answersLogoWhite

0


Best Answer

Basically the formula is I = P / V where I = amps, P = power (kV) and V = volts for a single phase 11 kV genset the formula is 11000/400 = 27.5 amps max load. For a 3 PHASE GEN then 11000x0.8/400/3 = 7.3 amps per phase.

User Avatar

Wiki User

15y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What is the formula for calculating the full load current of 11 kV generator?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What is the formula for calculating the full load current of 3kW motor?

The formula you are looking for is I = Watts/ Voltage, I = 3000/voltage.


What is voltage regulation of synchronous generator?

The volatge regaulation be calculated by calculating the percentage difference between volatge at no load and voltage at full load


What is the formula for calculating the full current load of a 400 watt light?

Assuming an incandescent bulb and a 120 volt supply the formula is Watts = Volts x Amps x Power Factor where PF = 1 for resistive load. Amps = 400 / 120.


What type of current flows in stator and rotor winding of a dc shunt generator?

The field winding in the stator is exposed to the full current generated by the rotor's winding.


What is the full load current of 200kW 380V 3-phase generator with 0.8 lagging power factor?

304 Amperes


What is is the formula for calculating the full load current of 23KVA generator?

to calculate the motor full load current one should know motor power factor, supply voltage and phase of supply. Assuming your motor is with 0.85 pf and 3 phase, 415V source then P = (Sqrt3)*V*I*pf 18500 = 1.732*415*0.85*I hence I = 30.2A


What will be full load current for 500KVA generator?

KVA = Root 3 VII = KVA *1000 / 1.73 * 415I = 500000 / 717I = 697 ApproxAnswerIt depends on the rated voltage of the generator.


What is the formula for calculating the full current load of a 400 watt metal halide light?

For the amperage of a metal halide fixture look for the nameplate which can be found on the side of the ballast. There it will tell you what the amperage of the fixture draws. Knowing what one fixture draws will allow you to size the lighting circuit for wire and breaker sizes.


What is the formula to calculate the overload setting for a star delta starter?

Full load current ofthe motor x 0.58


How do you figure the gallons of fuel in a horizontal cylinder tank?

The actual gallons of fuel would depend on how full the cylinder tank is. Here is the formula for calculating the maximum capacity of the tank.The formula for calculating the volume of a cylinder is V = πr2hV = volumeπ = PI (approximately 3.14)r = radius (half the diameter of the round portion of the tank)h = height (or length) of the tank


What is the formula to find reading of ammeter?

V=I x R Voltage= Current x Resistance to make it easier you could rearrange the formula so it looks like this: I=V/R


What is full form of ABACUS?

ABACUS is a name of a calculating apparatus - it is not an acronym.