answersLogoWhite

0


Best Answer

No. A megger's output voltage is not high enough to test the insulation of a high-voltage transformer if, by 'high-voltage transformer ', you mean a distribution transformer or power transformer. Instead, a high-voltage test set or 'pressure tester' (e.g. a 'HiPot' tester) must be used, as these produce far higher voltages.

User Avatar

Wiki User

10y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can a high voltage transformer be megged with a megger meter?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

How voltage increase in megger meter from 9vots battery to 500 voltage and hw voltage increase in multimeter.?

A megger measures very high resistance to check insulation, therefore it must use very high voltages so as to detect the very small current flowing.


How do you connect a megger on a three phase wye - wye transformer for testing?

First you would disconnect the HO bushing connection from ground. Then you would megger low-side phase to ground.. Next you would megger high-side phase to ground.. Lastly megger high-side to low-side phase to phase. You would not megger phase to phase on each side because this is a direct connection.


What do megger measure?

Megger is usually short for Mega Ohm Meter. It measures high values of resistance with good accuracy. Most often used to test insulation.


How do you measure the current and voltage in high tension line?

To measure high voltage use suitable instrument transformer (potential transformer) Very carefully. It can kill you. The higher the voltage the more the danger or arcing over even when two conductors are not touching. Voltage meters are rated and the rating should not be exceeded. Depending on the voltage you will need the proper meter and a high voltage probe rated for the voltage you are measuring. If you don't know what you are doing, don't mess with high voltage. Leave to the pros.


Construction of ohm meter and megger?

Ohm meter is basically a series combination of resistances and galvanometer and source of current .Used to determine unknown resistance.

Related questions

Why not use an ohm meter to check leakage in a wires insulation?

An ohm meter doesn't put out enough voltage, you need to use a megger.


How do you test motor for burn?

To test a motor, use a megger (megohm meter) to test the insulation of the internal motor windings. Select a voltage to apply to the motor using an output from the megger that is higher that the operating voltage that the motor operates on.


How voltage increase in megger meter from 9vots battery to 500 voltage and hw voltage increase in multimeter.?

A megger measures very high resistance to check insulation, therefore it must use very high voltages so as to detect the very small current flowing.


What is the purpose of voltage transformer?

A 'voltage transformer' (called a 'potential transformer' in North America) is classified as an 'instrument transformer', and is used to reduce the voltage of an electrical system to a lower, safe, level for the purposes of either operating a voltmeter or supplying a protection relay. At the same time, it electrically-isolates the meter or relay from the high-voltage system.


How do you use a meggar?

A megger is used to test the resistance of high voltage cables, insulation and motor windings. The test employs a megohm meter.


What is the principle used in a megger?

A "Megger" (which is short for "Megohm meter") is an instrument which generates a very high DC voltage so as to be able to test the quality of insulation which should have a very high resistance that can only be measured in megohms.


What do electricians use to test circuits?

Continuity tester, volt meter, clamp on amp meter, megger and ohm meter.


How do you connect a megger on a three phase wye - wye transformer for testing?

First you would disconnect the HO bushing connection from ground. Then you would megger low-side phase to ground.. Next you would megger high-side phase to ground.. Lastly megger high-side to low-side phase to phase. You would not megger phase to phase on each side because this is a direct connection.


What is a main distributors service cable and what is it connected to when first enering a build?

The main supply will first come from the power company to a transformer to reduce the voltage then from the transformer to the weatherhead then through the house meter to the main disconnect on the outside of building then to the switchgears main. The cable coming from the transformer to the meter and to the top of the main disconnect is the Main service cable


What do megger measure?

Megger is usually short for Mega Ohm Meter. It measures high values of resistance with good accuracy. Most often used to test insulation.


Can insulation resistance of cable be checked with a volt meter?

No. A volt-ohmmeter will not check insulation. To check cable insulation you need a special device (called a megger) made for the purpose that imposes a high voltage and measures current leaks.


What is the maximum voltage a meter can handle?

A meter that you find in large distribution panels only receives part of the supply voltage. The volt meters have a full scale deflection of 5 volts. The amp meters have a full scale deflection of 5 amps. These meters are supplied from, for voltage, potential transformers and for amperage, current transformers. The transformers are ratio driven so that the maximum input will always produce a 5 volt or 5 amp output.The legend on the meter is matched to the transformers. For example, if the maximum current applied to a current transformer is 300 amps then the transformer ratio will be 60:1. So for every 60 amps the transformer detects the meter needle will move up to a position on the meter face equalling 60 amps. This is a linear movement all the way up to full scale deflection of 300 amps equalling 5 amps to the meter.