== == By asking this question you are probably not quite ready to take on this particular task. The correct answer to your question will depend on the exact locations of the desired GFCI-protected socket outlets. <><><> There is not, per se, a standard for location of ground fault interrupt receptacles around sinks.

There are rules requiring the placement of receptacles

These can be found in the NEC in Article 210.52

NEC 210.52(D) mandates a MINIMUM of one receptacle outlet in a bathroom in a "dwelling unit" and states that it shall be within three feet of the outside edge of EACH basin, and in a wall adjacent to the basin or countertop, with exception.

The balance of Article 210.52 gives requirements for placement of other receptacles throughout the "dwelling unit"

There are rules requiring that these receptacles be GFCI protected

These can be found in the NEC in Article 210.8

NEC 210.8(A)(1) mandates that the required bathroom receptacle in a "dwelling unit" shall be GFI protected

The balance of 210.8 addresses other GFI protection requirements.

Kitchen placement is also in these Articles. <><><>

Electricity 101, Logically, anywhere you think you need one, and anywhere within 6 feet of the rim of the outside edge of the sink. <><><>

As always, if you are in doubt about what to do, the best advice anyone should give you is to call a licensed electrician to advise what work is needed.

Before you do any work yourself,

on electrical circuits, equipment or appliances,

always use a test meter to ensure the circuit is, in fact, de-energized.

IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOB

SAFELY AND COMPETENTLY

REFER THIS WORK TO QUALIFIED PROFESSIONALS. == ==

User Avatar

Wiki User

14y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

14y ago

Typically it is within 6ft, but you should your local codes and ask them what they

use as code.

So any outlet that is within 6 feet of water must be a ground fault outlet or the breaker

must be a ground fault breaker.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What are the standards for the location of gfci ground fault circuit interrupt socket outlets around sinks?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How many standard lighting outlets on a 20 ampere circuit?

16 outlets or 80% of the total Amperage of the circuit.


Does a GFCI need to be on an independent circuit?

No, it can be on a circuit with conventional outlets.


Can the outlets in a circuit be arranged in different groupings to obtain the same result Why?

Can the outlets in a circuit be arranged in different groups to obtain the same result? Why?


What size circuit breaker do you need for kichen counter outlets?

Two 20 Amp circuits with the outlets staggered so a different circuit is on two adjacent outlets. Should be GFCI protected.


Infer which type of circuit an outlet is part of?

Outlets are part of a "branch" circuit.


What happens if only half the outlets work on run the main breaker?

assuming you have reset all of the other circuit breakers as well, look for a ground fault interrupt outled (GFI). It will have a small red and black button in the middle. It will probably be near water, in bathroom kitchen or garage. Reset it and the other outlets should work again.


What is the symbol for special-purpose outlets?

The symbol for special-purpose outlets can vary depending on the specific purpose. For example, the symbol for a GFCI (Ground Fault Circuit Interrupter) outlet is a rectangle with two vertical lines and a curved line inside. The symbol for an AFCI (Arc Fault Circuit Interrupter) outlet typically includes a rectangle with the letters AFCI inside.


What is a dedicated circuit?

A "dedicated" circuit is one to which only one device is or can be connected; therefore the circuit is "dedicated" to the device. A NON dedicated circuit will therefore be one to which multiple devices can connect, such as the wall outlets in your home. Multiple wall outlets are connected to a common circuit breaker, making that an example of a non-dedicated circuit.


How many outlets are allowed on a 240 circuit branch?

1


How many outlets can be wired to a 20A circuit?

No more than 13.


How many elec outlets can a GFCI detect?

7 on a 15 amp circuit and 9 on a 20 amp circuit.


Can you back wire an outlet on a gfi circuit?

Don't know what you mean by back wire, but most GFCI outlets have a circuit to attach additional outlets that will be protected by the GFCI. Keep total load in minds.