A typical PC might use 200-300 watts, a laptop might use 40-60 watts. A 30-amp circuit can supply 3600 watts on a 120 v system (US) or 7200 watts on a 240 v system (Europe), so 8 typical/average computers should be all right.

User Avatar

Wiki User

11y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can a 30 amp circuit breaker supply 8 computers?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

Does a double 50 amp breaker make a 100 amp?

No, a double pole 50 amp breaker protects a 240 volt supply at 50 amps. The number that is on the handle of the breaker is the amperage that the breaker will trip at if an overload occurs on the circuit.


Can you replace a 20 amp circuit breaker with a 25 amp circuit breaker?

No. The breaker must protect the circuit components such as wiring, outlets and switches that are connected to the breaker. Therefore if you have a 30 amp circuit as dictated by its components you need to protect it with a 30 amp or less breaker.


Can a 3 phase 220 volt machine that usually plugs into a line with a twenty amp breaker can a thirty amp breaker be used instead?

No, you should not install a 30 amp circuit breaker to a machine which normally requires a 20 amp supply. The circuit breaker is protecting the wire to the machine. That wire is likely only rated for 20 amps, (# 12 awg). Therefore, a 30 amp breaker could allow too much current to go through the wiring to the machine and cause the wire to burn down. Replace the 3 phase 20 amp breaker with the same amperage breaker.


What size circuit breaker is needed for a 300 watt bulb?

A 15 amp circuit breaker will handle this situation very well. The smallest home breaker is rated at 15 amp.


What size amp circuit breaker should be used for a home entertainment system?

You use the correct size breaker depending on the size wire in the circuit. If the circuit is wired with AWG #12 wire use a 20 amp breaker. If it is wired with AWG #14 wire then use a 15 amp breaker.

Related questions

Does a double 50 amp breaker make a 100 amp?

No, a double pole 50 amp breaker protects a 240 volt supply at 50 amps. The number that is on the handle of the breaker is the amperage that the breaker will trip at if an overload occurs on the circuit.


Can you replace a 20 amp circuit breaker with a 25 amp circuit breaker?

No. The breaker must protect the circuit components such as wiring, outlets and switches that are connected to the breaker. Therefore if you have a 30 amp circuit as dictated by its components you need to protect it with a 30 amp or less breaker.


How do you turn a 30 amp circuit into a 15 amp cicuit?

Replace the 30 Amp Breaker with a 15 Amp breaker.


What are the circuit requirements to power 8 computers?

It depends on how much current each computer draws. An average rating for a computer power supply for a home computer is about 250 watts. A 20 amp circuit breaker can handle about 8 of this type of computer.


Can you upgrade a 15 Amps circuit breaker for a 40 Amp for a 8.5 Watt shower?

Not unless you change the wiring for that circuit. The breaker protects the wiring and if you install a 40 amp breaker on a 15 amp wire circuit you will have a fire in your home.


Can a 3 phase 220 volt machine that usually plugs into a line with a twenty amp breaker can a thirty amp breaker be used instead?

No, you should not install a 30 amp circuit breaker to a machine which normally requires a 20 amp supply. The circuit breaker is protecting the wire to the machine. That wire is likely only rated for 20 amps, (# 12 awg). Therefore, a 30 amp breaker could allow too much current to go through the wiring to the machine and cause the wire to burn down. Replace the 3 phase 20 amp breaker with the same amperage breaker.


What size amp circuit breaker should be used for a pool light?

The pool light is usually on a 15 amp circuit. The breaker feeding this circuit must have a GFCI rating.


New shop 20 amp circuit 32 amp fixture how many fixtures can be put on circuit?

A 32 amp fixture can not be fed from a 20 amp breaker as the breaker will trip every time.


What size circuit breaker is needed for a 300 watt bulb?

A 15 amp circuit breaker will handle this situation very well. The smallest home breaker is rated at 15 amp.


What size amp circuit breaker should be used for a home entertainment system?

You use the correct size breaker depending on the size wire in the circuit. If the circuit is wired with AWG #12 wire use a 20 amp breaker. If it is wired with AWG #14 wire then use a 15 amp breaker.


Is a double throw 15amp breaker the same as a 30 amp breaker amp?

You have a double pole breaker for 240Volt supply. The maximum current is 15 amp.


Can a circuit breaker be tripped by using 20 amp sockets instead of 15 amp sockets?

A circuit breaker protects the wires that the devices are connected to. If the devices that are connected to the circuit are 20 amps the wire size should be #12 wire fed from a 20 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. If the devices that are connected to the circuit are15 amps the wire size should be #14 wire fed from a15 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. Putting 20 amp sockets on this 15 amp circuit will work but the circuit is limited to the amount of load that can be plugged in. You will not get the full capacity of the 20 socket because the breaker will trip at 15 amps.