it depends on the voltage source being offered by the generator.

watts / volts = amps

If the generator is providing 120V, it is capable of pushing 125 Amps.

If the generator is providing 240V, it is capable of pushing 62.5 Amps.

User Avatar

Wiki User

14y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

14y ago

None. A transformer does not generate electricity, it transforms it. Equations for transforming:

KVA (three phase) = 1250kVA = V(line to line) * I * sqrt(3)

KVA (single phase) = 1250kVA = V (line to neutral) * I

This will give "full load amperage". Transformers sometimes can be overloaded, but you'd need to look at the transformer spec's to know by home much and for how long.

This answer is:
User Avatar

User Avatar

Wiki User

14y ago

A generator does not "put out" amps. Amps are the power consumption of whatever is using the electricity. A 5 kw generator can handle up to 41 amps, but not continuous. It can handle a continuous load of about 33 amps. Amps = Watts/Volts, 5000/120 = 41.66, 41.66 at 80%=33.3.

This answer is:
User Avatar

User Avatar

Wiki User

12y ago

A 1250-kV.A transformer should be able to supply a 1250-kV.A load permanently, or a greater load for short periods of time.

And note that the symbol for kilovolt amperes is 'kV.A', not 'kva'.

This answer is:
User Avatar

User Avatar

Wiki User

13y ago

Watts = Amps x Volts

Amps = Watts / Volts

Amps = 12000 / 120 or 12000 / 240 depending on voltage supplied.

This answer is:
User Avatar

User Avatar

Wiki User

13y ago

All generators/power sources, unless specified, should produce the regular 13amps.. All different gadgets use different amps though.

This answer is:
User Avatar

User Avatar

Wiki User

9y ago

426,517.75 BTU/hr for 125kW

This answer is:
User Avatar

User Avatar

Wiki User

11y ago

600 kva

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How much amps can a 500 kilowatt generator put out?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

If you have 500 watts and 240v what is the amperes?

The equation that needs to be used is I = W/E. Amps = Watts/Volts. Amps = 500/240 = 2.08 amps.


How much did the first electric generator cost?

almost $500 too $800 dollars maybe?


How much of a load is placed on a battery that has a 500 CCA rating?

250 amps for 15 seconds.


Will a 500 watt generator run a hair dryer?

Most hair dryers are rated at least 800 watts to as much as 1875 watts. Given that, a 500 watt generator will NOT run a hair dryer. You would need at least a 2000 watt generator, just be be on the safe side.


Which is bigger between .5 amp and .400mA?

.5 amps equals 500 ma, which is much larger than .400 ma.If you meant between .5 amps and 400 ma, then again, .5 amps equals 500 ma, which is larger than 400 ma by a factor of 100 ma.


500kva how many amps given capacity?

500 KVA how many amps? almost 650 Amps according to formula.


How many amps does 500 watt halogen pull?

At 120 volts it will pull 4.166 amps. At 240 volts it will pull 2.08 amps.


What is the formula to convert hp or horsepower to kilowatts or kw?

1 Horsepower equals 746 watt, or 0.746 kilowatt. To convert horsepower to kilowatt, one has to multiply the amount of horsepower by 0.746. For example: 500 hp = (500*0.746) kW = 373 kW


How many amps is 500 watts for a jump starter?

To answer this question a voltage needs to be stated. Amps = Watts/Volts.


What size generator to produce 50 amps?

To completely power everything you would need a 12KW generator. However in an emergency you can live with a 5.5KW generator. You will not however be able to run an electric oven at all. To run an electric water heater almost everything else will have to be shut off. You will have to ration the power.


What is the max load of 500 kva DG?

I=Kva*1000/v*1.732 =500*1000/415*1.732 =500,000/718.78 =695.62 Amps. So max.load of 500kva DG is 695.62 Amps


120 volts plus 500 watts equals how many amps?

The formula you are looking for is I = W/E. Amps = Watts/Volts.