answersLogoWhite

0


Best Answer

isolator is a off load device which is used for isolating the downstream circuits from upstream circuits for the reason of any maintanance on downstream circuits. it is manually operated and does not contain any solenoid unlike circuit breaker. it should not be operated while it is having load. first theload on it must be made zero and then it can safely operated. its specification only rated current is given.

but circuit breaker is onload automatic device used for breaking the circuit incase of abnormal conditions like shortcircuit, overload etc., it is having three specification 1 is rated current and 2 is short circuit breaking capacity and 3 is instantaneous tripping current.

User Avatar

Wiki User

8y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

13y ago

An isolator has no circuit protection included in its operation. It just opens or closes a circuit. A circuit breaker has circuit protection included in its operation. A breaker has both overload and short circuit protection in its operation.

This answer is:
User Avatar

User Avatar

Wiki User

11y ago

Isolation: It means separation between equipment and main

supply. When we want to maintain a particular equipment it

should be isolate with mains supply. Other wise we can not

maintain it.

Insulation: It means an insulating material is provided on

the (live) cables or equipment according to their voltage

rating to avoid short ckt b/w live parts and earth faults

b/w live part and ground. This for our safety as well as

equipment safety. if it is not provided may cause so many

electrical hazards or limit the usage of cables in various

places.

S. K. Srivastava

Commercial Officer

KEC International Ltd.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What are the differences between isolator and circuit breaker?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

What is the difference between 16A TP and 16A TPN isolator?

The difference between 16A TP and 16A TPN isolator is the type of the circuit breaker that is used. The terminal design is the other difference.


What is different Circuit Breker And Isolater?

I think that the questioner is asking what is the difference between an isolator and a circuit breaker.A circuit breaker is a switching device designed to interrupt a fault current.An isolator is not intended to break a live circuit but, rather, to provide a visible separation between a circuit component and live conductors.For example, isolators (or 'disconnectors' in US parlance) are located on either side of a high-voltage circuit breaker. If the circuit breaker requires maintenance, then the procedure is to:a. trip the circuit breaker.b. open the isolators on each side of the circuit breaker, so there is a visible gap between the circuit breaker and the 'hot' conductors.c. apply temporary earths (grounds) between each isolator and the circuit breaker.d. complete a 'permit to work' card.e. begin work.


What is a 132 KV line isolator?

An isolator (disconnector in US terminology) is a switch designed to isolate a section of line afterthat line has been de-energised using a circuit breaker, allowing maintenance work to be carried out on the de-energised section.It's function is to provide a visual break between an energised line and a section of de-energised line and, therefore, is usually one of a pair (one at opposite ends of the de-energised section).Isolators are generally not designed to break load currents (and definitly NOT fault currents!!), so the line must be de-energised using a circuit breaker before the isolator is opened, and the isolator must be closed before the circuit breaker is then used to reclose the line.


Why are Isolatorts not opened on Load?

To interrupt the current requires a more-expensive circuit-breaker. An isolator is used to isolate a section of power line after the current has been stopped.


Can a Circuit breaker be used as a Switch?

Yes a circuit breaker is a switch but it should not be used as a switch. The continuous turning off and on of a breaker weakens the internal mechanism and reduces the tripping value of the breaker. There is in the marketplace breakers that are designed to be used as switches. These are usually used in large warehouses where the lights are turned on in the morning and shut off at night. Using these specifically designed breakers for switches does not wear out the tripping mechanism or reduce the tripping value. <<>> A circuit breaker can be used as a switch, although in most cases there are less expensive switches you can use.

Related questions

What is the difference between 16A TP and 16A TPN isolator?

The difference between 16A TP and 16A TPN isolator is the type of the circuit breaker that is used. The terminal design is the other difference.


What is different Circuit Breker And Isolater?

I think that the questioner is asking what is the difference between an isolator and a circuit breaker.A circuit breaker is a switching device designed to interrupt a fault current.An isolator is not intended to break a live circuit but, rather, to provide a visible separation between a circuit component and live conductors.For example, isolators (or 'disconnectors' in US parlance) are located on either side of a high-voltage circuit breaker. If the circuit breaker requires maintenance, then the procedure is to:a. trip the circuit breaker.b. open the isolators on each side of the circuit breaker, so there is a visible gap between the circuit breaker and the 'hot' conductors.c. apply temporary earths (grounds) between each isolator and the circuit breaker.d. complete a 'permit to work' card.e. begin work.


Need of isolator on both side of circuit breaker?

Before anyone is allowed to work on a high-voltage circuit breaker, it must be tripped, electrically isolated, earthed (grounded), barriers/warning notices put in place, and a permit to work document issued by an engineer to the senior member of the maintenance crew. 'Isolation' means a physical (and visible) break in the conductors between the circuit breaker and any potential source of supply -and this is provided by placing isolator switches on each side of the circuit breaker. Without these isolators, the circuit breaker would remain energized, even though the circuit has been broken by the circuit breaker.


How can you recognize the circuit breaker and Isolator?

A circuit breaker's contacts are enclosed, and must provide a means of extinguishing the arc created when the device opens on a fault current. An isolator's contacts are normally visible -they are not designed to break a fault current or, in most cases, a load current, but merely to provide a visible break between the supply and the load.


What are the differences between a vacuum breaker and a SF6 gas circuit breaker breaker and a sf6 gas circuit breaker?

vcb is have vaccume and sf6 cb is filled with sf6 gas which will have good arc quencing property


What is the difference between an isolator switch and miniature circuit breaker?

An isolator is just a disconnector ; it disconnects the load from the supply. The method of operating the isolator can be through a handle or through a spring or through a motor. Isolators can be on-load isolators , which can be switched off on load , or they can be off-load isolators which should not be switched off on load. A Miniature Circuit Breaker can break or open in the event of a fault. Thus its load carrying capacity is extremely high , up to 10 kiloamperes or more. What this means is that if a short circuit current to the tune of 10 kA flows through an isolator , it will melt the isolator contacts , and the damage can be irrepairable. When the same current flows through an MCB , the breaker will trip , without suffering any permanent damage. Thus an MCB is a protective device.


What is an electrical isolator?

Something that doesn't let electricity throughAnswerAn isolator (UK terminology) or disconnector (US terminology) is a switch used to isolate a section of a circuit from any energised conductors, by presenting a visible break in the circuit. Isolators are not designed to break load currents (unless fitted with optional arc-breaking feature) or to break fault currents. In high-voltage systems, isolators are used in conjunction with circuit breakers -with the isolators opened after a circuit breaker has opened the circuit, and closed before the circuit breaker closes the circuit. For example, before one can perform maintenance work on, say, a high-voltage circuit breaker, the following sequence must be followed:the circuit breaker is opened, breaking the circuit.isolators located on either side of the circuit breaker are opened, presenting a visible break between the isolator and energised lines.temporary earth (ground) connections are applied to each side of the circuit breaker.barriers and warning signs are erected around the circuit breaker to define the permitted work area.a permit to work card, listing the work to be performed, and any potential hazards, is issued to the personnel who are to maintain the circuit breaker.


What is a 132 KV line isolator?

An isolator (disconnector in US terminology) is a switch designed to isolate a section of line afterthat line has been de-energised using a circuit breaker, allowing maintenance work to be carried out on the de-energised section.It's function is to provide a visual break between an energised line and a section of de-energised line and, therefore, is usually one of a pair (one at opposite ends of the de-energised section).Isolators are generally not designed to break load currents (and definitly NOT fault currents!!), so the line must be de-energised using a circuit breaker before the isolator is opened, and the isolator must be closed before the circuit breaker is then used to reclose the line.


What is spn isolator switch?

An SPN isolator switch is a circuit breaker; they are a device, which when used can automatically switch off the flow of electricity. They are used to protect a piece of machinery or equipment from damage by an overload of electricity.


What will happend when isolater will open on load?

An 'isolator' (UK terminology) or 'disconnect' (US terminology) are generally not designed to break a load current. The circuit must first be broken using a circuit breaker. If an isolator were to be opened 'on load', then it's likely to draw an arc which it has no means of breaking. The heat produced by that arc is likely, then, to damage the isolator's contacts.


Why do you use isolator on both side of circuit breaker?

Opening a circuit breaker merely interrupts the current flowing through that circuit. It doesn't remove the voltage from the circuit breaker. Isolators (called 'disconnects' in North America) place a visible gap between the circuit breaker and energised conductors, allowing work to be performed on the circuit breaker safely. The full procedure involves: 1. Tripping the circuit breaker (CB). 2. Opening both isolators. 3. Applying temporary earth (ground) connections on either side of the CB. 4. Placing barriers and warning signs around the CB. 5. Issuing a permit to work card to the maintenance supervisor.


What is the operation of isolator?

An 'isolation transformer' is a 1:1 ratio mutual transformer. It electrically isolates the secondary circuit from the primary circuit without changing the voltage level. A bathroom shaver socket uses an isolation transformer.