At what voltage? When you know the voltage then, to get the amps those kilovolt.amps contain, you simply divide the kilovolt.amps by the voltage.
<><><>
You can't convert kVA (kilovolt.amps) to amps unless you know either the source voltage (as was explained above here in the first answer) or the load resistance which is drawing the current from the source.
If you know them both you can use Ohm's Law to get the amperage:
I = V / R
In words, Ohm's law is:
Current (amps) equals voltage divided by resistance (ohms)
For single phase, RMS values of volts and amps:
KVAR = kVoltage * Amps
For three phase, RMS valuse of volts and amps, with voltage phase to phase:
KVAR = kVolt * Amps * sqrt(3)
For three phase, RMS values of volts and amps, with voltage phase to ground:
KVAR = kVolt * Amps * 3
You can't convert current (amps) to voltage (volts or kilovolts) unless you know the load resistance which is drawing the current from the source.
Then use Ohm's Law to get the voltage:
V = I x R
In words, Ohm's law is:
Volts = current (amps) times resistance (ohms)
Watts = Volts x Amps x Power Factor
KWH is kilowatt hours and is the measure of energy usage for which the power company would charge
A megavolt = 1 million volts
A Volt Ampere = a watt if the Power Factor is one.
1000 KW = 1 MVA
If you use the 1000 KW for one hour it would = 1 MVA per hour.
Your question is rather like asking, "How do you convert kilometres to Celsius?" The volt ampere is the unit for apparent power, while the ampere is the unit for current -two different quantities.
The same way, as you convert Appels to Carrots ........... There is a formula: KVAr = KVA / KW or cos=KW/KVA > Yes, we are treating KW, KVA, & KVAr as the 3 sides in a 90 deg TRIANGLE ! KW= vertical katede KVAr = horizontal katede KVA = hypotenuse
{| |- | capacitance of the capacitor is mentioned in KVAR. Formula : KVAR = KW*tan@ FOR tan@, First note the power factor & KW without connecting capacitor. The noted power factor is in cos@.Convert the cos@ value in tan@. for ex. If power factor is 0.6, KW = 200 cos@ = 0.6 cos-1 (0.6) = 53.1 tan (53.1) = 1.333 200*1.333 = 266.6 KVAR if you use 266 KVAR capacitor, Then the power factor improves to unity (1.000). |}
KVAR Kilovolt-Ampere Reactive KVAR Kilovolt-Ampere-Reactance {| ! Acronym ! Definition | Formular for calculation of kvar |}
KV is the unit used for VOLTAGE measurement. AC power is complex quantity that is it has both magnitude and direction and hence has two parts real part and imaginary part. complex power is measured in KVA (kilo volts amps) real part (active component ) is measured in KW (kilo watts) imaginary part (reactive component) is measured in KVAR (kilo volts amps reactive)
kvar can be calculated as follows the a product KVA andt the sine of the angle between the KVA and KW.
kV is kilovolts, kW is kilowatts, kVA is kilovolt amps and kVAR is kilovolt-amps reactive. A common formula is kVA-squared = kW-squared + kVAR-squared.
The same way, as you convert Appels to Carrots ........... There is a formula: KVAr = KVA / KW or cos=KW/KVA > Yes, we are treating KW, KVA, & KVAr as the 3 sides in a 90 deg TRIANGLE ! KW= vertical katede KVAr = horizontal katede KVA = hypotenuse
4.3 amps
{| |- | capacitance of the capacitor is mentioned in KVAR. Formula : KVAR = KW*tan@ FOR tan@, First note the power factor & KW without connecting capacitor. The noted power factor is in cos@.Convert the cos@ value in tan@. for ex. If power factor is 0.6, KW = 200 cos@ = 0.6 cos-1 (0.6) = 53.1 tan (53.1) = 1.333 200*1.333 = 266.6 KVAR if you use 266 KVAR capacitor, Then the power factor improves to unity (1.000). |}
KVAR Kilovolt-Ampere Reactive KVAR Kilovolt-Ampere-Reactance {| ! Acronym ! Definition | Formular for calculation of kvar |}
Amps is amps be it DC or AC.
kvar
Watts are the product of amps x volts.
Kvar = Kilo Volt Amp Reactance.
kvar = kva*sin@
kvar = kva*sin@
KVAR - FM - was created in 2008.