we will get its insulation resistance value wchich should be greater than 200Mohms
Megger the body and the earth point. It should be zero
To test a motor, use a megger (megohm meter) to test the insulation of the internal motor windings. Select a voltage to apply to the motor using an output from the megger that is higher that the operating voltage that the motor operates on.
You need a Megger tester. With one lead attached to the winding and the other attached to the motor housing, the Megger sends a high voltage through the winding. The Megger reads the resistance, letting you know if there is a short to ground.
Briefly, a megger test is testing an electric circuit at load. The circuit might prove good at normal resistance measuring but fails when applying high voltage. Read the megger result correctly, every electric circuit will fail if stressed high enough. Disconnect any servo drive or frequency controller before testing.
Normally the megger should be selected based on the following criteria. 1.Voltage rating of the megger 2.Range of the megger value 3.Manual - Hand operated analogue type 4.Auto- Digital Megger To measure the insualtion resistance of Motor (LV Motors) Up to 500 V/1000 V Megger is sufficient To measure the insualtion resistance of Motor (HV Motors) Up to 5000 V can be choosen Normaly the range starts from 0.5 to Infinity meg value in the analogue However in digital the based on the least count /range of the instrument we can able to measure the insualtion value.
Yes, a megger can potentially damage the insulation of a motor if used improperly. Meggers apply high voltage to test insulation resistance, which can stress or break down the insulation if the motor is not designed for such testing. It's important to ensure that the motor is disconnected from power and that the insulation is rated for the megger's test voltage. Always follow manufacturer guidelines and use appropriate testing techniques to minimize risk.
By Megger testing (meggering) of the motor any one can measure the IR of the motor. MEGGER is a device used to measure IR. Analog Megger device may generate 500 volts..it gives coil to coil or coil to body IR value...it should not be less than 2 Mega ohm, generally it should be or kept more than 5 mega ohm...thanks ...DEEPAK RAJPUT
You use a device called a megger or meg ohm meter. Have the voltage range of the megger set to the working voltage of the motor. The first test should be to ground. One lead on the frame of the motor , the other lead one of the 6 wires. Test all 6 wires. If no ground shows up, test the individual coils against one another. If the coils are not grounded together, the motor is safe to energize.
Any good motor shop should sell Baldor motor parts or be able to obtain them for you.
415V commonly available wire is 300V or 600V so that would need to be 600V wire to use a megger or a hipot tester (2* operating voltage +1000V) 2000 volt megger or hipot should verify the wiring in this instance 2500v megger will be necessary for 600V wire and wiring devices you also must look and ambient temperature and humidity a test after some operation time can verify this
what will be the result if the starting winding in a split phase motor fails
To megger a 3-phase 2-speed motor, begin by disconnecting the motor from the power supply to ensure safety. Use a megohmmeter to test the insulation resistance by connecting one lead to each phase terminal and the other lead to the motor frame (ground). Perform this test for all three phases, and check the readings; they should typically be above 1 MΩ. If insulation resistance is below this threshold, it indicates potential insulation failure that may require further inspection or repair.