You cannot convert them. KVA is a measure of power, while amperes are a measure of current.
kvar can be calculated as follows the a product KVA andt the sine of the angle between the KVA and KW.
Rating for DG set and any of electrical machines is calculated in KVA. KVA is calculated as KW/pf. One can calculate the required KVA for DG set with this formulation: (KW/pf)/load rate. For example KW=110, pf=0.8 and one loads the DG at 75%, so KVA= (110/0.8)/0.75=185 KVA.
kvar = kva*sin@
kvar = kva*sin@
If you multiply kVA by Power Factor (Ranges from zero to one) you get watts which is effective power.
Power requirements are measured in KVA, which stands for Kilo-Volt-Amperes. To calculate the amount of power you require you would use the following formula. KVA = Volts * Amps / 1000
To convert 'kwh' to 'kvah' you first need to measure the length of time. You will then convert this amount to hours by dividing by 3,600. You will then divide this amount by the length of time.
Use the link below and scroll down.
2.5 kVA means 2500 VA (volt-ampere). To calculate the amperes you need the voltage. 2.5 kVA x cos (phi) = 2.5 kW (kilowatts) if phi is 0 or power factor (phi) is unity.
KVA is the vector sum of real and reactive power; put differently, KVA at a specified power factor will tell you how many KW you have: KW = KVA * pf You must provide a power factor or power factor angle (if angle, replace pf with cos (pf) in above equation) or total reactive power to calculate.
Power Factor = KVA/KW. This has no unit. Its value is always 1 or less.