What is no load current in a transformer?

Updated: 8/20/2019
User Avatar

Wiki User

12y ago

Best Answer

A transformer's 'no-load current' is the primary current flowing, when the secondary winding is open circuited -i.e. with no secondary current flowing. The no-load current (Io) is determined by dividing the primary supply voltage by the impedance of the primary winding. As the primary winding's inductive reactance is very much greater than its resistance, the no-load current lags the supply voltage by very nearly 90 degrees. This current can be resolved into two components, (Ii) in phase with the supply voltage, and (Im) lagging the supply voltage by exactly 90 degrees. Ii is responsible for the losses, while Im is responsible for the magnetising flux.

User Avatar

Wiki User

12y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What is no load current in a transformer?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

The current load of a transformer is the current drawn by the?

load


What is zero current transformer?

It is a transformer with No load attach to it.


What is the percentage of the no-load current in a transformer to its full load current?

2 to 5% of full load current


Why no load current in transformer small?

No load current is energizing current. This is effectively "lost" power, power used in the transformer to energize the core. It, therefore, should be small!


What is full load magnetising current of transformer?

is it primary current ?


Function of no-load in transformer in a open-circuit?

To calculate the no load current from transformer & core loss is also calculated.


How is no load current reduced?

No load current, in a transformer for example, is the current necessary for exciting the transformer. If you wish to keep it energized, and you need to keep it energized at full voltage, there is nothing you can do to reduce this other than replace the transformer with one that has lower no load current. If you are referring to a different piece of equipment, you may need to specify what you are meaning by "no load current".


What is the function of the primary current when the secondary winding of the transformer is open?

When the secondary of a transformer is opened, there is no longer any load on the transformer. There will be some current flowing in the primary winding, which is needed to induce the voltage in the secondary. This primary current is referred to as the "no load" current, and is indicative of the core losses in the transformer.


What will happen when we change value of load resistance in transformer?

When the value of the load resistance in a transformer is changed, it will affect the current flowing through the circuit. Increasing the load resistance will decrease the current, while decreasing the load resistance will increase the current. This change in current will in turn affect the voltage across the load and the efficiency of the transformer.


What is the no load current of 1600 kva transformer?

No load current depends on the design of the transformer, and what voltage it is energized at. It will typically be below 1% of full load, and can be significantly below 1% for utility sized transformers.


What is the secondary rating of a 50KVA transformer?

The secondary current is determined by the load, not by the transformer. For example, if the secondary voltage is 50 V and the load is 100 ohms, then the secondary current will be 0.5 A. If the load is 25 ohms, then the secondary current will be 2 A. It is important that a continuous secondary current doesn't exceed the rated secondary current of the transformer.


Why less current increases in transformer than in induction motor when load is increase?

The current flowing through a transformer's secondary is the current drawn by the load, so it will be exactly the same as the current flowing through your induction motor -assuming that is the load. Don't really understand the point of your question!