answersLogoWhite

0

Answer for USA, Canada and countries running a 60 Hertz supply service.Yes, a 240v 50amp circuit can be changed to a 120v 30amp circuit. The wire for the 50 amp circuit should be a #6. This is more than ample for a 30 amp circuit. Remove the two pole 60 amp breaker and replace it with a single pole 30 and a single pole 15 amp breaker. One of the two #6 wires will be terminated on the neutral bus (if there is a white use it) and the other #6 will be terminated on the new 30 amp breaker. This will give you the required 120 volt 30 amp circuit. The new 15 amp breaker that was installed just to fill the hole from the two pole 60 amp breaker will give you a spare 15 amp circuit.

<<>>

I have no idea what you are trying to do, but there is no way you can change 220v 50 amp to 120v 30 amp. You can take 220 volt input in the top of your circuit breaker box. Then half of one side will be 120v and half of the other side will be 120v. You can install a 30 amp fuse. You should hire an electrician.

Before you do any work yourself,

on electrical circuits, equipment or appliances,

always use a test meter to ensure the circuit is, in fact, de-energized

IF YOU ARE NOT REALLY SURE YOU CAN DO THIS JOB

SAFELY AND COMPETENTLY

REFER THIS WORK TO QUALIFIED PROFESSIONALS.

User Avatar

Wiki User

15y ago

What else can I help you with?

Related Questions

What type of diode is a msc 8832 s 2140?

120v/12v 30amp power supply comes to mind.


what is the resistance of circuit with 120v and 10A?

12


How many watts in 120v-60Hz-12A?

To calculate watts, you can use the formula: Watts = Volts × Amps. For a 120V, 60Hz, 12A circuit, it would be: 120V × 12A = 1,440 watts. Therefore, the circuit uses 1,440 watts.


What is the voltage of a series circuit with four voltage drops of 30 volts?

there is 120V across the circuit.


What is the voltage drop of a series circuit with four voltage drops of 30 volts?

there is 120V across the circuit.


In a 120V 24A circuit what amp fuse is needed to protect it?

A 30A fuse would be appropriate to protect a 120V 24A circuit, as fuses are typically chosen to be slightly higher than the circuit load to prevent nuisance tripping.


Could 12 gauge wire is used on a 20 amp circuit at 120V?

Yes.


Can you feed a 208v 200amp panel from 480v 20amp circuit?

Not directly, you would need to transform 480v circuit to 120v with a transformer first.


How many amps would a 150 watt bulb draw in a 120v circuit?

1 amp


How many amps does 230 watts equal is you are using 120V ac circuit?

1.9 amps


If a 120 volt current is protected by a 25 amp circuit breaker What is the largest number of watts an appliance can safely use?

The largest number of watts an appliance can safely use on a 120V circuit protected by a 25A breaker is 3000 watts. You calculate this by multiplying the voltage (120V) by the amperage (25A). This gives you a maximum power capacity of 3000 watts on this circuit.


Can you use a 600v fuse in a 120v circut?

No, it is not safe to use a 600V fuse in a 120V circuit. The fuse voltage rating should be equal to or greater than the circuit voltage to ensure proper protection. Using a higher-rated fuse can lead to safety hazards and may not provide adequate protection for the circuit. It is recommended to always use the correct voltage-rated fuse for the circuit.