answersLogoWhite

0


Best Answer

No. The receptacle, wiring, and breaker ratings should all be matched properly. Replacing the 50A receptacle with a 30A receptacle isn't a problem, since the wire should be rated at least 50A. But a 30A receptacle should be protected with a 30A double pole breaker. The breaker only costs about $8.00, so why wouldn't you change it given you don't have to change the wire which would actually be expensive or time consuming? The fact that you mention a 50A receptacle protected by a 20A existing breaker isn't normal either. I would check to make sure the wiring is actually rated for 50A and that someone didn't just throw a 50A receptacle onto a 20A circuit. (This means your wiring should be at least #8AWG THHN Copper wire.) If you protected a 30A receptacle with a 20A breaker, the load might trip the breaker often, considering the appliance requiring a 30A receptacle probably requires about 30A. If you do not understand the work well enough to accomplish it yourself properly and safely, don't try it. Consult a professional electrician, as they are proficient enough to do it properly and safely. When working on electrical circuits and equipment, make sure to de-energize the circuit you will be working on. Then test the circuit with a definitive means to make sure it is off (multimeter with metal tipped leads, voltage tester with metal tipped leads, etc., not a non-contact tester, which is non-definitive.)

User Avatar

Wiki User

15y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

15y ago

== == === === STOP! DO NOT DO THIS! More than likely the wire in the wall is only rated to carry 30 amps. Running fifty amps through it will start a fire! You MUST upgrade the wiring in the wall to upgrade the current rating of the circuit! The wire in the wall must be properly sized. Go out and buy a book. You are on the fast track to a house fire. Buy a book and read up on wire sizes, current ratings, and why they matter. Remember, negligence is fatal with electricity.ANSWER

Before you can know that you only need to change the outlet and the breaker you must make sure that the wire already in the wall is equal to, or heavier than, the size required to carry 50A safely. So calculate the wire size needed to carry 50A for your length of run and check the gage of the wire in the wall. If the wire is lighter, you must run new wire of the correct size. == ==

IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOB

SAFELY AND COMPETENTLY

REFER THIS WORK TO QUALIFIED PROFESSIONALS.

If you do this work yourself, always turn off the powerat the breaker box/fuse panel BEFORE you attempt to do any work AND always use a meter or voltage indicator to insure the circuit is, in fact, de-energized.

This answer is:
User Avatar

User Avatar

Wiki User

9y ago

In the UK, yes but the new socket would be able to supply only up 20 amps instead of up to 50. It would not make full use of the wiring that is capable of supplying 50 amps.

Up to three 20-amp sockets could be connected to a 50-amp supply on the basis that not all three sockets would be fully loaded at any moment.

<<>>

In North America the answer is also yes, but the circuit's breaker would have to be changed out to a 20 amp breaker from the 50 amp breaker. The maximum rating of the receptacle is only 20 amps so it would not be protected by being fed from the 50 amp breaker..

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How do you upgrade a 30A outlet to a 50A outlet can I just change the outlet and upgrade the circuit breakers?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

A wall outlet has no electricity What could be wrong?

There are several possibilities: Check the breakers to make certain that none have "tripped". Open the outlet box and verify that there are no loose connections, if that doesn't prove helpful, follow the wiring back to the previous outlet on the circuit and see if THAT one has power. Verify that the wall outlet is not part of a switched circuit. Sometimes wall outlets are designed to be for lighting purposes only, and as such are put on a switch.


When the test button is pressed on a gfci outlet it sparks and trips two breakers in the main panel What could be the problem?

The test button should only trip the GFCI. The fact that it is tripping two breakers indicates that somehow both breakers are feeding your GFCI circuit. I have seen this when there was a wiring error and two circuits were joined in an outlet that was connected to a breaker and through the GFCI outlet. To troubleshoot determine which outlets are effected when both breakers are off. Pull outlet from box and if there are two feeds remove one from outlet and run a toner on wire left on outlet to panel and one off outlet to panel. The GFCI could block the toner so if one side of the outlet does not tone back to panel check at GFCI. There must be two paths to your electric panel for the two breakers to trip and the GFCI may be faulty as well. Another way to check is to have the GFCI reset and both breakers on. Check each outlet that you have identified as being on GFCI noting that they can be in different rooms. With all outlets working turn off one of the tripped breakers. See if any outlets so off. If not turn off the other breaker and turn on the first breaker. If power is still present then the outlets are being fed by both breakers.


Outlet stopped working and it is not a GFCI?

First, check the circuit breakers; make sure they are all ON. Find out if any other outlets on the same breaker are working; it's always possible that a breaker is faulty. If the breaker is on and everything else on the circuit is working, it could be as simple as a poor connection inside the outlet. Also even though the outlet is not a GFCI, it may be fed from a GFCI outlet. Check near by outlets to see if any are GFCI and are tripped.


How do you dedicate a wall outlet?

A dedicated wall outlet is the only one on the circuit.


If your wall receptacle has tripped but not at the circuit breaker how can this problem be repaired?

If it's a GFCI receptacle and the button is not resetting then change the GFCI outlet.

Related questions

How many outlet for ELECTRIC circuit in a house?

As many as you like but the total current taken is limited by the circuit breakers.


What if your circuit breaker started tripping with no change of things plugged into an outlet Does this mean the circuit breaker needs to be replaced?

Circuit breakers can degrade over time but it would be better to get a competant electrician to do it. It might also mean you have too many things plugged into one outlet. Sometimes one circuit breaker may protect several outlets so it might be tripping because of a change in another outlet. ELECTRICTY IS DANGEROUS!!!! Don't do it yourself.


How can all breakers be live and outlets not work?

The very first outlet in the circuit has a break, probably where the wires enter the receptacle.


What might cause low voltage at one outlet on a multioutlet circuit?

its an overload on the circuit breaker the 3 outlets are on.. many times groups of outlets are on different circuit breakers.. even though they are in the same room... especially if some are on a gfi outlet


A wall outlet has no electricity What could be wrong?

There are several possibilities: Check the breakers to make certain that none have "tripped". Open the outlet box and verify that there are no loose connections, if that doesn't prove helpful, follow the wiring back to the previous outlet on the circuit and see if THAT one has power. Verify that the wall outlet is not part of a switched circuit. Sometimes wall outlets are designed to be for lighting purposes only, and as such are put on a switch.


When the test button is pressed on a gfci outlet it sparks and trips two breakers in the main panel What could be the problem?

The test button should only trip the GFCI. The fact that it is tripping two breakers indicates that somehow both breakers are feeding your GFCI circuit. I have seen this when there was a wiring error and two circuits were joined in an outlet that was connected to a breaker and through the GFCI outlet. To troubleshoot determine which outlets are effected when both breakers are off. Pull outlet from box and if there are two feeds remove one from outlet and run a toner on wire left on outlet to panel and one off outlet to panel. The GFCI could block the toner so if one side of the outlet does not tone back to panel check at GFCI. There must be two paths to your electric panel for the two breakers to trip and the GFCI may be faulty as well. Another way to check is to have the GFCI reset and both breakers on. Check each outlet that you have identified as being on GFCI noting that they can be in different rooms. With all outlets working turn off one of the tripped breakers. See if any outlets so off. If not turn off the other breaker and turn on the first breaker. If power is still present then the outlets are being fed by both breakers.


Outlet stopped working and it is not a GFCI?

First, check the circuit breakers; make sure they are all ON. Find out if any other outlets on the same breaker are working; it's always possible that a breaker is faulty. If the breaker is on and everything else on the circuit is working, it could be as simple as a poor connection inside the outlet. Also even though the outlet is not a GFCI, it may be fed from a GFCI outlet. Check near by outlets to see if any are GFCI and are tripped.


What is flex outlet?

An appliance cable or "flex" outlet is a type of electrical outlet which is NOT a "socket outlet" to take plugs for appliances so that they can be plugged and un-plugged. An appliance cable or "flex" outlet has terminals inside it. The terminals allow the wires in an appliance cable or "flex" to be connected to the household wiring in a building. The household wiring comes from the building's main electrical power panel, which carries the main circuit breakers. The circuit breakers are fitted to protect the household wiring from catching on fire if any circuit is overloaded. Such appliance cable or "flex" outlets also have strain-relief clips. A strain-relief clip helps to prevent the cable from being yanked out of the outlet if the appliance gets moved away from the wall where the outlet is installed. Such outlets, with terminals inside and strain-relief clips, are used for fixed appliances, such as ranges or dryers, which should never have to be un-plugged during normal use of the appliance by the user.


If one outlet on a circuit is not working will the entire circuit not work?

No


How do you dedicate a wall outlet?

A dedicated wall outlet is the only one on the circuit.


If your wall receptacle has tripped but not at the circuit breaker how can this problem be repaired?

If it's a GFCI receptacle and the button is not resetting then change the GFCI outlet.


Infer which type of circuit an outlet is part of?

Outlets are part of a "branch" circuit.