answersLogoWhite

0


Best Answer

NO - it is not safe to do that. A GFCI breaker is only a secondary safety device and your primary safety still depends on the earth wire in a 3-pin supply.

User Avatar

Wiki User

11y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can you change a 2 prong plug with a three prong plug if you use a GFCI breaker?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Do you need a gfci outlet if you have a gfci breaker?

Not if the GFCI breaker is supplying the circuit you are wanting to put the GFCI receptacle into.


If your wall receptacle has tripped but not at the circuit breaker how can this problem be repaired?

If it's a GFCI receptacle and the button is not resetting then change the GFCI outlet.


A GFCI device in a breaker is intended to?

A GFCI device in a breaker is intended to trip the breaker open when a ground fault is sensed in the circuit that the breaker is protecting.


Does anyone make a 100 amp GFCI breaker?

Not that I know of. The largest GFCI breaker I have seen is a 60 amp.


Can a circuit with a GFCI be shared at the box?

Your question is a bit vague, but let's try a two part answer. If you have a GFCI breaker in an electric panel you should only have one connection at the breaker, but the breaker will protect all devices on the circuit. If you are talking about a GFCI outlet, they are equipped to extend the GFCI protection to other non-GFCI outlets by using the proper "output" connection on the GFCI.


Are gfci receptacles required in kitchens?

No, you could use a GFCI circuit breaker instead.


What is distribution box?

An ELCB (Earth Leakage Circuit Breaker) distribution box is a type of electrical box that is used for electrical GFCI (Ground Fault Circuit Interrupter) outlets. This is the type of outlet that requires a three-prong plug in, one wire of which is grounded. GFCI outlets are set up so that if there is a circuit overload, the outlet is shut off until it is reset, manually.


What is ELCB distribution box?

An ELCB (Earth Leakage Circuit Breaker) distribution box is a type of electrical box that is used for electrical GFCI (Ground Fault Circuit Interrupter) outlets. This is the type of outlet that requires a three-prong plug in, one wire of which is grounded. GFCI outlets are set up so that if there is a circuit overload, the outlet is shut off until it is reset, manually.


Is a ground fault indicator outlet installed at the breaker box?

There are tow places to put a Ground Fault Circuit Interrupter. There is a GFCI breaker which would be installed in a breaker box and a GFCI outlet that can be installed anywhere. Most GFCI outlets allow you to connect regular outlets to the GFCI and those outlets will also be protected.


Are gfci plugs required in a bathroom?

Deoends on code you are governed by. In USA, a GFCI outlet or a circuit controlled by a GFCI circuit breaker would be required.


Why and when would you use a GFCI breaker within a older home with a groun?

You need a GFCI outlet at any location that is within 6' of a water source. You also need a GFCI outlet in a room with a concrete floor, any garage, and any location outside the home or under the home in the crawl space. A GFCI outlet protects you from electrical shock near water or moisture. You can protect more than one outlet with 1 GFCI outlet. Connect the incoming power to the LINE side of the GFCI outlet and all the other outlets getting power from that outlet to the LOAD side of the GFCI outlet. That way they will all be protected by 1 GFCI. A GFCI breaker is used to protect an entire circuit and not just individual receptacles. It is often cheaper to use GFCI receptacles than a breaker, especially if "piggy-backed" such as described above. It is also more convenient to reset a GFCI receptacle than to reset a breaker. But your question is "why." From this I suspect you may be misunderstanding the difference between a breaker and GFCI protection. To keep things simple let me say that a GFCI does not work on the same principles as a standard breaker. It provides a much safer protection than a standard breaker. Even with a ground you need GFCI protection as listed above.


If the test switch is bad on a gfci will the breaker still work?

If the test switch is faulty then there is no convenient way to determine if the GFCI is functioning, and technically, if the test switch is faulty, then as it is a part of the GFCI, the GFCI is faulty and should be replaced.