answersLogoWhite

0


Best Answer

No, and here's why: the rating of the branch, determined by the overcurrent protection, is designed for the ampacity of the branch conductors so that they breaker trips before the conductors heat up enough to start a fire. If you put in smaller wires on the same branch, they will get MUCH hotter before the circuit breaker trips, if it ever does.

For example, a 20A branch, protecting 12AWG wiring; add some 14 AWG rated for 15A. Something faults the switched leg at 18A; enough to burn out the wiring but not enough to trip the breaker. House burns down, insurance doesn't pay because of "faulty wiring" installed negligently by a person without proper training and credentials.

User Avatar

Wiki User

10y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

11y ago

The current (amps) rating of switch legs should be that of the circuit breaker or fuse for the circuit it branches from.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Does the code permit the ampacity of switch legs to be less than the ampere rating of the branch circuit?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Electrical Engineering

DoesCode permit connecting receptacles to a 20ampere branch circuit using short lengths of 14AWG conductors as the pigtail between the receptacle terminals and the 12AWG branch-circuit conductors?

No. This practice is a violation of Article 210.19 (A) of the NEC. "Conductors of branch circuits supplying more than one receptacle for cord-and-plug-connected portable loads shall have an ampacity of not less than the rating of the branch circuit."


Explain what a circuit main earth does?

Basically, it's an earth connection applied for the purpose of making apparatus safe to work on before a Permit to Work or Sanction for Test is issued. Disconnect from power, test dead, apply CME.


Why do you use isolator on both side of circuit breaker?

Opening a circuit breaker merely interrupts the current flowing through that circuit. It doesn't remove the voltage from the circuit breaker. Isolators (called 'disconnects' in North America) place a visible gap between the circuit breaker and energised conductors, allowing work to be performed on the circuit breaker safely. The full procedure involves: 1. Tripping the circuit breaker (CB). 2. Opening both isolators. 3. Applying temporary earth (ground) connections on either side of the CB. 4. Placing barriers and warning signs around the CB. 5. Issuing a permit to work card to the maintenance supervisor.


What is an electrical isolator?

Something that doesn't let electricity throughAnswerAn isolator (UK terminology) or disconnector (US terminology) is a switch used to isolate a section of a circuit from any energised conductors, by presenting a visible break in the circuit. Isolators are not designed to break load currents (unless fitted with optional arc-breaking feature) or to break fault currents. In high-voltage systems, isolators are used in conjunction with circuit breakers -with the isolators opened after a circuit breaker has opened the circuit, and closed before the circuit breaker closes the circuit. For example, before one can perform maintenance work on, say, a high-voltage circuit breaker, the following sequence must be followed:the circuit breaker is opened, breaking the circuit.isolators located on either side of the circuit breaker are opened, presenting a visible break between the isolator and energised lines.temporary earth (ground) connections are applied to each side of the circuit breaker.barriers and warning signs are erected around the circuit breaker to define the permitted work area.a permit to work card, listing the work to be performed, and any potential hazards, is issued to the personnel who are to maintain the circuit breaker.


How much is a permit for installing a 200 amp service panel in Tucson AZ?

A permit in Tucson can run up to 95 dollars depending on the size of the installation. The best way of finding out a price of the permit is to ask an electrical contractor for an estimate on the job that you want done. Ask the contractor what the cost of the permit is, as a break out price. If the contractor says that you don't need a permit then move on to another contractor. It is in your best interest to obtain a permit and get the job inspected by an inspector. That way if anything goes wrong after the installation is finished and the insurance company gets involved, you won't get blamed for an illegal wiring installation that had never been inspected.

Related questions

DoesCode permit connecting receptacles to a 20ampere branch circuit using short lengths of 14AWG conductors as the pigtail between the receptacle terminals and the 12AWG branch-circuit conductors?

No. This practice is a violation of Article 210.19 (A) of the NEC. "Conductors of branch circuits supplying more than one receptacle for cord-and-plug-connected portable loads shall have an ampacity of not less than the rating of the branch circuit."


How do I know if I can add a plug to a circuit?

In most home renovations there is ample room on a branch circuit to add another outlet. Very seldom does an electrician, when wiring a home, load the circuit up to maximum outlet that the electrical code will permit. Now the thing that has to be kept in mind is what is the load on the circuit now. The second thing to keep in mind is how much is the new receptacle outlet's load going to be. A home branch circuit is protected by a 15 amp breaker, so that is the maximum amperage load you are able to apply to the circuit without the circuit tripping. If you are able to stay within this parameter you should be able to add another receptacle outlet to the existing circuit.


What is the phone number of the Princeton Branch in Princeton?

WikiAnswers does not permit private details to be posted.


Explain what a circuit main earth does?

Basically, it's an earth connection applied for the purpose of making apparatus safe to work on before a Permit to Work or Sanction for Test is issued. Disconnect from power, test dead, apply CME.


Does Orthodox Judaism permit same-sex marriage?

No. This branch of Judaism rejects homosexuality as immoral, since the Torah forbids it (Leviticus ch.18).


What are the specific questions on the actual Florida permit test?

You should be able to obtain an idea of the specific questions on the Florida drivers' permit test by going to the local branch of the Florida Department of Motor Vehicles and asking for the booklet to study for the test from. Further, any driving school in Florida should be able to teach you enough to get your permit.


Is it Possible to trek Manaslu Circuit Single person?

The second reason is that the Manaslu Region Trek has restricted area status. This means it requires a special permit (see below), that the group has two or more members and that a registered trekking guide accompanies the group. In 2011, for Nepal Tourism Year, the permit fee was reduced to US$50 per week.These two factors together have made the Manaslu Trek affordable for budget travelers and it is now being referred to as The New Annapurna Circuit Trek.


How much do you have to pay for your learner's permit in Arizona?

When you're ready, take the test at any Motor Vehicle Division (MVD) branch office or third-party office. You don't need an appointment, and the test is free to take. The same is true for the required vision test. Come to the branch with a parent or legal guardian, who must sign your instruction permit application. Whoever signs must be willing to be legally responsible for your driving conduct. If your parents are married or you have a single legal guardian, you'll just need one signature on the application. But if your parents are divorced and share joint custody, both must come with you when you apply for the permit, or both must sign the application in front of a notary public. Keep in mind that whoever signs the permit application will also be required to sign when you apply for your driver's license. Once you've passed the tests and completed the paperwork, the MVD will issue you an instruction permit for $7. The permit is valid for one year.


How can you use permit in sentences?

I have a permit to drive this car. I'm about to get my permit.


Can you make a sentence for permit?

Please permit me to answer this for you. You'll need a permit for that! My hunting permit expired last month.


What to do to get a gun permit in ms?

If you mean a permit to carry a gun, you apply for it through the DMV. Depending on where you are, you may have to go to another location. For instance, if you live in north MS (Southaven, Olive Branch, etc) you have to go to Batesville, and IIRC, they only take applications on Monday. Mississippi does not require a training class to get a permit, however, if you take a training class from an approved instructor, you qualify for an enhanced or endorsed permit, which entitles you to carry your gun legally in more places. In other words, there are less off limits locations if you have an endorsed permit.


Need of isolator on both side of circuit breaker?

Before anyone is allowed to work on a high-voltage circuit breaker, it must be tripped, electrically isolated, earthed (grounded), barriers/warning notices put in place, and a permit to work document issued by an engineer to the senior member of the maintenance crew. 'Isolation' means a physical (and visible) break in the conductors between the circuit breaker and any potential source of supply -and this is provided by placing isolator switches on each side of the circuit breaker. Without these isolators, the circuit breaker would remain energized, even though the circuit has been broken by the circuit breaker.