = 19,121; KVA = 19,121/1000 = 19.1 Note that KVA is higher than KW (true power) in circuits that are not purely resistive. The vector difference of the two is "Power factor".
To convert amps to kVA, you use the following formula: Amps = (kVA x 1000 / voltage) / 1.73
To determine the KVA needed for a 200A panel, you can use the formula KVA = (Voltage x Amperage)/1000. Assuming a standard voltage of 120V, the KVA would be 24 KVA (120V x 200A / 1000 = 24 KVA).
12HP is approximately 10.8 KVA. You would want to use a 15KVA transformer to supply this motor. KW = HP * .75 KVA = KW * 1.2 (These formulas are approximate)
a kva is 1000 vaK is kilo, which means 1000 similar to how a kilometer is 1000 metersTransformers are usually rated in KVA, so a 45 KVA Transformer is a 45 000 VA Transformer
To convert amps to kilovolt-amperes (kVA), you need to know the voltage level. The formula is kVA = (Amps × Volts) / 1000. For example, at 240 volts, 800 amps would equal 192 kVA, while at 480 volts, it would equal 384 kVA. Thus, the kVA value will vary depending on the voltage used in the calculation.
To convert amps to kVA, you use the following formula: Amps = (kVA x 1000 / voltage) / 1.73
To determine the KVA needed for a 200A panel, you can use the formula KVA = (Voltage x Amperage)/1000. Assuming a standard voltage of 120V, the KVA would be 24 KVA (120V x 200A / 1000 = 24 KVA).
The formula you are looking for is , A = kva x 1000/Volts.
Amperes when kva is shown. The formula is, Amps = kva x 1000/1.73 x volts.
12HP is approximately 10.8 KVA. You would want to use a 15KVA transformer to supply this motor. KW = HP * .75 KVA = KW * 1.2 (These formulas are approximate)
The formula to find amps is: I = (KVA x 1000)/(E x 1.73) I = (2500 x 1000) / (480 x 1.73) I = 2500000 / 830.4 I = 3010.597A
a kva is 1000 vaK is kilo, which means 1000 similar to how a kilometer is 1000 metersTransformers are usually rated in KVA, so a 45 KVA Transformer is a 45 000 VA Transformer
To convert amps to kilovolt-amperes (kVA), you need to know the voltage level. The formula is kVA = (Amps × Volts) / 1000. For example, at 240 volts, 800 amps would equal 192 kVA, while at 480 volts, it would equal 384 kVA. Thus, the kVA value will vary depending on the voltage used in the calculation.
To convert 2 kW to kVA in single phase, you need to know the power factor. If we assume a power factor of 0.8 (common for many single-phase loads), the conversion formula is kVA = kW / power factor. Therefore, for 2 kW at a power factor of 0.8, the result would be 2 kVA / 0.8 = 2.5 kVA.
Va=volts x amps. The K stands for one thousand. So 1 Kva is one thousand watts. So 415v times 120a= 49,800 what's. You divide that by a thousand and you get 49.8. So it would be 49.8 Kva.
There are a few components missing from your question. I need to know either the voltage or the amperage and the power factor. For single phase, the formula for Kilowatts is Amps x Volts x pf/1000. The formula for Kilovolt-Amperes is Amps x Volts/1000. As you can see more info is needed.
It could be as much as 63 kW (63,000 Watts) into a load with a power factor of 1.0. For other loads, multiply the kVA by the power factor.